AP7930 SNMP command issue - need to reboot interface

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • AP7930 SNMP command issue - need to reboot interface
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
108
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:48 PM . Last Modified: ‎2024-04-09 01:20 AM

0 Likes
4
824
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:48 PM . Last Modified: ‎2024-04-09 01:20 AM

AP7930 SNMP command issue - need to reboot interface

I have a bunch of AP7930 remoted power strips and I have been loosing control of them. I am not able to control them via DCE or by sending SNMP commands to them. When this happens, I reboot the network management  interface card and then I get all control back.

It appears to be random and I don't notice there is an issue until I go to command an outlet off.

Is there a lockout if it receives too many connections? I have two systems access the same device via the same SNMP strings. Would that pose an issue? It doesn't seem to affect 90% of my devices. But it seems to be happening more and more often.

AOS = 3.7.3

APP = 3.7.3

Regards,

J

(CID:105461491)

Labels
  • Labels:
  • DCIM Support
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:48 PM . Last Modified: ‎2024-04-09 01:20 AM

0 Likes
2
824
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:48 PM . Last Modified: ‎2024-04-09 01:20 AM

Hi John,

Here are a few questions I had upon reading your post:

1.) Is this SNMPv1 or SNMPv3? Depending on your answer, are both interfaces enabled on the PDUs?

2.) When SNMP does not work and you reboot the management interface, how are you doing this? Web, telnet, etc? Those interfaces still work okay and just SNMP does not? Can we limit the access issue to the SNMP interface?

3.) Do you have a ballpark on how frequently this happens on each PDU? Like once a day on each PDU, or once a week, etc? We did have an issue in an earlier firmware version where SNMP could timeout after about 50 days and would require a reboot of the management interface.

On the PDU, you can query it with multiple systems. But, I think of it as a little PC/CPU. If you are doing a full walk on the device repeatedly from multiple locations one after the other, then it could get bogged down. A get/set here and there from multiple locations should be fine. You could experience an issue if both systems are trying to do similar actions on the PDU at the same exact time depending on what gets/sets/walks they are doing.

Anyway, you are a few firmware revisions behind. Just as a test, I am not sure if you want to consider upgrading a few PDUs to see if it changes the behavior. The latest available for these devices is AOS 3.9.0/rpdu APP v3.7.4. (You can get it here: ftp://restrict:Kop$74!@ftp.apcc.com/restricted/hardware/nmcard/firmware/rpdu/374/apc_hw02_aos390_rpd...) 

The other thing you could do is check the PDU event log during the time you have an issue and see if it is reporting anything strange. If you can give me the time/date and post a PDU event log here, I could take a look for you. Instructions on downloading it in the preferred format are here: http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156131 

Let me know if you have any questions on what I suggested and asked.

(CID:105461519)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:48 PM . Last Modified: ‎2024-04-09 01:20 AM

In response to DCIM_Support
0 Likes
0
825
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:48 PM . Last Modified: ‎2024-04-09 01:20 AM

1) It is SNMP V1. Some devices are using both but in the cases I have been able to review, only SNMP V1 has been enabled to my knowledge. 2) The devices have been rebooted using telnet into the device as it is the quickest way. On the one device I was able to really play with, it seemed all other functions worked. Just the SNMP seemed to fail. I think the device is still in it's hung up state. Most others we had to reboot and move on. 3) I have not been able to determine a time frame between device hang ups. The unit reports normal until we go to control it and that is random at best. I have held up doing any further upgrading to the units because when i push 3.7.4 firmware I loose all web connectivity to the units. I have not been able to determine the reason why. Port setting, change of protocol, etc. I have looked though the event log and haven't seen anything I could relate to this issue. There is only login/out events and some other minor items like set date/time.

(CID:105461527)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:49 PM . Last Modified: ‎2024-04-09 01:20 AM

In response to DCIM_Support
0 Likes
0
825
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:49 PM . Last Modified: ‎2024-04-09 01:20 AM

Hi John, Nothing jumps out at me with what we've discussed so far beyond it being related to an issue we saw at 49.7 days and fixed it. I thought it was fixed by AOS 3.7.3 though. Next time it happens, could you make note of the device's management interface uptime prior to issuing the reboot to fix SNMP? This would be right on the main screen after you log in via Telnet or it is also in the web interface under Administration->General->About. And to clarify, when this issue happens, no OIDs respond to queries, not just outlet control SETs? (not sure if you can try to check any other OIDs or do a walk) Do you get a timeout or some other type of error message?

(CID:105461529)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:49 PM . Last Modified: ‎2023-10-31 10:15 PM

0 Likes
0
825
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:49 PM . Last Modified: ‎2023-10-31 10:15 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of