Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

DCE Server not backing up

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCE Server not backing up
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:24 PM . Last Modified: ‎2024-04-05 12:14 AM

0 Likes
8
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:24 PM . Last Modified: ‎2024-04-05 12:14 AM

DCE Server not backing up

I have an issue with DCE where I am unable to back up to a remote location. Having looked at the version its currently on and the version of the last backup, it doesn’t appear to have backed up since upgrading from 7.3.1 to 7.4.3.

 

Server Version

Last backup

I cant perform the upgrade without being able to back up the environment first as there have been a couple of additions since the last backup has ran.

(CID:130093698)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:24 PM . Last Modified: ‎2024-04-05 12:14 AM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:24 PM . Last Modified: ‎2024-04-05 12:14 AM

 

Some things to you may want to check:

Does dce test mounting to the shared folder work?

Are you using windows smb share of nfs share?

Also, contact your local tech support so they can guide you over the phone on some of the steps.

(CID:130093706)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:24 PM . Last Modified: ‎2024-04-05 12:14 AM

0 Likes
2
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:24 PM . Last Modified: ‎2024-04-05 12:14 AM

Hello Mr. Parks, I have a similar issue becasu I can´t mount the remote windows shared folder, is it your situation? If so, please check your server logs for a "cifs mount error" I´m not sure if the error code was -112, I search for that error and the solution was enable the SMB 1.0/CIFS windows feature.... Good luck!

Regards,

Note: My Windows 10 is a Spanish version.

(CID:130093709)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:24 PM . Last Modified: ‎2024-04-05 12:14 AM

In response to DCIM_Support
0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:24 PM . Last Modified: ‎2024-04-05 12:14 AM

Thank you for the reply,

We have disabled SMBv1 so this could be the reason why it has stopped working. 

re-enabling SMBv1 is not really an option though due to the vulnerabilities.

Is there a way for DCE to use SMBv2?

(CID:130093716)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:24 PM . Last Modified: ‎2024-04-05 12:14 AM

In response to DCIM_Support
0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:24 PM . Last Modified: ‎2024-04-05 12:14 AM

Hello Mr. Parks, 

I don´t know in new version, I left the question for the friends of the community..

 

Best regards...

(CID:130093720)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:24 PM . Last Modified: ‎2024-04-05 12:14 AM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:24 PM . Last Modified: ‎2024-04-05 12:14 AM

Thank you for your reply, 😀

when running the Test Mounting it is unable to mount.

after seeing the reply below, it appears this may be because of SMBv1 being disabled.

(CID:130093718)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:25 PM . Last Modified: ‎2024-04-05 12:14 AM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:25 PM . Last Modified: ‎2024-04-05 12:14 AM

Yea, that might be the most likely case, hence earlier question in the comment.

Now back to the topic on running backup first, several alternatives:

  • Backup to NFS shared folder instead of windows (SMB)
  • If this is a physical DCE, connect to the 2nd nic(apc lan), instead of 1st nic (public lan)with a laptop to run, with SMBv1 temporarily enabled
  • If this is a DCE VM, do a VM snapshot.

Also, appreciate if you can spend a bit of time to add a feature request on SMBv2 support, so we can add your details into this particular request on DCE support for SMBv2.

Feature requests

 

(CID:130093877)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:25 PM . Last Modified: ‎2024-04-05 12:14 AM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:25 PM . Last Modified: ‎2024-04-05 12:14 AM

Dear Martin Parks,

Have you been able to solve your problem, or do you have any more questions about it?

With respect.

(CID:130680485)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:25 PM . Last Modified: ‎2023-10-22 01:20 AM

0 Likes
0
1385
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:25 PM . Last Modified: ‎2023-10-22 01:20 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore