Alert when status is cleared
Good Morning,
I've connected third parties UPS to our IT Expert infrastructure console and I've correctly set up the alerts when the device lost input voltage.
From the web console I can also see when the problem status is cleared ( picture below ), but I would like to have also an email alert when this happen. Is possible to configure it?
Thanks
Andrea
- Labels:
-
IT Expert
- Tags:
- english
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-15 02:59 PM
Hi @Andrea_996
Please check your profile in IT Expert to see if you have checked the option to send clearing alarms.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-15 02:59 PM
Hi @Andrea_996
Please check your profile in IT Expert to see if you have checked the option to send clearing alarms.