PS100_Particles sensor

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • PS100_Particles sensor
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:49 AM . Last Modified: ‎2024-04-08 04:23 AM

0 Likes
4
1035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:49 AM . Last Modified: ‎2024-04-08 04:23 AM

PS100_Particles sensor

Hello,

I connected several PS100 Particles sensor for several months.
The measures remain at zero.

Two solutions :

1/ No dust in our datacenter
2/ There is configuration error or bug

 

 

What do you think ?
How can i test the sensor ? Blowing dust on it ?

Thanks you for your help.

Best regards. 

(CID:108827909)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:49 AM . Last Modified: ‎2024-04-08 04:23 AM

0 Likes
0
1035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:49 AM . Last Modified: ‎2024-04-08 04:23 AM

Hi Anthony,

Where do you have the particle sensor placed? As per the document below, it should placed on the floor, or as close as possible to the floor.  You could test it by letting some dust fall in front of the sensor, but do not blow dust on to the sensor.
Make sure the lens is clean in order to ensure the reliability of the sensor. This is also discussed in the document below.

http://www.apcmedia.com/salestools/ASTE-6Z5S83/ASTE-6Z5S83_R0_EN.pdf?sdirect=true

Regards

 

 

 

(CID:108828087)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:49 AM . Last Modified: ‎2024-04-08 04:23 AM

0 Likes
1
1035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:49 AM . Last Modified: ‎2024-04-08 04:23 AM

Hi Anthony,

 

I've not seen these sensors record nothing at all, especially multiple sensors. I did a quick test where I hooked up a sensor to a 570 running 4.5.2 andI took off the plastic side cover that is used for cleaning the lenses:

I then took a pen and ran it from lower left to top to lower right a few times. You can see where the graph shows only small particles to apparently huge ones (the pen) then back again:

Make sure the PS2 type cable is actually connected to port one on the sensor pod as your image shows (ext1) as the particle sensor. As you can see here, I have configured the pod to believe it has 2 particle sensors but only one is connected to port #1:

The port (ext2) that has nothing connected is reporting 0 p/in3 as is happening on your image.  If the sensors are still not showing values on the appliance, first connect to the sensor pod using the shortest possible cable. Then make sure the sensor pod is connected to the appliance directly and use the shortest possible USB cable. You may want to configure all ports to be particle sensors and then connect the sensor to a different port every 30 seconds or so to verify the port is not the issue. If you have other older version 2 sensors you can connect, you may want to also try them to be sure the pod is not faulty.

 

Steve

(CID:108828093)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:49 AM . Last Modified: ‎2024-04-08 04:23 AM

In response to DCIM_Support
0 Likes
0
1035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:49 AM . Last Modified: ‎2024-04-08 04:23 AM

Hello John, Steven

Thanks you for your feedback. I tested, it works from the beginning.

The two sensors wich i tested are positionned on the ground. But if I do not breath dust in front of the sensor, the valor stay at 0 or 1.

I'll think about the positionning of the sensor.

 

Best regards.

(CID:108828642)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:49 AM . Last Modified: ‎2023-10-22 03:31 AM

0 Likes
0
1035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:49 AM . Last Modified: ‎2023-10-22 03:31 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore