AP 9335T sensors intermittent disconnect/connect problem

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • AP 9335T sensors intermittent disconnect/connect problem
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
125
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:18 AM . Last Modified: ‎2024-04-08 11:41 PM

0 Likes
6
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:18 AM . Last Modified: ‎2024-04-08 11:41 PM

AP 9335T sensors intermittent disconnect/connect problem

Hi All, 

I am a freshman in this forum and would like to ask my temperature sensors 9335T problem. Some of 9335T sensors are having intermittent disconnected just for few seconds and back to connected itself. Then repeated again. I've seen so many event logs (only for this). Have you ever had this problem before or what would be the root cause of this? I've provided the devices and sensors list as below and I am using Datacentre structured cabling for connection between Netbotz and sensors.

- 1x Netbotz 200,

- 3x Netbotz 150,

- 7x AP 9520T

- 4x AP 9335TH

- 19x AP 9335T

Thanks in advance...

Regards,

(CID:106210136)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:18 AM . Last Modified: ‎2024-04-08 11:41 PM

0 Likes
1
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:18 AM . Last Modified: ‎2024-04-08 11:41 PM

Hi Mike!

It seems like your appliance have no enough power to supply sensors.

1) Check  and ensure that yours cables are not damaged.

2) If you are using DC cabling, ensure that cable length from appliance (pod)  to the sensor is not exceed 100 ft (30m)

3) Add an additional power supply to your setup. You can connect AP9505i power supply to any of 150's sensor pod you want.

 

(CID:106210143)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:18 AM . Last Modified: ‎2024-04-08 11:41 PM

In response to DCIM_Support
0 Likes
0
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:18 AM . Last Modified: ‎2024-04-08 11:41 PM

Hi Valentin, First of all, sorry for my late update. I was assigned to other project and just came back a few week ago. I know it been too long already. As you suggest I did connect additional powers to 2 of 3 Pod 150 (Previously no power). But the alerts (disconnect/connect) keep coming from all the AP9335T sensors constantly. For the cable length (Pod to Sensors), since it been used over DC structured cabling the end to end length can be more than 30m (i guess). Any thought? Regards,

(CID:110005509)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:18 AM . Last Modified: ‎2024-04-08 11:41 PM

0 Likes
2
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:18 AM . Last Modified: ‎2024-04-08 11:41 PM

Hi Valentin! Thanks for your valuable advices. I assure the cables are good and not physically damage. For the cable length, i think I am within a range 30m as Pod to MDF then MDF to sensors. But my counterpart regions proved that it can go beyond 30m so I am not sure it that really matter. Third one is most possible for me. Now only Netbots 200 connected power source and the other 3x Pod 150 don't. I will connect AP 9505i to one of Pod 150 and observe. Thanks again Valentin! I will keep posted outcomes. Cheers,

(CID:108826581)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:19 AM . Last Modified: ‎2024-04-08 11:41 PM

In response to DCIM_Support
0 Likes
0
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:19 AM . Last Modified: ‎2024-04-08 11:41 PM

Hi aungbobo, any updates to this? Kind regards, Stine

(CID:108826583)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:19 AM . Last Modified: ‎2024-04-08 11:41 PM

In response to DCIM_Support
0 Likes
0
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:19 AM . Last Modified: ‎2024-04-08 11:41 PM

Hi Stine, sorry for my late update. My comment as below

(CID:110005510)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:19 AM . Last Modified: ‎2023-10-31 10:15 PM

0 Likes
0
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:19 AM . Last Modified: ‎2023-10-31 10:15 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore