Error message when I try to lunch PDU AP8886 via DCE 7.3.1

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Error message when I try to lunch PDU AP8886 via DCE 7.3.1
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:50 AM . Last Modified: ‎2024-04-08 04:23 AM

0 Likes
7
1070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:50 AM . Last Modified: ‎2024-04-08 04:23 AM

Error message when I try to lunch PDU AP8886 via DCE 7.3.1

Hi fellows,

I have the attached error message every time  I try to log into PDU AP8886 via DCE 7.3.1, while I can access the same PDU via web interface and I can modify any thing from web interface, Anyone can help me taking into consideration the following:

1- I have many PDU AP8886 are working normally.

2- I've rebooted this device via webpage and I removed it from DCE then added it again and i still face the same issue.

BR,

Sameeh

(CID:108827950)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:50 AM . Last Modified: ‎2024-04-08 04:22 AM

0 Likes
1
1070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:50 AM . Last Modified: ‎2024-04-08 04:22 AM

Hi Sameeh,

Have you checked the Device Launch Settings in DCE for that device?  
Check FA266820 for more information about this.  
Also, check the PDU Event log to see if it shows any signs of unauthorised SNMP access from the IP address of the DCE.
Finally, check if there are any differences in the configuration of the working and non working PDUs.  

Regards

 

(CID:108827972)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:50 AM . Last Modified: ‎2024-04-08 04:22 AM

In response to DCIM_Support
0 Likes
0
1070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:50 AM . Last Modified: ‎2024-04-08 04:22 AM

Thanks for reply, 1- On the private interface. 2- As I mentioned I can access them via web interface with no problem ( of course when I am connected to the Private LAN). 3- The firmware for all PDUs are v6.1.0. 4- HTTP 5- HTTP 6- Yes the same as other PDUs, Kindly check the attached. 7- Both HTTP and HTTPS, Kindly check the attached. 8- No, Kindly check the attched.

DCE server access.PNG

Device Lunch settings.PNG

My PC Internet Options.PNG

PDU web access Configuration.PNG

(CID:108828005)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:50 AM . Last Modified: ‎2024-04-08 04:22 AM

0 Likes
3
1070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:50 AM . Last Modified: ‎2024-04-08 04:22 AM

Sameeh,

1) Is the device on the public or private interface of the StruxureWare Data Center Expert server?

2) If they are on the public interface, can you type the IP address in your Internet Explorer web address bar and navigate to the device?

3) What firmware revision are the Network Management Cards that are installed within the PDUs?

4) Is the device using HTTP or HTTPS?  

5) If using HTTPS, on the devices web interface, what is the minimum protocol version set to under the web settings for HTTPS?

6) Have you verified the device launch settings by right-clicking on the device and selecting Device Launch Settings?

7) What web settings are enabled on the server, in regards to HTTP/HTTPS (System Menu > Server Administration Settings > Server Access > Web Server Tab)?

😎 Are any proxies enabled on your computer (Control Panel > Internet Options > Connections Tab > LAN Settings)?

Regards,

Cory

(CID:108827973)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:50 AM . Last Modified: ‎2024-04-08 04:22 AM

In response to DCIM_Support
0 Likes
0
1070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:50 AM . Last Modified: ‎2024-04-08 04:22 AM

Thanks for reply, 1- On the private interface. 2- As I mentioned I can access them via web interface with no problem ( of course when I am connected to the Private LAN). 3- The firmware for all PDUs are v6.1.0. 4- HTTP 5- HTTP 6- Yes the same as other PDUs, Kindly check the attached. 7- Both HTTP and HTTPS, Kindly check the attached. 8- No, Kindly check the attched.

DCE server access.PNG

Device Lunch settings.PNG

My PC Internet Options.PNG

PDU web access Configuration.PNG

(CID:108828000)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:50 AM . Last Modified: ‎2024-04-08 04:22 AM

In response to DCIM_Support
0 Likes
0
1070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:50 AM . Last Modified: ‎2024-04-08 04:22 AM

Sameeh, Please ensure that the PDU is the only device on the network that has that IP address. You can need to test this by trying to ping the IP address from a computer on the public network. If that is no the issue, try upgrading the firmware on one of the PDUs to the most recent version to see if it improves launching to the device. What are the public and private IP address schemes? They should be on two completely different networks, such as the public network is 10.X.X.X and the private is 192.X.X.X. This ensures that the server will connect through the correct interface when attempting to launch to the web interface. The private network needs to be a completely isolated network, except for a connection to the Data Center Expert server. Regards, Cory

(CID:108828081)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:50 AM . Last Modified: ‎2024-04-08 04:22 AM

In response to DCIM_Support
0 Likes
0
1070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:50 AM . Last Modified: ‎2024-04-08 04:22 AM

Hi Cory, Thanks for your reply, I've solved the problem yesterday ans it was as following: - The DHCP is enabled in Private LAN port and the client gave me a range of (xx.xx.xx.40 to xx.xx.xx.137) and the subnetmask is ( 255.255.255.0). - The A/M PDUs IP adresses were ( xx.xx.xx.128-135), when I increased the range of DHCP IPs to (xx.xx.xx.150) I was able to lauch then them via DCE client. - The A/M IP addrese are suposed to be in the same range of DCE server DHCP, but I don't know why I couldn't reach them via DCE server, but anyway the problem has been resolved now. I have two more querries: 1- Do you have concern if the Puplic IP address is ( 20.100.221.90) and the Private IP address is (20.100.212.90) while the subnet mask is (255.255.255.0) I think in this case the Puplic and Private network will be isolated. 2- The ask me to disable the DHCP after I finish the configuration, what is the proper wat to do this, to access each device via DCE client and change the IP address to be manual and set the IP address then after I finish all device I can disable the DHCP or disable the DHCP then loginto each device ?. BR, Sameeh

(CID:108828123)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:50 AM . Last Modified: ‎2023-10-22 02:03 AM

0 Likes
0
1070
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:50 AM . Last Modified: ‎2023-10-22 02:03 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore