Posted: 2023-03-15 01:44 AM
Hi !
I have a problem with a Netbotz 250 and 150 Pods, it seems that dry contacts and temp/humid sensors that are from the 150 Pods will not appear under the Relay Output Abnormal state or Threshold Violation tabs.
The only Dry contacts or Temp/Humid that appears in the Relay Output Abnormal state or Threshold Violation is the ones that are inserted in the Netbotz 250.
None of the Dry contacts and Thresholds that are violated in the 150 Pods affects the Output relay.
Is this a bug in Firmware 7.0.6 ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-05 06:55 PM
Hi @Hamid1,
This issue can be found in the known issues of the NetBotz 250A release notes:
"Sensors connected to a Sensor Pod 150 can be mapped for the beacon only, and not for the switched
outlet or output relay. Door switch sensors connected to Door 1 or Door 2 ports can be mapped for the
beacon only, and not for switched outlet or output relay. Alarm mapping is not available for any wireless
sensors."
Regards,
Cory