AD User Groups in DCE

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • AD User Groups in DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:21 PM . Last Modified: ‎2024-04-09 02:50 AM

0 Likes
10
1467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:21 PM . Last Modified: ‎2024-04-09 02:50 AM

AD User Groups in DCE

I have a client that has configured authentication servers within DCE. For individual remote users all works fine but they having issues with User Groups. They are able to see the User Groups but not the members of the groups and members of these group cannot log into DCE. Is there something they could have missed? 

Apparently the same User Groups work fine on all other systems but on DCE.

(CID:103585126)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:22 PM . Last Modified: ‎2024-04-09 02:50 AM

0 Likes
1
1467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:22 PM . Last Modified: ‎2024-04-09 02:50 AM

Kevin,

I have been unable to replicate the error message that you are receiving.  Please add a new user group within the bind location, and provide it with a name that does not have any special characters or spaces.  Add a new test user within the same location and ensure that it is a member of the group.  The group should be a Universal group.  Provide screen captures of the preference settings for the user and user group within the active directory server.  Ensure that the bind user has full control the user groups within active directory.

How many objects are within the bind location?

Best Regards,

Cory

(CID:103585818)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:21 PM . Last Modified: ‎2024-04-09 02:50 AM

0 Likes
3
1467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:21 PM . Last Modified: ‎2024-04-09 02:50 AM

Kevin,

Please reference knowledge base article FA158395 for some tips on configuring Active Directory.  Please ensure that the group type is NOT a global group.  The users and groups need to be within the same search base that is being defined within DCE for your Active Directory server.  If the users are outside of the search base, but the group is not, StruxureWare will not be able to authenticate the users.

Best Regards,

Cory

 

(CID:103585133)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:22 PM . Last Modified: ‎2024-04-09 02:50 AM

In response to DCIM_Support
0 Likes
0
1467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:22 PM . Last Modified: ‎2024-04-09 02:50 AM

Thank you Cory. The knowledge is quite helpful. Will revert back once i have feedback from the client.

(CID:103585143)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:22 PM . Last Modified: ‎2024-04-09 02:50 AM

In response to DCIM_Support
0 Likes
0
1467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:22 PM . Last Modified: ‎2024-04-09 02:50 AM

Hi Cory, I was on site to assist with configuring User Groups from AD for DCE. For individual users it worked fine but we could not get the User Groups to work. We were getting an error pop-up stating " Error setting the remote authentication values." We had changed the group from Global to Universal. The search base only had 146 entries and there are two redundant AD servers. The version of AD is 6.0.6002.18005 and it is on a Server 2003 platform. Is there anything else we can have a look at?

(CID:103585339)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:22 PM . Last Modified: ‎2024-04-09 02:50 AM

In response to DCIM_Support
0 Likes
0
1467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:22 PM . Last Modified: ‎2024-04-09 02:50 AM

Kevin, Please try copying the settings from your current Active Directory server bind within DCE and then deleting/re-adding the remote authentication server. Best Regards, Cory

(CID:103585384)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:22 PM . Last Modified: ‎2024-04-09 02:50 AM

0 Likes
1
1467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:22 PM . Last Modified: ‎2024-04-09 02:50 AM

Hi Kevin,

 

Just to add to Cory's response, you will never see the individuals in the group within DCE. You will only be able to see the group itself and can only apply rights to that group within DCE and not the individuals contained within.

 

Steve

(CID:103585144)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:22 PM . Last Modified: ‎2024-04-09 02:50 AM

In response to DCIM_Support
0 Likes
0
1467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:22 PM . Last Modified: ‎2024-04-09 02:50 AM

Thank you Steven!

(CID:103585145)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:22 PM . Last Modified: ‎2024-04-09 02:50 AM

0 Likes
0
1467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:22 PM . Last Modified: ‎2024-04-09 02:50 AM

 

Hi Cory,

The server bind settings have been deleted and re-added as instructed. The client is now able to add individual users and domain admin group (Global) but there are still issues with user groups (Universal). Could there be something we are missing? Please note we have tried T2_Engineers as a Universal Group without any luck.

 

(CID:103585696)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:22 PM . Last Modified: ‎2024-04-09 02:50 AM

0 Likes
1
1468
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:22 PM . Last Modified: ‎2024-04-09 02:50 AM

Kevin,

I have been unable to replicate the error message that you are receiving.  Please add a new user group within the bind location, and provide it with a name that does not have any special characters or spaces.  Add a new test user within the same location and ensure that it is a member of the group.  The group should be a Universal group.  Provide screen captures of the preference settings for the user and user group within the active directory server.  Ensure that the bind user has full control the user groups within active directory.

How many objects are within the bind location?

Best Regards,

Cory

(CID:103585818)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:22 PM . Last Modified: ‎2024-04-09 02:50 AM

In response to DCIM_Support
0 Likes
0
1467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:22 PM . Last Modified: ‎2024-04-09 02:50 AM

Hi Cory, thank you for the assistance. Removing the special characters resolved the issue. All is working as it should now. Much appreciated.

(CID:103585921)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:22 PM . Last Modified: ‎2023-10-31 10:14 PM

0 Likes
0
1467
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:22 PM . Last Modified: ‎2023-10-31 10:14 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of