NetBotz 450 and sensor pod NetBotz 150

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • NetBotz 450 and sensor pod NetBotz 150
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:54 AM . Last Modified: ‎2024-04-09 12:08 AM

0 Likes
5
1359
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:54 AM . Last Modified: ‎2024-04-09 12:08 AM

NetBotz 450 and sensor pod NetBotz 150

Hello.

After sensor change, on netbotz sensor pod 150, i try connect 450 and 150, but after connect, all icons in Netbotz advanced view go grey and all sensor reading status change to N/A.

(CID:106204277)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:54 AM . Last Modified: ‎2024-04-09 12:08 AM

0 Likes
2
1361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:54 AM . Last Modified: ‎2024-04-09 12:08 AM

Dear Leonid,

As far as I know, the Netbotz Sensors will be shown N/A while the Netbotz A-Link establishes the communication to the Appliance after the sensors are attached. The Sensors will show the values once the appliance senses the Pods sensors after some time. Do these sensors showing the values after some time? If so, its normal. 

If the sensors are still showing N/A on the Advance View, then I request you to do the following:

Please make sure that the Sensor Pod is connected as per the A-Link Communication instructions as per user manual. If possible, Restart the appliance with the sensors and see if the values are shown on the advance view. 

Please make sure that the Botzware of the appliance is the latest version. 

If the problem remains same, please provide the following details:

How many sensors pods are connected to the appliance? 

Is this a new installation or had it been working before? 

Are there any sensors connected to the appliance? If so, are they showing the sensor values?

Botzware version. 

 

(CID:106204300)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:54 AM . Last Modified: ‎2024-04-09 12:08 AM

In response to DCIM_Support
0 Likes
0
1361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:54 AM . Last Modified: ‎2024-04-09 12:08 AM

Hello,

 

After appliance restart system not found 150 sensor pod, in Advanced view all sensor pods icons go to grey, sensors  reading change N/A (only a-link bus power and ethernet link stay normal) and system start send alerts “Sensor unplugged”.

Netbotz 450 -> (alink in) Netbotz 150 (alink out)-> (alink in) AP9520 -> (alink out)terminator. If i disconnect Netbotz 150 all work normal.

This system works 6 months normal to change sensors (It planned to add two Netbotz 150 and change many sensor place). Used only APC sensors.

Now in appliance Netbotz 450 connected 3 AP9335TH, 3 NBES0301, Leak rope all showing values normal. Only after connect 150 in alink all sensors go N/A, it does not matter whether the sensors are connected and 150 power to it, the result is same.

Lates version 4.5.1.

Best regards

Leonid Ossul

(CID:106204722)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:54 AM . Last Modified: ‎2024-04-09 12:08 AM

In response to DCIM_Support
0 Likes
0
1361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:54 AM . Last Modified: ‎2024-04-09 12:08 AM

Dear Leonid,

Thanks for your reply. 

With a NetBotz 450, you can cascade up to a combined total of two NetBotz Rack Sensor Pod 150s
(NBPD0150) and NetBotz Room Sensor Pod 155s (NBPD0155), plus up to a combined total of eight
Temperature Sensors with Digital Display (AP9520T) and Temperature/Humidity Sensors with Digital
Display (AP9520TH).

If possible, please verify if the sensor Pod(NBPD0150) is cascaded as shown below. 

Please also make sure that the device ID is set correctly for the AP9520TH Display sensors. AP9520TH sensor can not decides its ID/Address on the A-Link bus unless we manually set the switch settings. 

I think that AP9520TH dipswitches are probably the cause of the problem. I suggest you to follow the guidelines for dipswitch settings that are located in the manual of AP9520TH and make sure that the following is noted:

 Make sure that before connecting the sensors that the dipswitches are set.  Connecting sensors with the same address will probably cause the sensor not to show correctly.

Make sure that standard Cat5 cables are being used to connect each sensor.

I hope this helps. 

Regards,

Bala

(CID:106204723)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:54 AM . Last Modified: ‎2024-04-09 12:08 AM

0 Likes
0
1362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:54 AM . Last Modified: ‎2024-04-09 12:08 AM

I checked all the connections of the procedure and settings. Effect is still there. Apparently there is a physical deffekt. The warranty period is over, if the point of having to send checks to the nearest APC service?

(CID:106205317)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:54 AM . Last Modified: ‎2023-10-31 11:24 PM

0 Likes
0
1361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:54 AM . Last Modified: ‎2023-10-31 11:24 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore