StruxureWare Portal can't show anything?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • StruxureWare Portal can't show anything?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:22 PM . Last Modified: ‎2024-04-05 12:15 AM

0 Likes
11
1626
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:22 PM . Last Modified: ‎2024-04-05 12:15 AM

StruxureWare Portal can't show anything?

After install StruxureWare Portal. I try to access http://localhost:8080 via IE. But don't show more information except this thing below.

When I click 【sign in】, I just show blank interface below.

It do not show error information. How do I Troubleshoot ?

I use IE , FIREFOX , and Google to have a test below. But all show same things.

IE version 11.1106.10586.0 , 

Firefox  v 53.0.2 (32 bit),

Google Chrome Version 52.0.2743.116 m

(CID:130093629)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:23 PM . Last Modified: ‎2024-04-05 12:15 AM

0 Likes
7
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:23 PM . Last Modified: ‎2024-04-05 12:15 AM

Dear Yonker Wang,

Tell us, is there any other software installed on the server running SxW Portal software?

Are the physical resources of the server sufficient?

Additionally check the output of these two commands in the console of your SxW Portal server:

sc query Tomcat7
sc query postgresql-x64-9.1

What is the result, is everything normal?

Still, based on my experience, I recommend that you perform a clean installation of the latest SxW Portal 1.3.7 software.

I hope this helps you.

With respect.

(CID:130093992)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:22 PM . Last Modified: ‎2024-04-05 12:15 AM

0 Likes
1
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:22 PM . Last Modified: ‎2024-04-05 12:15 AM

Hi 

Try changing your compatibility settings, untick the box and it will display 

 

 

Martin

(CID:130093647)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:23 PM . Last Modified: ‎2024-04-05 12:15 AM

In response to DCIM_Support
0 Likes
0
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:23 PM . Last Modified: ‎2024-04-05 12:15 AM

Hi Martin ,

I untick the box , follow what you describe .But don't show more information below.

When I click 【sign in】 ,It always show blank interface below.

 

How do I Troubleshoot  now?

(CID:130093896)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:23 PM . Last Modified: ‎2024-04-05 12:15 AM

0 Likes
7
1630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:23 PM . Last Modified: ‎2024-04-05 12:15 AM

Dear Yonker Wang,

Tell us, is there any other software installed on the server running SxW Portal software?

Are the physical resources of the server sufficient?

Additionally check the output of these two commands in the console of your SxW Portal server:

sc query Tomcat7
sc query postgresql-x64-9.1

What is the result, is everything normal?

Still, based on my experience, I recommend that you perform a clean installation of the latest SxW Portal 1.3.7 software.

I hope this helps you.

With respect.

(CID:130093992)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:23 PM . Last Modified: ‎2024-04-05 12:15 AM

In response to DCIM_Support
0 Likes
0
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:23 PM . Last Modified: ‎2024-04-05 12:15 AM

Hi Engineer,

Thanks for your help~! 

Yes, I install the latest SxW Portal 1.3.7 software. Reinstall more than three times. But abnormal phenomenon is still the same.

Physical resources of my server below.

I check the services . they are all normal .


I can't know how to Troubleshoot now.

(CID:130094195)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:23 PM . Last Modified: ‎2024-04-05 12:14 AM

In response to DCIM_Support
0 Likes
0
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:23 PM . Last Modified: ‎2024-04-05 12:14 AM

Does your windows server on which portal is installed also have a java 8 installation on it? Portal 1.3.x has its own java 7.x installation, if another/newer java version is present on the host the portal may not work properly.

If there is a java8 install on this server, remove java8 and re-install portal.

GregS

(CID:130094238)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:23 PM . Last Modified: ‎2024-04-05 12:14 AM

In response to DCIM_Support
0 Likes
0
1628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:23 PM . Last Modified: ‎2024-04-05 12:14 AM

Dear Yonker Wang,

Greg Sterling correctly noted about the JVM version: for example, you can read about it in topics:

  • SxW Portal: Tomcat Error – prunsrv.c Failed creating java jvm.dll)

Try and report the result.

With respect.

(CID:130094260)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:23 PM . Last Modified: ‎2024-04-05 12:14 AM

In response to DCIM_Support
0 Likes
0
1628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:23 PM . Last Modified: ‎2024-04-05 12:14 AM

Thanks for your help.

After I uninstall JAVA 8 , It's normal now.

Regards,

Yonker wang

(CID:130095459)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:23 PM . Last Modified: ‎2024-04-05 12:14 AM

In response to DCIM_Support
0 Likes
0
1628
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:23 PM . Last Modified: ‎2024-04-05 12:14 AM

Dear Yonker Wang,

It is not necessary to uninstall the latest JVM from your server (for security reasons, for example). This means, that on the server you can have multiple versions of the JVM.

For the correct working of the SxW Portal, you only need to specify which version of the JVM to use. How to do it you can read in my post SxW Portal: Tomcat Error – prunsrv.c Failed creating java (jvm.dll).

With respect.

(CID:130095536)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:23 PM . Last Modified: ‎2024-04-05 12:14 AM

In response to DCIM_Support
0 Likes
0
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:23 PM . Last Modified: ‎2024-04-05 12:14 AM

I have uninstalled JAVA 8, The problem has been solved. I review  SxW Portal: Tomcat Error – prunsrv.c Failed creating java (jvm.dll) again. It's very useful.

Thanks for sharing.

Regards,

Yonker wang

(CID:130095578)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:24 PM . Last Modified: ‎2024-04-05 12:14 AM

In response to DCIM_Support
0 Likes
0
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:24 PM . Last Modified: ‎2024-04-05 12:14 AM

Many thanks for the feedback 😀.

(CID:130095584)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:24 PM . Last Modified: ‎2023-10-22 04:01 AM

0 Likes
0
1629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:24 PM . Last Modified: ‎2023-10-22 04:01 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore