Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

StruxureOn for DCE or EcoStruxure IT Gateway for DCE

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • StruxureOn for DCE or EcoStruxure IT Gateway for DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:13 PM . Last Modified: ‎2024-04-04 03:24 AM

0 Likes
9
2487
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:13 PM . Last Modified: ‎2024-04-04 03:24 AM

StruxureOn for DCE or EcoStruxure IT Gateway for DCE

What ist the difference in using StruxureOn for DCE or EcoStruxure IT Gateway for DCE? Do I get more benefit installing the gateway?

(CID:133375759)

Labels
  • Labels:
  • Data Center Expert
  • IT Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:13 PM . Last Modified: ‎2024-04-04 03:24 AM

0 Likes
0
2486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:13 PM . Last Modified: ‎2024-04-04 03:24 AM

Dear Marcello Migliore,

As I mentioned in topic , my organization uses EcoStruxure IT digital service for years:

My company uses Schneider Electric's digital service EcoStruxure IT (early RemoteOn, then StruxureOn) for the third year already 😀.

Before the official release this summer, it was a single digital service of this kind from Schneider Electric. But after the official release, the digital service now represents two separate digital services that are different. These differences can be seen on the official website https://ecostruxureit.com/.

EcoStruxure IT Expert - this digital service works only with free EcoStruxure IT Gateway software. Here is an example of a screenshot if you have a DCE server connected instead of a gateway:

The advantage of this digital service is its simplicity and quick of deployment for the end customer. Of the money costs, you will only have expenses of $60/USD/device/year (is the suggested retail price) and that's it 😀. As a result, you will receive a monitoring system, that is accessible to you both through a web-browser and through a special EcoStruxure IT mobile application.

You will also always be aware of the critical alarms and warnings from your devices (but without real time notification – see my detailed answer ). And managing/resolving these alarms is the concern of your organization, i.e. this is your concern. In addition, like DCE software, free gateway software also allows you to create custom alarms, but their functionality is unfortunately significantly inferior to DCE software.

The disadvantages of this digital service based on free gateway software is in my opinion two, but significant.

At first – free gateway software still very little supports 3rd party devices. For example, I have not yet been able to connect all air conditioners, generators, power meters and many other 3rd party equipment to the digital service. In addition, even some native equipment Schneider Electric is connected with restrictions. For example, using NetBotz devices and free gateway software, you can monitor only temperature/humidity sensors, but not dry contacts, for example. 

Secondly – a real time notification for this digital service is not available at all (see my detailed answer ).

EcoStruxure Asset Advisor – this digital service is like a continuation of the previous digital service, and there are no above mentioned disadvantages. This is very good 😀, i.e. you can connect standard DCE software, with all your custom alarms, settings, 3rd party devices and so on. You will have real time notifications, incident tracking (for premium upgraded devices) and 24/7 support of Schneider Electric experts.

The disadvantages - probably the price of the service, i.e. at least $365/USD/device/year. In addition, do not forget that you also need to pay for DCE software/appliance, for device licenses and for its technical support and technical support of your native Schneider Electric devices...

If you have any further questions, please ask.

With respect.

(CID:133375775)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:13 PM . Last Modified: ‎2024-04-04 03:24 AM

0 Likes
0
2486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:13 PM . Last Modified: ‎2024-04-04 03:24 AM

Dear Marcello Migliore,

Tell us, please, have you solved this question or not?

With respect.

(CID:134026458)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:13 PM . Last Modified: ‎2024-04-04 03:24 AM

0 Likes
5
2486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:13 PM . Last Modified: ‎2024-04-04 03:24 AM

Hello Marcello,

 

Thanks for the question. Let me try to add some clarity around our offer and the previous comment.

 

StruxureWare Data Center Expert and StruxureWare Data Center Operation are our on premise monitoring and management platforms respectively. We enabled Data Center Expert to connect to our cloud platform so it could act as an aggregator for our remote monitoring service which at the time was called StruxureOn.

 

As our analytics capabilities improved we wanted our monitoring, remote monitoring and management solutions to take advantage of these benefits thus re-platforming them and changing the name to Ecostruxure. The Ecostruxure IT Gateway pulls more data from the devices and does so in a more uniform manner which enables us to perform the data analysis needed to gain deeper insights into the behavior of the critical infrastructure. 

 

Ecostruxure IT Expert is the cloud enabled monitoring and analytics platform which requires the improved polling capabilities of the gateway. Ecostruxure Asset Advisor is our cloud enabled remote monitoring service and Ecostruxure IT Advisor is our hosted management solution.

 

Currently the gateway ships with the same on board device support as Data Center Expert and we are continually adding device support to the gateway. The gateway supports the same protocols and remains vendor agnostic. If you have a custom DDF for DCE you will most likely need to request that DDF be migrated to the gateway. This process takes roughly 2 weeks.

 

Both the Gateway and Data Center Expert have a polling interval. DCE polls between a configurable 1 and 5 minutes while the gateway polls at 5 minutes. The gateway does not have notification capabilities, instead these notifications will appear within the mobile app or web app. For APC devices specifically when a device enters an alert state a trap is sent to the gateway prompting a poll for the current conditions. This poll happens immediately and the resulting information is sent to the Ecostruxure platform. For third party devices we pick up the alarm during the next polling cycle which could result in a 5 minute delay. If a custom threshold on the gateway is breached there is no need to poll the device and the alert is sent to the Ecostruxure platform immediately. The response rate is very similar to that of DCE as it uses the same mechanism.

 

As mentioned in the previous comment for the Netbotz 200 series we are experiencing a bug with dry contacts which we are addressing. Surveillance will be supported in a future release.

 

For more information on our Ecostruxure offers please visit

https://ecostruxureit.com/all-solutions/

 

For up to date pricing I encourage you to look here

https://ecostruxureit.com/how-to-buy/

(CID:134026566)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:14 PM . Last Modified: ‎2024-04-04 03:24 AM

In response to DCIM_Support
0 Likes
0
2486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:14 PM . Last Modified: ‎2024-04-04 03:24 AM

Dear Ryan Harriman,

Thank you for your reply, but as a representative of end customers, I want to note the following.

From your answer:

If you have a custom DDF for DCE you will most likely need to request that DDF be migrated to the gateway. This process takes roughly 2 weeks.

In fact, this process lasts longer and longer ☹️. For example, below are my support requests for some 3rd party devices with DCE software DDF-files attached by the new gateway software:

Look carefully at the dates of requests, and you will become clear...

From your answer:

As mentioned in the previous comment for the Netbotz 200 series we are experiencing a bug with dry contacts which we are addressing. Surveillance will be supported in a future release.

This problem also lasts longer and longer, see for example the topics  and .

I think it will be superfluous to remind, that because of both of the above problems, it becomes absolutely impossible to migrate end customers with existing equipment to the new gateway software, that is, to the new digital service EcoStruxure IT Expert. This is important to understand, since end customers lose critical information from part of their already functioning equipment...

With respect.

(CID:134027124)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:14 PM . Last Modified: ‎2024-04-04 03:24 AM

In response to DCIM_Support
0 Likes
0
2486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:14 PM . Last Modified: ‎2024-04-04 03:24 AM

Hi spezialist,

Our DDF response times have been longer and inconsistent as of late, which we are working hard to improve. With regard to your specific requests, we'll come back to you with an ETA on them by the end of this week.

Thank you for your patience,

Brian Behbehani

(CID:134027389)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:14 PM . Last Modified: ‎2024-04-04 03:24 AM

In response to DCIM_Support
0 Likes
0
2486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:14 PM . Last Modified: ‎2024-04-04 03:24 AM

Ok, in any case, thanks for the feedback.

(CID:134027483)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:14 PM . Last Modified: ‎2024-04-04 03:24 AM

In response to DCIM_Support
0 Likes
0
2486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:14 PM . Last Modified: ‎2024-04-04 03:24 AM

Hi spezialist,

To follow up, we've looked into your requests and will be beginning work on them next week. We'll reach out to you directly on the specific requests as we develop and test each, to verify with you that they are completed correctly. We are planning for all of these DDFs to be included in the 1.4.1 update, planned for release by the end of September.

Thanks,

Brian Behbehani

(CID:134028381)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:14 PM . Last Modified: ‎2024-04-04 03:24 AM

In response to DCIM_Support
0 Likes
0
2486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:14 PM . Last Modified: ‎2024-04-04 03:24 AM

Dear Brian Behbehani,

Well, I'll wait for a new version of the gateway software to test on real hardware.

Very thanks for the support.

(CID:134028386)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:14 PM . Last Modified: ‎2023-10-22 04:00 AM

0 Likes
0
2486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:14 PM . Last Modified: ‎2023-10-22 04:00 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore