Hi all
i have an issue with Rpdu debug_5A1734E07443.tar
i'm not able to login to configuration
via serial port nor http, after i insert user and password, Rpdu reboot itself
i have also upgrade by usb to last fw 6.5.6
is it broken?
is there any way to reset all inside nmc?
thanks
(CID:132652363)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:56 PM . Last Modified: 2024-04-04 11:23 PM
Hi Gianluca,
These APC PDUs function the same way as an NMC2. Holding the reset button for 20 seconds when the NMC's status LED is pulsing green. As soon as this LED changes to amber or orange, release the reset button.
This is ideal if you can no longer do a terminal emulation session (via serial) and issue a format command or before doing a recovery via bootmonitor as advised by Cees.
I hope this helps.
Cheers!
(CID:132652607)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:56 PM . Last Modified: 2024-04-04 11:23 PM
Hi Gianluca,
Check this link : http://www.apc.com/nl/en/faqs/index?page=content&id=FA293874
it describes recovery via the bootmonitor
Good luck,
Cees
(CID:132652557)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:56 PM . Last Modified: 2024-04-04 11:23 PM
Hi
it works
i have tested it today
Thanks for all
(CID:132655551)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:56 PM . Last Modified: 2024-04-04 11:23 PM
Hi Gianluca,
These APC PDUs function the same way as an NMC2. Holding the reset button for 20 seconds when the NMC's status LED is pulsing green. As soon as this LED changes to amber or orange, release the reset button.
This is ideal if you can no longer do a terminal emulation session (via serial) and issue a format command or before doing a recovery via bootmonitor as advised by Cees.
I hope this helps.
Cheers!
(CID:132652607)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 06:56 PM . Last Modified: 2024-04-04 11:23 PM
Thanks
next week i will try
(CID:132659418)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.