Hello,
I have looked through out the community & through the tutorial, but no answer to the 2N redundancy problems. I have removed all the breakers I could, but it didn`t help.
Measurement calculation is "predicted value".
Setup is:
UPS - 2 X 100kVA PF 1 (dropped to 50%)
Cooling units InRow - 4 X 37.5 kW
Rack enclosures - 18 pcs - design limit 6,25kW
PDU AP8553 - 36 pcs
Measured load per UPS: UPS A - 10002 W , UPS B 9850 W.
Displayed: Capacity : 200 kW(50%now = 100 kW), Load 49 kW.
I need to finish the calculations by monday, but I can`t get the right display calculation.
Biggest problem is that I can`t get calculation instantly, but have to wait 24 hours for KPI to calculate.
Help please.
(CID:136153923)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:22 PM . Last Modified: 2024-04-03 11:56 PM
Hi Boris,
Depending on complexity of the modeled equipment, redundancy settings, power path settings etc. the capacity calculations can get quite complex. Following pages (and other related pages) contain detail description that may help us to understand how the software works:
Configuring distributed redundant UPS systems
Just a thought, you do not need to reduce the power capacity of the modeled UPS's, just set them to their full capacity.
And for the cooling simulation, that seems to be configuration related, and/or at least just a notification concerning the accuracy of the temperature map. If adding some temperature sensors (from the integrated external system/DCE) could be an option, then running the 3D view on Measured plane would give us more realistic picture of the data center.
Kind regards
(CID:136645098)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:22 PM . Last Modified: 2024-04-03 11:56 PM
Hi Jef,
I had to complete some other projects. But the troubleshooting topics didn`t help.
Also the big problem is that it takes 30 days to see if the calculations will be right.
The problem is that I get the cooling insufficient for this case.
I don`t want to see this error message in DCO.
For 200 kW in 2N instalation( A feed & B feed) with power distributed redundant in rack enclosures the 150 kw cooling has to be more than enough.
What can I do. Now also the simple PUE scale is going wild. It is not set on the value that is shown on web, but shows over 5(points to 6 o`clock)
(CID:137104398)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:22 PM . Last Modified: 2024-04-03 11:56 PM
Hi Jef,
Problem is that Customer would like to se the project calculations.
For this numbers should be:
Max load: 100 kW
Current load: 22 kW / 22%
With this calculation I should`nt get cooling insufficient error. Because cooling power is 150 kw.
Here is the pic with sensors, is this enough sensors? Also there are sensors in cooling units.
(CID:137102978)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:22 PM . Last Modified: 2023-10-20 04:53 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.