Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

NetBotz 570 end of line

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • NetBotz 570 end of line
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
Mike-Sutton
Mike-Sutton
Troubleshooter

Posted: ‎2020-11-04 01:32 AM

2 Likes
5
3859
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-04 01:32 AM

NetBotz 570 end of line

Hi,

 

We have recived confirmation the Botz 570 along with others are being replaced with the 750. the problem here is we use Sea Level and GSM devices that work with 570 etc, but the 750 cannot utilize the USB ports will this be incorperated into the next FW revision for the 750 or not?

 

TIA

 

Mike

Labels
  • Labels:
  • NetBotz
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Rick_O
Rick_O Troubleshooter
Troubleshooter

Posted: ‎2020-11-18 11:19 AM

0 Likes
0
3764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-18 11:19 AM

@Mike-Sutton 

 

Thank you for the question.

 

First to answer the question about SMS support and Sea Level support. These features will not be in our next major release which is due sometime in Q1 of 2021, but they are on the backlog and we are hoping to add them later in 2021 once resources can be assigned.

 

When it comes to SMS messages there's actually a solution available now that doesn't involve having the customer install an email to SMS server. Many ISP's actually offer email to SMS as part of their service. This is not an exhaustive list, but shows many carriers and what email addresses to send to in order to translate it to SMS. https://support.teamunify.com/en/articles/227-email-to-sms-gateway-list

 

Thanks,
Rick

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2020-11-04 11:49 AM

0 Likes
2
3844
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-04 11:49 AM

Hi @Mike-Sutton ,

 

That is correct. The version 3 appliances will be out of circulation at the end of 2020. For now consider additional sensor pods and dry contact sensors for the SeaI/O and an email to SMS service for the GSM modem.

Cannot comment about when the 250 or 750 appliances will support these unfortunately. Hopefully someone in the forum can share more info. 

 

Kevin

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Mike-Sutton
Mike-Sutton
Troubleshooter

Posted: ‎2020-11-09 02:27 AM

In response to Anonymous user
1 Like
1
3821
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-09 02:27 AM

Hi Kevin,

I am aware of the work arounds but when you are monitoring 30+ dry contacts individual sensors are not cost effective and not a lot of clients have email to SMS servers.

Could someone from platform comment please

 

Cheers,

 

Mike

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-11-12 03:41 AM

In response to Mike-Sutton
0 Likes
0
3812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-12 03:41 AM

Thanks for the update and quick reply. I'll be sure to keep an eye on this thread Upsers

  • Tags:
  • answer
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Rick_O
Rick_O Troubleshooter
Troubleshooter

Posted: ‎2020-11-18 11:19 AM

0 Likes
0
3765
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-18 11:19 AM

@Mike-Sutton 

 

Thank you for the question.

 

First to answer the question about SMS support and Sea Level support. These features will not be in our next major release which is due sometime in Q1 of 2021, but they are on the backlog and we are hoping to add them later in 2021 once resources can be assigned.

 

When it comes to SMS messages there's actually a solution available now that doesn't involve having the customer install an email to SMS server. Many ISP's actually offer email to SMS as part of their service. This is not an exhaustive list, but shows many carriers and what email addresses to send to in order to translate it to SMS. https://support.teamunify.com/en/articles/227-email-to-sms-gateway-list

 

Thanks,
Rick

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

harleywatsan
harleywatsan
Explorer

Posted: ‎2023-01-28 06:35 AM

0 Likes
0
2309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-28 06:35 AM

I appreciate the update and prompt response. I'll make sure to follow this thread. Vn Video Editor For PC 

Armoury Crate 

Evone Executor

Blox Fruit Script

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore