2N redundancy calculation issues

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • 2N redundancy calculation issues
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
108
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:22 PM . Last Modified: ‎2024-04-03 11:56 PM

0 Likes
4
878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:22 PM . Last Modified: ‎2024-04-03 11:56 PM

2N redundancy calculation issues

Hello, 

I have looked through out the community & through the tutorial, but no answer to the 2N redundancy problems. I have removed all the breakers I could, but it didn`t help.

Measurement calculation is "predicted value".

  1. If I use 2 UPS with real power it shows double the power - I tried to solve this with droping the power to 50% of real power, but no use, something comes out red(in alarm)
  2. The load in 2N redundancy on racks & equipment is shown double the real value because the load is shown as sum of estimated load & failower load on both paths & then total capacity is 50% instead of 25%.
  3. Whatever I do the cooling capcity always gives me error with calculations & I get message: "Insufficient cooling, so the temparatures may be inacurate." I have even removed rised floor & droped ceilling from the rooms.

Setup is:

UPS - 2 X 100kVA PF 1 (dropped to 50%)

Cooling units InRow - 4 X 37.5 kW

Rack enclosures - 18 pcs - design limit 6,25kW

PDU AP8553 - 36 pcs

 

Measured load per UPS: UPS A - 10002 W , UPS B 9850 W.

Displayed: Capacity : 200 kW(50%now = 100 kW), Load 49 kW.

 

I need to finish the calculations by monday, but I can`t get the right display calculation.

Biggest problem is that I can`t get calculation instantly, but have to wait 24 hours for KPI to calculate.

 

Help please.

 

(CID:136153923)

Labels
  • Labels:
  • Data Center Operation
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:22 PM . Last Modified: ‎2024-04-03 11:56 PM

0 Likes
1
877
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:22 PM . Last Modified: ‎2024-04-03 11:56 PM

Hi Boris,

Depending on complexity of the modeled equipment, redundancy settings, power path settings etc. the capacity calculations can get quite complex. Following pages (and other related pages) contain detail description that may help us to understand how the software works:

Power redundancy

Configuring distributed redundant UPS systems

Redundancy examples

Just a thought, you do not need to reduce the power capacity of the modeled  UPS's, just set them to their full capacity. 

And for the cooling simulation, that seems to be configuration related, and/or at least just a notification concerning the accuracy of the temperature map. If adding some temperature sensors (from the integrated external system/DCE) could be an option, then running the 3D view on Measured plane would give us more realistic picture of the data center.

Kind regards

(CID:136645098)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:22 PM . Last Modified: ‎2024-04-03 11:56 PM

In response to DCIM_Support
0 Likes
0
877
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:22 PM . Last Modified: ‎2024-04-03 11:56 PM

Hi Jef,

I had to complete some other projects. But the troubleshooting topics didn`t help.

 

Also the big problem is that it takes 30 days to see if the calculations will be right. 

The problem is that I get the cooling insufficient for this case.

I don`t want to see this error message in DCO.

For 200 kW in 2N instalation( A feed & B feed) with power distributed redundant in rack enclosures the 150 kw cooling has to be more  than enough.

What can I do. Now also the simple PUE scale is going wild. It is not set on the value that is shown on web, but shows over 5(points to 6 o`clock) 

 

 

 

(CID:137104398)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:22 PM . Last Modified: ‎2024-04-03 11:56 PM

0 Likes
0
877
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:22 PM . Last Modified: ‎2024-04-03 11:56 PM

Hi Jef,

Problem is that Customer would like to se the project calculations.

For this numbers should be:

Max load: 100 kW

Current load:  22 kW / 22%

With this calculation I should`nt get cooling insufficient error. Because cooling power is 150 kw.

Here is the pic with sensors, is this enough sensors? Also there are sensors in cooling units.

(CID:137102978)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 02:22 PM . Last Modified: ‎2023-10-20 04:53 AM

0 Likes
0
877
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 02:22 PM . Last Modified: ‎2023-10-20 04:53 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of