Hello!
IT Security department made an order to disable using of SMB v1 in company network.
But I have faced that I can't find how to change version of protocol SMB for external storage in AV. Is it possible to change?
device: NetBotz Rack Monitor 450
firmware: NetBotz4.6.2
(CID:133370304)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:38 PM . Last Modified: 2024-04-04 03:36 AM
Dear Micheal,
From your question:
...But I have faced that I can't find how to change version of protocol SMB for external storage in AV. Is it possible to change?
As far as I know, unfortunately this is not possible in the current version of NetBotz-4.x firmware.
Therefore, if this is very critical for you, I recommend migrating to use the NFS protocol. Fortunately, setting up an NFS service on Windows servers is very simple. The staff of your IT department should not have any problems. At the moment this is a quick real solution to your problem.
And again, I can recommend you to use the Feature requests option here on the EcoStruxure IT. And it is possible in the future version of NetBotz-4.x firmware this feature will be implemented.
With respect.
(CID:133370543)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:38 PM . Last Modified: 2024-04-04 03:36 AM
Dear Micheal,
From your question:
...But I have faced that I can't find how to change version of protocol SMB for external storage in AV. Is it possible to change?
As far as I know, unfortunately this is not possible in the current version of NetBotz-4.x firmware.
Therefore, if this is very critical for you, I recommend migrating to use the NFS protocol. Fortunately, setting up an NFS service on Windows servers is very simple. The staff of your IT department should not have any problems. At the moment this is a quick real solution to your problem.
And again, I can recommend you to use the Feature requests option here on the EcoStruxure IT. And it is possible in the future version of NetBotz-4.x firmware this feature will be implemented.
With respect.
(CID:133370543)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 09:38 PM . Last Modified: 2023-10-22 04:12 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.