Posted: 2020-07-06 01:13 AM . Last Modified: 2024-04-02 11:18 PM
Does NBES0201 (APC NetBotz Particle Sensor PS100) still is supported by some netbotz appliance or sensor pod?
According to installation manual, it needs a 6 Pin port, and as afar as i know there is no such port available on any current sensor port.
(CID:154403198)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-06 01:13 AM . Last Modified: 2024-04-02 11:18 PM
Victor Juarez Velazquez,
There is no solution that can be sold for the NBES0201 particle sensor. It required a V2 appliance or a Sensor Pod 120, both of which are end-of-sale and end-of-support. There is no current NetBotz Solution that can be sold for a particle sensor.
You may be able to find a third party sensor that can communicate via: 4-20mA, 0-5V, or dry contacts; but I have not looked into a possible integration that way.
Regards,
Cory
(CID:154403201)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-06 01:13 AM . Last Modified: 2024-04-02 11:18 PM
Victor Juarez Velazquez,
There is no solution that can be sold for the NBES0201 particle sensor. It required a V2 appliance or a Sensor Pod 120, both of which are end-of-sale and end-of-support. There is no current NetBotz Solution that can be sold for a particle sensor.
You may be able to find a third party sensor that can communicate via: 4-20mA, 0-5V, or dry contacts; but I have not looked into a possible integration that way.
Regards,
Cory
(CID:154403201)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-06 01:13 AM . Last Modified: 2024-04-02 11:18 PM
So clear
(CID:154403508)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-06 01:13 AM . Last Modified: 2023-10-22 01:55 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.