Dear Community Members, We are currently experiencing a technical issue that is affecting the ability to create new posts. Our team is actively investigating the root cause and working to resolve it as quickly as possible. We apologize for the inconvenience and appreciate your patience. SE Community Team!
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-20 02:19 AM
Hi team , We know our APC rack PDU can mapping to ITA for peak KW association. Here are two questions need your advice .
1. If we use AP7XXX series that only have Amp value , does it work for ITA peak value monitor ?
2. If we use 4 rPDU mirror port function to group it , in only one IP address situation , does it work mapping to ITA for device association for these 4 rPDU ?
Your input would be appreciated .
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-20 03:13 AM
Hi Billy,
1) If the device/rack pdu can only report amp values, then the amp measurements expected to be displayed in ITA. Peak and Average values are power (watt) related data.
2) In ITA we cannot associate same item multiple times - so your 'grouped r-pdu' may show-up as one device (with one IP address) and may only be associated once. And concerning the measured data, it may depend on how the data being reported to ITA (from DCE). But in general the functionality of the daisy chained rack pdus may not be supported in ITA.
Kind regards,
Jef
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-20 03:13 AM
Hi Billy,
1) If the device/rack pdu can only report amp values, then the amp measurements expected to be displayed in ITA. Peak and Average values are power (watt) related data.
2) In ITA we cannot associate same item multiple times - so your 'grouped r-pdu' may show-up as one device (with one IP address) and may only be associated once. And concerning the measured data, it may depend on how the data being reported to ITA (from DCE). But in general the functionality of the daisy chained rack pdus may not be supported in ITA.
Kind regards,
Jef
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.