3 phase rack PDUs - power configuration issue

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • 3 phase rack PDUs - power configuration issue
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
108
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:18 PM . Last Modified: ‎2024-04-09 04:14 AM

0 Likes
3
796
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:18 PM . Last Modified: ‎2024-04-09 04:14 AM

3 phase rack PDUs - power configuration issue

I'm trying to model a room in Europe, is 230V , 50Hz per phase.

The configuration I have is that the cabinet PDUs receive a 3 phase 16A supply. The PDU outputs are 3 banks of sockets, one back of L1 sockets, one bank of L2 and one bank of L3.

The configuration in DCO is OK up until I try and connect a server to the rack PDUs. When I do this, the software wants to connect across the phases (as is used in 110V systems), so I can only pick L1-L2, L2-L3 or L3-L1, not L1, L2 or L3 as is the actual configuration.

I've tried all combinations of Voltage output settings on the PDU, but nothing I can do will allow me to connect to a single phase. Am I using the wrong gnome?

I amusing the "Smart PDU - 3 Phase 208-240V 30A" with the output voltage set to "230v, 50Hz, Single", with the PDU being fed from a "16A 3P IEC309" breaker module.

Any help on how ths shoudl be configured, or what gnomes I should be using would be appreciated.

Thanks,

Steve

(CID:99157379)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:18 PM . Last Modified: ‎2024-04-09 04:14 AM

0 Likes
1
796
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:18 PM . Last Modified: ‎2024-04-09 04:14 AM

Hi Steve,

From reading your configuration it seems like the problem most likely is located in the floor PDU output voltages which must be set to the right voltages as well (400,50hz,3p).

If that is not the case it would be nice to see a screenshot from the power dependency view with the linking turned on and the server selected in order to the see the power path from server to UPS.

Besides that view also the power properties of the PDU, rack mount PDU and server would be information needed.

However please let me know because maybe a screensharing session will be an easier way going forward?!?

/Søren

(CID:99157387)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:18 PM . Last Modified: ‎2024-04-09 04:14 AM

0 Likes
1
797
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:18 PM . Last Modified: ‎2024-04-09 04:14 AM

Hi Steve,

From reading your configuration it seems like the problem most likely is located in the floor PDU output voltages which must be set to the right voltages as well (400,50hz,3p).

If that is not the case it would be nice to see a screenshot from the power dependency view with the linking turned on and the server selected in order to the see the power path from server to UPS.

Besides that view also the power properties of the PDU, rack mount PDU and server would be information needed.

However please let me know because maybe a screensharing session will be an easier way going forward?!?

/Søren

(CID:99157387)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:18 PM . Last Modified: ‎2024-04-09 04:14 AM

In response to DCIM_Support
0 Likes
0
796
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:18 PM . Last Modified: ‎2024-04-09 04:14 AM

Hi, Thank you that seems to have worked. I had the PDUs set for 415V and that for some reason only allows servers to be connected between the phases. Thanks, Steve

(CID:99157404)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:19 PM . Last Modified: ‎2023-10-31 10:12 PM

0 Likes
0
796
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:19 PM . Last Modified: ‎2023-10-31 10:12 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of