New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
SDCE Client on Windows 2012 R2 Remote Desktop Server - Unable to Start
EcoStruxure IT Forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-2211:47 PM
SDCE Client on Windows 2012 R2 Remote Desktop Server - Unable to Start
We are unable to get the DCE client to execute on our Remote Desktop Server, even by users with admin rights all users get the following;
Invalid Configuration Location
The configuration area at 'C:\Users\[Username]\.isxc\7.9.2\configuration' is not writable. Please choose a writable location using the '-configuration' command line option.
Troubleshooting steps already taken;
There is plenty of free disk space on C:\
Using the '-configuration' parameter to point at another location gives the exact same message as above just to the new path.
Server was put into 'Change User /Install' mode.
Are there any special considerations or permissions needed to run DCE in a Remote Desktop Server environment?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-3005:11 PM
For anyone else that may come across this issue we believe we have found the problem. There is a version of the Oracle Java Runtime Environment already on server where we have installed the DCE Full Client.
Seems that the behaviour of DCE Client is that if you have no Java Runtime environment at all that it copies files from it's own installation path (probably from within .jar Libraries?) BUT if you have another Runtime it tries to source these files from there and fails given version 7.9.2 uses OpenJDK Java version: Adoptium 8u345b01