Procedure to update the Netbotz Wireless Sensors firmware

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Procedure to update the Netbotz Wireless Sensors firmware
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:07 PM . Last Modified: ‎2024-04-07 11:58 PM

0 Likes
1
1037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:07 PM . Last Modified: ‎2024-04-07 11:58 PM

Procedure to update the Netbotz Wireless Sensors firmware

Please find the steps to upgrade the Wireless sensors firmware versions. 

Step 1: Download the wireless firmware File from DCIM support in below link:

https://dcimsupport.apc.com/download/attachments/108827510/netbotzwirelessutilitysetup_v101-03.exe?v...

Step 2: Install the Utility by using an option "Run as Administrator"

 

Remove the Wireless Coordinator from the Netbotz and connect it in the laptop.
Install the appropriate drive for the wireless coordinator to communicate with wireless sensors
Drivers ere available in the Firmware package itself as shown in below snap.

Install the driver and verify that the driver installed properly.

Open the Utility and select the Auto Join and click on OK.
Please make sure all the wireless sensors were switched ON.

Utility will be automatically join all the wireless sensors when Auto join is enabled. Confirm, all the sensors were available in the Network list as shown below

•Browse for the firmware package “NB250_wireless_firmware.zip”.Dont unzip the file.
•Once firmware is loaded to the utility ,you can able to see the current version and available update version.
•Once the devices are ready, click on “Apply”.
•Firmware will start to Upgrade.

Once firmware upgrade is completed, remove the USB coordinator and install it back in Netbotz device.

When update is completed status will be changed to “Done” and Progress will be changed to “Success”.

I hope this helps. 

Regards,

Bala

(CID:122691506)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:08 PM . Last Modified: ‎2023-10-22 03:40 AM

0 Likes
0
1037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:08 PM . Last Modified: ‎2023-10-22 03:40 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore