Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DCO sensor import error from DCE

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCO sensor import error from DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:12 PM . Last Modified: ‎2024-04-04 03:25 AM

0 Likes
6
1381
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:12 PM . Last Modified: ‎2024-04-04 03:25 AM

DCO sensor import error from DCE

Hi team,

we have in DCE 4 UPSs with the same firmware, but only two of them the firmware and the serial number are recognized by DCE:

Four UPSs have the same firmware 5.300.7 and the sensors are read properly in all of them in DCE.

But in DCO we can only see in external systems, the UPS that have the serial number and the application version displayed in the previous picture.

We have reseated the managament card in these two UPSs (10.26.46.242 & 10.26.46.146) but the problem continues.

Any idea?

Regards.

(CID:133375662)

Labels
  • Labels:
  • Data Center Expert
  • DDF
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:12 PM . Last Modified: ‎2024-04-04 03:25 AM

0 Likes
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:12 PM . Last Modified: ‎2024-04-04 03:25 AM

Hi Javier,

What do you mean by "have reseated the managament card in these two UPSs"? management cards have been replaced? Did they work before hardware changes? Have they been rediscovered?

If I understand correctly, those 2 UPS's without serial number, they do not appear in DCO at all (Planning Device Association / Unassociated Devices), right?

If you add a new device (any device, such as rack pdu), would that device appear in DCO?

Do you know if they (all 4 UPS's) are added/discovered same way and same time in DCE? or perhaps there might have been discovered with different DCE version? Apparently they seem to be different model (just wondering). If possible perhaps they could be tested by re-adding/re-discovering them (all 4) in DCE.

Kind regards

(CID:134023899)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:12 PM . Last Modified: ‎2024-04-04 03:25 AM

0 Likes
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:12 PM . Last Modified: ‎2024-04-04 03:25 AM

Hi Jef,

we rebooted the management card in these four UPSs and we have deleted and discovered again in DCE with this result:

There are two UPSs that DCE recognizes as UPS, the other two appear as SNMP Device. In DCE we can see the sensors of the four UPSs.

But in DCO we can only see the sensors, as external systems of the UPSs that in DCE are recognized as UPS:

 

 

(CID:134025099)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:12 PM . Last Modified: ‎2024-04-04 03:24 AM

0 Likes
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:12 PM . Last Modified: ‎2024-04-04 03:24 AM

Hi Javier,

Strange that they are being discovered as "SNMP device"s (in DCE), (wondering if they are being discovered differently somehow?)

Assuming no hardware/ddf related issue, can you run a quick test by changing the device type to UPS (from SNMP Device).

(in DCE) Right click on one of those "SNMP Device" -> Change Device Type, and then select "UPS" from the list.

after awhile (5 min - 1 hr or so) check your DCO (Unassociated Devices).

Kind regards

(CID:134025119)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:13 PM . Last Modified: ‎2024-04-04 03:24 AM

0 Likes
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:13 PM . Last Modified: ‎2024-04-04 03:24 AM

Hi Jef,

we have changed manually the device type from SNMP Device to UPS and we have still the same problem, we do not see the external system information in DCO after 2 hours.

Regards

(CID:134025199)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:13 PM . Last Modified: ‎2024-04-04 03:24 AM

0 Likes
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:13 PM . Last Modified: ‎2024-04-04 03:24 AM

Hi Javier,

Many thanks for the update - assuming not hardware related issue, wondering perhaps firmware update and maybe new ddf could be an option to tryout.

Kind regards

(CID:134026982)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 10:13 PM . Last Modified: ‎2023-10-22 01:45 AM

0 Likes
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 10:13 PM . Last Modified: ‎2023-10-22 01:45 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore