EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 06:56 PM . Last Modified: β2024-04-04 11:23 PM
Hi all
i have an issue with Rpdu debug_5A1734E07443.tar
i'm not able to login to configuration
via serial port nor http, after i insert user and password, Rpdu reboot itself
i have also upgrade by usb to last fw 6.5.6
is it broken?
is there any way to reset all inside nmc?
thanks
(CID:132652363)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 06:56 PM . Last Modified: β2024-04-04 11:23 PM
Hi Gianluca,
These APC PDUs function the same way as an NMC2. Holding the reset button for 20 seconds when the NMC's status LED is pulsing green. As soon as this LED changes to amber or orange, release the reset button.
This is ideal if you can no longer do a terminal emulation session (via serial) and issue a format command or before doing a recovery via bootmonitor as advised by Cees.
I hope this helps.
Cheers!
(CID:132652607)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 06:56 PM . Last Modified: β2024-04-04 11:23 PM
Hi Gianluca,
Check this link : http://www.apc.com/nl/en/faqs/index?page=content&id=FA293874
it describes recovery via the bootmonitor
Good luck,
Cees
(CID:132652557)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 06:56 PM . Last Modified: β2024-04-04 11:23 PM
Hi
it works
i have tested it today
Thanks for all
(CID:132655551)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 06:56 PM . Last Modified: β2024-04-04 11:23 PM
Hi Gianluca,
These APC PDUs function the same way as an NMC2. Holding the reset button for 20 seconds when the NMC's status LED is pulsing green. As soon as this LED changes to amber or orange, release the reset button.
This is ideal if you can no longer do a terminal emulation session (via serial) and issue a format command or before doing a recovery via bootmonitor as advised by Cees.
I hope this helps.
Cheers!
(CID:132652607)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 06:56 PM . Last Modified: β2024-04-04 11:23 PM
Thanks
next week i will try
(CID:132659418)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 06:57 PM . Last Modified: β2023-10-20 04:55 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.