Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Incorrect values for a device (UPS) in EcoStruxure IT

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Incorrect values for a device (UPS) in EcoStruxure IT
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:20 PM . Last Modified: ‎2024-04-04 02:35 AM

0 Likes
18
3181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:20 PM . Last Modified: ‎2024-04-04 02:35 AM

Incorrect values for a device (UPS) in EcoStruxure IT

(CID:134030464)

Labels
  • Labels:
  • IT Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:22 PM . Last Modified: ‎2024-04-04 02:34 AM

0 Likes
2
3181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:22 PM . Last Modified: ‎2024-04-04 02:34 AM

Dear John Beck,

Hence, there is no bug in the gateway software, just need to keep the firmware of the devices up to date 😀.

Thanks for the good feedback.

With respect.

(CID:134030790)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 18
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:20 PM . Last Modified: ‎2024-04-04 02:35 AM

0 Likes
0
3181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:20 PM . Last Modified: ‎2024-04-04 02:35 AM

Dear John Beck,

Please explain your problem in more detail, show a couple of screenshots. And then you will help faster and better 😀.

With respect.

(CID:134030474)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:20 PM . Last Modified: ‎2024-04-04 02:35 AM

0 Likes
0
3181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:20 PM . Last Modified: ‎2024-04-04 02:35 AM

The following are screenshots with regards to a temperature probe and with regards to the date of our UPS and its batteries:

 

This is from EcoStruxure IT:

 

This is from EcoStruxure IT:

This is from the Network Management Card on the UPS itself:

So the ambient temperature isn't 170.6 degrees F.

 

This is from EcoStruxure IT:

 

This is from the Recertification Report of the UPS from a Schneider Electric Technician:

 

In fact, I was onsite in 2013 when this UPS was started. So it isn't 7.38 years old and the batteries aren't 17.45 years old.

 

(CID:134030487)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:20 PM . Last Modified: ‎2024-04-04 02:35 AM

0 Likes
0
3181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:20 PM . Last Modified: ‎2024-04-04 02:35 AM

I did put in screenshots - see the five (5) I put in above.

(CID:134030517)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:20 PM . Last Modified: ‎2024-04-04 02:35 AM

0 Likes
0
3181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:20 PM . Last Modified: ‎2024-04-04 02:35 AM

Excellent, thanks for the detailed screenshots.

Please tell us more about your Smart-UPS VT 30kVA:

  • the firmware version of the UPS;
  • the firmware version of the NMC.

With respect.

(CID:134030524)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:21 PM . Last Modified: ‎2024-04-04 02:35 AM

0 Likes
0
3181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:21 PM . Last Modified: ‎2024-04-04 02:35 AM

The Versions are as follows:

 

 

(CID:134030690)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:21 PM . Last Modified: ‎2024-04-04 02:35 AM

0 Likes
0
3181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:21 PM . Last Modified: ‎2024-04-04 02:35 AM

The Firmware Versions of the NMC were as follows:

 

APC Boot Monitor v1.0.1 - August 3, 2009

 

APC OS (AOS) v5.1.3 - May 4, 2010

 

SUMX v5.1.3 - May 4, 2010

(CID:134030694)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:21 PM . Last Modified: ‎2024-04-04 02:35 AM

0 Likes
0
3181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:21 PM . Last Modified: ‎2024-04-04 02:35 AM

I just upgraded the NMC and the new versions are as follows:

 

(CID:134030699)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:21 PM . Last Modified: ‎2024-04-04 02:34 AM

0 Likes
0
3181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:21 PM . Last Modified: ‎2024-04-04 02:34 AM

Dear John Beck,

Ok, very thanks for the information.

After updating the firmware of the NMC, has something changed in the gateway software? Or all also you have the above bugs?

With respect.

(CID:134030720)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:21 PM . Last Modified: ‎2024-04-04 02:34 AM

0 Likes
0
3181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:21 PM . Last Modified: ‎2024-04-04 02:34 AM

This is very strange, since I, for example, have the same gateway software, the same NMC firmware, but I have a Smart-UPS VT 40kVA. And I have temperature readings in Celsius.

I do not have the above bugs, i.e. in the gateway software I have the right temperature, the correct age of the UPS and batteries:

and

With respect.

(CID:134030735)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:21 PM . Last Modified: ‎2024-04-04 02:34 AM

0 Likes
0
3181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:21 PM . Last Modified: ‎2024-04-04 02:34 AM

Then I re-ran the discover and the Temperature Probe Temperature was correct but the Battery Age and the UPS Age were still wrong - see the following:

 

(CID:134030749)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:21 PM . Last Modified: ‎2024-04-04 02:34 AM

0 Likes
0
3181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:21 PM . Last Modified: ‎2024-04-04 02:34 AM

Ok, then please show us two screenshots from NMC of this UPS:

  • UPS Status -> Intelligence Module
  • Configuration -> UPS -> Last Battery Replacement

What do you have there?

With respect.

(CID:134030765)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:21 PM . Last Modified: ‎2024-04-04 02:34 AM

0 Likes
0
3181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:21 PM . Last Modified: ‎2024-04-04 02:34 AM

See below for the Intelligence Module and Last Battery Replacement:

 

 

I will change the "2001" to "2011"

(CID:134030777)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:22 PM . Last Modified: ‎2024-04-04 02:34 AM

0 Likes
2
3182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:22 PM . Last Modified: ‎2024-04-04 02:34 AM

Dear John Beck,

Hence, there is no bug in the gateway software, just need to keep the firmware of the devices up to date 😀.

Thanks for the good feedback.

With respect.

(CID:134030790)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:22 PM . Last Modified: ‎2024-04-04 02:34 AM

In response to DCIM_Support
0 Likes
0
3181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:22 PM . Last Modified: ‎2024-04-04 02:34 AM

So, either I as the customer, or an APC (Schneider Electric) Field Engineer needs to check this during the Semi-Annual or Annual PM's that are performed on this UPS (such as the Annual PM we had last week on Wednesday 9/5/18).

(CID:134030854)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:22 PM . Last Modified: ‎2024-04-04 02:34 AM

In response to DCIM_Support
0 Likes
0
3181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:22 PM . Last Modified: ‎2024-04-04 02:34 AM

Yes, of course, besides the firmware of your UPS (not the NMC) is also very outdated. But only APC (Schneider Electric) Field Engineer can update the firmware of the UPS.

You as a customer should and can keep it under control.

With respect.

(CID:134030950)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:22 PM . Last Modified: ‎2024-04-04 02:34 AM

0 Likes
0
3181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:22 PM . Last Modified: ‎2024-04-04 02:34 AM

It's good now - as follows:

 

(CID:134030797)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:22 PM . Last Modified: ‎2024-04-04 02:34 AM

0 Likes
0
3181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:22 PM . Last Modified: ‎2024-04-04 02:34 AM

And UPS Age also:

Manufacture Date 04/26/11 = 7.38 years.

(CID:134030802)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 11:22 PM . Last Modified: ‎2023-10-22 02:44 AM

0 Likes
0
3181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 11:22 PM . Last Modified: ‎2023-10-22 02:44 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore