Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Netbotz 750 fails to boot

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Netbotz 750 fails to boot
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
Avila.Andres
Avila.Andres
Explorer

Posted: ‎2023-05-18 06:42 AM

0 Likes
11
4355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-18 06:42 AM

Netbotz 750 fails to boot

Hey guys, trying to boot the app on a netbotz 750 I keep getting boot errors, they look like this

 

[ OK ] Reached target Local File Systems (Pre).
[ OK ] Reached target Containers.
Mounting /var/volatile...
Starting udev Kernel Device Manager...
[ OK ] Mounted /var/volatile.
Starting Load/Save Random Seed...
[ OK ] Started udev Kernel Device Manager.
[ OK ] Started Load/Save Random Seed.
[ OK ] Started Flush Journal to Persistent Storage.
[ OK ] Started udev Coldplug all Devices.
[ OK ] Found device /dev/ttyS0.
[ OK ] Found device /dev/mmcblk0p9.
[ OK ] Found device /dev/mmcblk0p10.
[ OK ] Listening on Load/Save RF …itch Status /dev/rfkill Watch.
Mounting /opt/netbotz...
Mounting /mnt9...
[FAILED] Failed to mount /opt/netbotz.
See 'systemctl status opt-netbotz.mount' for details.
[DEPEND] Dependency failed for Local File Systems.
[ OK ] Mounted /mnt9.
[ OK ] Stopped Forward Password R…uests to Wall Directory Watch.
[ OK ] Reached target Timers.
ive root password for maintenance

 

How can I proceed to reformat the Netbotz and update the firmware, old data does not need to be saved.

 

Thanks

Labels
  • Labels:
  • NetBotz
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 11
Avila.Andres
Avila.Andres
Explorer

Posted: ‎2023-05-18 06:47 AM

0 Likes
3
4354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-05-18 06:47 AM

when running the systemctl status I get this prompt

 

● opt-netbotz.mount - /opt/netbotz
Loaded: loaded (/etc/fstab; generated)
Active: failed (Result: exit-code) since Wed 2023-03-01 15:18:08 EST; 2min 1>
Where: /opt/netbotz
What: /dev/mmcblk0p10
Docs: man:fstab(5)
man:systemd-fstab-generator(8)

Mar 01 15:18:06 snarc-soca9 systemd[1]: Mounting /opt/netbotz...
Mar 01 15:18:08 snarc-soca9 mount[213]: mount: /opt/netbotz: wrong fs type, bad>
Mar 01 15:18:08 snarc-soca9 systemd[1]: opt-netbotz.mount: Mount process exited>
Mar 01 15:18:08 snarc-soca9 systemd[1]: opt-netbotz.mount: Failed with result '>
Mar 01 15:18:08 snarc-soca9 systemd[1]: Failed to mount /opt/netbotz.
lines 1-13/13 (END)

Reply

Link copied. Please paste this link to share this article on your social media post.

Tafadzwa
Tafadzwa
Contributor

Posted: ‎2023-09-26 12:57 AM

In response to Avila.Andres
0 Likes
1
4128
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-09-26 12:57 AM

Hi @Avila.Andres 

 

I am having the same problem with my NetBotz 755.

 

Did you eventually find a solution for this?

 

I engaged with Technical support but all the methods they suggested did not work for me.

 

Thank you!

Connecting Devices!
Reply

Link copied. Please paste this link to share this article on your social media post.

tjlaw
tjlaw Mentor
Mentor

Posted: ‎2023-09-29 07:35 PM

In response to Tafadzwa
0 Likes
0
4111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-09-29 07:35 PM

Hi, 

 

You may try to follow up closely with the technical support team for a possible solution. Try to provide any logs or file requested by the technical support. 

 

BR

 

TJ

Reply

Link copied. Please paste this link to share this article on your social media post.

Fgrieco
Fgrieco
Contributor

Posted: ‎2023-11-06 12:05 PM

In response to Avila.Andres
0 Likes
0
4029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-11-06 12:05 PM

Hi, Andrés. 

We have the same problem on a Netbotz 755. 

It seems that the file system is damage. 

Do anyone have the maintenence root password?

Support said that we have to run a file check command but it's imposible to run anything without that root passoword. 

Thanks

 

dgt_error_netbotz_2.png

Reply

Link copied. Please paste this link to share this article on your social media post.

SonNG
SonNG
Explorer

Posted: ‎2024-10-10 09:11 PM

0 Likes
5
3245
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-10 09:11 PM

I am also facing the same problem with Netbotz 750. Has anyone solved the above error? Please help me how to solve it. Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Tafadzwa
Tafadzwa
Contributor

Posted: ‎2024-10-13 11:29 PM

In response to SonNG
2 Likes
4
3210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-13 11:29 PM

Hi @SonNG 

 

I faced this issue twice on different instances, the second time was on a NetBotz 750 and even after following all recommended steps to fix this, I could not succeed. I ended up returning the unit to SE and claimed under warranty for a replacement unit.

 

Please get in touch with your local technical support team.

 

Regards,

 

Tafadzwa.

Connecting Devices!
Reply

Link copied. Please paste this link to share this article on your social media post.

Fgrieco
Fgrieco
Contributor

Posted: ‎2024-10-14 12:58 AM

0 Likes
0
3197
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-14 12:58 AM

It would be a good idea to have some mechanism to be able to format and replace the entire contents of the netboz flash from scratch, because this problem is frequent and there is no way for the user to solve it and it always ends in the replacement of the equipment. Thanks. 

Reply

Link copied. Please paste this link to share this article on your social media post.

SonNG
SonNG
Explorer

Posted: ‎2024-10-16 01:50 AM

In response to Tafadzwa
0 Likes
3
3170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-16 01:50 AM

Hi @Tafadzwa

 

Can you share the recommended steps to fix the above issue, I am currently waiting for a new SE device warranty but it will take a long time. So I want to do something temporary with this Netbotz device that is having this issue.

 

Regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

Tafadzwa
Tafadzwa
Contributor

Posted: ‎2024-10-17 12:04 AM

In response to SonNG
0 Likes
2
3151
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-17 12:04 AM

Hi @SonNG 

 

Follow the link below to see the steps SE suggested for fixing the issue with the NetBotz.

 

https://www.apc.com/us/en/faqs/FA373416/

 

Regards,

 

Tafadzwa.

Connecting Devices!
Reply

Link copied. Please paste this link to share this article on your social media post.

Fgrieco
Fgrieco
Contributor

Posted: ‎2024-10-17 12:27 AM

In response to Tafadzwa
0 Likes
1
3141
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-17 12:27 AM

Hi Tafadzwa. 

The process of the link is for reset root password and is no applicable to the fail mentioned by @Avila.Andres . When this fails occurs, nothing at all works, because the OS doesn't load. So as I mentioned, we need some process to format an reload the entire flash memory to fix the problem. Regards

Reply

Link copied. Please paste this link to share this article on your social media post.

Tafadzwa
Tafadzwa
Contributor

Posted: ‎2024-10-17 01:48 AM

In response to Fgrieco
0 Likes
0
3138
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-17 01:48 AM

Hi @Fgrieco ,

 

That is correct however that was the procedure I was asked to execute by the SE Technical Support after my NetBotz failed however the procedure did not resolve the problem as I could not access the NetBotz via Serial.

I returned the NetBotz to SE.

 

Regards,

 

Tafadzwa.

Connecting Devices!
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore