Hello team!
I have a brain teaser and cant find the answer no where
So I just installed DCE server and client, added a rPDU device with the correct ddf
integrated DCE in DCO and found that device in discoveries with some of its sensor data
and now i am trying to associate it with the device in DCO
I cant find a way of dragging it to the rack/rPDU, tried looking around the different menus and found nothing relevant over there, browsed this forum and no luck here too
Could you please help me understand what is the correct way of doing this association?
and one more thing for some reason the data it shows in DCO is only the sensors connected to the rPDU data, and no actual data of the rPDU as kW, Amps and so - what could be the reason for that?
Thank you very much!
(CID:141265508)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 06:12 PM . Last Modified: β2024-04-03 03:04 AM
Okay so i have managed to find the answer on my own
there is an option in DCO which located under the drop menu of "Operation" and called "Device Association" - it will open a tab from which you can drag the sensor to its device and see your information
in my case i found that the kW data was transferring and after associating it with the pdu i saw the current kW and all the temperature data that my sensors provide
hope it helps anyone else who struggled
have a nice day
(CID:141265635)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 06:12 PM . Last Modified: β2024-04-03 03:04 AM
Okay so i have managed to find the answer on my own
there is an option in DCO which located under the drop menu of "Operation" and called "Device Association" - it will open a tab from which you can drag the sensor to its device and see your information
in my case i found that the kW data was transferring and after associating it with the pdu i saw the current kW and all the temperature data that my sensors provide
hope it helps anyone else who struggled
have a nice day
(CID:141265635)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 06:13 PM . Last Modified: β2024-04-03 03:04 AM
The information you were looking for was on the following page:
(CID:141266197)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 06:13 PM . Last Modified: β2023-10-20 05:01 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.