Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!
EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:57 AM . Last Modified: 2024-04-09 12:07 AM
Hi all
If we have a customer that has a CACS and just want his rear door monitored (front door is monitored over a special sliding door at the CACS entry), can he use one AP9361 or NBPD0171 for 2 racks by keeping full functionality as if he has on each rack AP9631/NBPD0171
Regards Christoph
(CID:106204555)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:58 AM . Last Modified: 2024-04-09 12:07 AM
Hi Christoph,
The rack access unit and pod can monitor one or 2 doors on supported racks. It does not matter if you are monitoring a front and rear, 2 front, or 2 rear doors. Please note that the AP9361 has the doors listed as front and rear and this can not be changed but it is simply a label. I'm assuming you're not looking to integrate our handles with any 3rd party system.
Steve
(CID:106204560)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 02:58 AM . Last Modified: 2023-10-31 10:15 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Welcome to your new personalized space.
of