We have 2 Switchgear which feed our Cooling Units via an ATS.
Switchgear A and Switchgear B both power the ATS which in turn power the Cooling Unit.
Using the Generic ATS genome, I can set the power dependancy from the ATS to a primary connection of Switchgear A and a secondary connection of Switchgear B, which is great (as previously they could only be powered from one source), however, I am unable to power the cooling unit from the ATS.
The genome suggests that the ATS has a Dist panel, but there are no properties in order to create a distribution panel. Assuming that this is why I can't power the cooling unit?
I have also tried to power single feed devices via an ATS (i.e. a Distribution Board), however am finding similar results. I assume this is due to the lack of a breaker panel in the genome?
(CID:140219010)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:19 PM . Last Modified: 2024-04-03 03:24 AM
Hi Sean,
I don't think equipment (such as cooling units) can be powered/connected directly to an ATS device (as power supply). You might want to add a PDU between cooling unit(s) and ATS.
Kind regards
(CID:140712759)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 05:19 PM . Last Modified: 2023-10-20 04:57 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.