About Rack PDU mapping to ITA for device association

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • About Rack PDU mapping to ITA for device association
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
sesa157186_brid
Ensign sesa157186_brid Ensign
Ensign

Posted: ‎2021-07-20 02:19 AM

0 Likes
3
1476
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-20 02:19 AM

About Rack PDU mapping to ITA for device association

Hi team , We know our APC rack PDU can mapping to ITA for peak KW association. Here are two questions need your advice .

 

1. If we use AP7XXX series that only have Amp value , does it work for ITA peak value monitor ?

 

2. If we use 4 rPDU mirror port function to group it , in only one IP address situation , does it work mapping to ITA for device association for these 4 rPDU ?

 

Your input would be appreciated .

Labels
  • Labels:
  • Data Center Expert
  • IT Advisor
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Jef
Admiral Jef Admiral
Admiral

Posted: ‎2021-07-20 03:13 AM

0 Likes
2
1472
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-20 03:13 AM

Hi Billy,

 

1) If the device/rack pdu can only report amp values, then the amp measurements expected to be displayed in ITA. Peak and Average values are power (watt) related data.

2) In ITA we cannot associate same item multiple times - so your 'grouped r-pdu' may show-up as one device (with one IP address) and may only be associated once. And concerning the measured data, it may depend on how the data being reported to ITA (from DCE). But in general the functionality of the daisy chained rack pdus may not be supported in ITA.

 

Kind regards,

Jef

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Jef
Admiral Jef Admiral
Admiral

Posted: ‎2021-07-20 03:13 AM

0 Likes
2
1473
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-20 03:13 AM

Hi Billy,

 

1) If the device/rack pdu can only report amp values, then the amp measurements expected to be displayed in ITA. Peak and Average values are power (watt) related data.

2) In ITA we cannot associate same item multiple times - so your 'grouped r-pdu' may show-up as one device (with one IP address) and may only be associated once. And concerning the measured data, it may depend on how the data being reported to ITA (from DCE). But in general the functionality of the daisy chained rack pdus may not be supported in ITA.

 

Kind regards,

Jef

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

sesa157186_brid
Ensign sesa157186_brid Ensign
Ensign

Posted: ‎2021-07-20 07:26 PM

In response to Jef
0 Likes
1
1461
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-20 07:26 PM

Hi Jef ,

 

Thank you for the clarify .

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Jef
Admiral Jef Admiral
Admiral

Posted: ‎2021-07-20 11:11 PM

In response to sesa157186_brid
0 Likes
0
1456
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-20 11:11 PM

You are very welcome, Billy
kind regards,

Jef

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of