Adding a Supplemental OID

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Adding a Supplemental OID
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-02 02:19 PM . Last Modified: โ€Ž2024-04-09 04:14 AM

0 Likes
7
880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-02 02:19 PM . Last Modified: โ€Ž2024-04-09 04:14 AM

Adding a Supplemental OID

Hi, I'm trying to get data from a generic SNMP device by adding a Supplemental OID. DCE (V7.2.6.24) reports that the device is being scanned successfully, but I can't see any sensor data. The sensor type configured in SNMP Device Settings is 'Generic ( deg C)', and the OID is .1.3.6.1.4.1.31440.10.5.1.1.1). All I see in 'View Device Sensors' is 'Link Status', with value 'Online', but I can't work out how to tell DCE that there is a temperature sensor at this MIB OID. Can anyone help, or point me at the right documentation ?

(CID:99157389)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-02 02:19 PM . Last Modified: โ€Ž2024-04-09 04:14 AM

0 Likes
1
880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-02 02:19 PM . Last Modified: โ€Ž2024-04-09 04:14 AM

Hi Hugh,

 

Please try polling the device using an SNMP scanning tool, either a command line utility or something with a mib browser such as a freeware app I often use called GetIf. You may find that the OID is returned with a specific instance. The OID

.1.3.6.1.4.1.31440.10.5.1.1.1

may actually be returned as

.1.3.6.1.4.1.31440.10.5.1.1.1.0

 

As an example, when I poll an APC UPS for basicIdentModel:

.1.3.6.1.4.1.318.1.1.1.1.1.1

It returns a value along with the OID including an instance

.1.3.6.1.4.1.318.1.1.1.1.1.1.0

 

Additionally, you may need to verify all of the SNMP parameters. You can also check other OIDs as maybe it is not responding to this one as it should. If the system is mib-2 compatible, it may respond to:

.iso.org.dod.internet.mgmt.mib-2.system.sysUpTime

.1.3.6.1.2.1.1.3.0

 

Another thing to look at is how the device responds if you do use getif or something like that. Is the device returning an integer or other numeric value or is it replying with a string? If it's 70 degrees, is the device returning 70, 700, 70.0 or is it returning text such as "70 degrees"? Supplimental OIDs can't be used with strings so "70 degrees" won't show up as a valid sensor. 700 will but without a multiplier, you'll have to deal with 700 and create thresholds based on that.

 

If this fails, you may want to either troubleshoot with support or possibly work with Multivendorsupport@apcc.com. the latter is a team that creates DDFs for Data Center Expert.

 

Steve

(CID:99157393)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-02 02:19 PM . Last Modified: โ€Ž2024-04-09 04:14 AM

In response to DCIM_Support
0 Likes
0
880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-02 02:19 PM . Last Modified: โ€Ž2024-04-09 04:14 AM

Hi Steven, Thanks for the response. I actually use GETIF already, so I do know the actual OID, and in this case, it does not have the trailing '0'. In fact, it has a number of temperature sensors connected, with the last digit incrementing from 1 through to 22, for each of those sensors.

However, the variable being returned is a string, as it needs a decimal point in it, and MIBs don't support that as a number, so I guess this might be the problem. So, I tried a different OID which is supposed (i.e. as reported by GETIF) to return an integer, but I still don't get how to see that listed as a sensor in 'View Device Sensors'. By the way, I can also see sysUpTime on GETIF, but I can't see how to get DCE to grab that, and there is no variable type for 'timeticks'.

I suspect that I am missing some essential step in getting DCE to 'create' a sensor, but I can't find any step-by-step instructions for doing that.

(CID:99157414)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-02 02:19 PM . Last Modified: โ€Ž2024-04-09 04:14 AM

0 Likes
1
880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-02 02:19 PM . Last Modified: โ€Ž2024-04-09 04:14 AM

Hi Hugh,

 

Maybe time ticks was a bad example, I didn't test it but was trying to think more generic OIDs. Th etrailing 0 is just the instance and if you're getting 31440.10.5.1.1.1 through 31440.10.5.1.1.22, that should work as well unless it is indeed a string. 

 

Creating of a sensor should be automatic. If we discover the device properly, if we can poll the device with a supplemental OID, it should simply appear as a sensor. There is no "create sensor" option available or needed. Keep in mind that after you add the OID, you may have to either wait for the next polling cycle or right click the device and select request device scan.

 

Do you have any devices that are communicating and showing valid sensors? Can you try adding a supplemental OID on one of those devices....even if it is something already showing as a sensor. Just name it something you can easily find. Here's an example of  output voltage that I added to a Smart-UPS:

.1.3.6.1.4.1.318.1.1.1.4.2.1.0

It should be just that simple:

 

Steve

(CID:99157401)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-02 02:19 PM . Last Modified: โ€Ž2024-04-09 04:14 AM

In response to DCIM_Support
0 Likes
0
880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-02 02:19 PM . Last Modified: โ€Ž2024-04-09 04:14 AM

OK. Just tried adding exactly that and our Symmetras are now showing the new sensor with value 240.0 V as per your picture. So, I'm a bit baffled as to how to get this other stuff working ๐Ÿ˜€ 

 

(CID:99157415)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-02 02:19 PM . Last Modified: โ€Ž2024-04-09 04:14 AM

0 Likes
1
880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-02 02:19 PM . Last Modified: โ€Ž2024-04-09 04:14 AM

Hi Hugh,

 

Maybe you want to try running a packet capture. Make sure DCE is sending the correct requests and make sure the device is responding properly. If you contact tech support, they can help with this. If a remote session is possible, they can actually run one for you.

 

Try SNMP V1 if you're currently using V3. If the device uses V2c, it's not going to communicate properly. You seem to be setting up DCE properly so the only thing left is the communications between DCE and the specific device.

 

Steve

(CID:99157406)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-02 02:19 PM . Last Modified: โ€Ž2024-04-09 04:14 AM

In response to DCIM_Support
0 Likes
0
880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-02 02:19 PM . Last Modified: โ€Ž2024-04-09 04:14 AM

Hi Steve, It looks like I'll have to go the Tech Support route, cos I am using SNMP V1, and V3 is not an option for these devices. I have a scheduled visit form our support engineer next week, so I'll follow up that way. Thanks for your help.

 

Regards

 

Hugh

(CID:100340653)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-02 02:19 PM . Last Modified: โ€Ž2023-10-31 10:13 PM

0 Likes
0
880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-02 02:19 PM . Last Modified: โ€Ž2023-10-31 10:13 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore