Hi all!
After upgrade to DCE-7.5.0, I found the above problem: that is, if rPDUs are connected together by a chain (via A-Bus link), then all sensors "Device n - Power, Bank m" are switched to the Unplugged state.
This problem occurred because of an error in the DDF-file apcpower.xml v.47. Below is my diff-file, which shows where you need to make corrections to fix the above error:
diffdiff apcpower.xml apcpower_mod.xml2740,2759c2740,2745 <After making the above changes, we finally get a fully working DDF-file apcpower_mod.xml, and the above problem with Unplugged sensors disappears.
I hope the DDF team will analyze this problem and make the necessary corrections.
With respect.
(CID:128760819)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:29 PM . Last Modified: 2024-04-05 02:37 AM
Thanks or your input, my team will have a look at this,
(CID:128760833)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:29 PM . Last Modified: 2024-04-05 02:37 AM
Thanks for the quick feedback 😀.
(CID:128760850)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:30 PM . Last Modified: 2024-04-05 02:37 AM
Dear Jesper Thomsen,
Unfortunately, the DCE-7.6.0 upgrade showed, that the above mentioned problem has not been resolved (the DDF-file apcpower.xml v.50 is used).
This is bad ☹️.
With respect.
(CID:137105519)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:30 PM . Last Modified: 2024-04-05 02:36 AM
Dear Jesper Thomsen,
For this annoying problem, I created the corresponding Request modification:
Hope to get a quick feedback...
(CID:137105529)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:30 PM . Last Modified: 2023-10-20 04:59 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.