Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

We have a ACRP in row cooling unit with acrp Version: v3.7.5 Date: 01/07/2015 SNMP and SMTP are not working at the same time?

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • We have a ACRP in row cooling unit with acrp Version: v3.7.5 Date: 01/07/2015 SNMP and SMTP are not working at the same time?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Cory_McDonald Champion
159
Jef
Jef Leader
114
gsterling
gsterling Mentor
77
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:25 PM . Last Modified: ‎2024-04-05 12:14 AM

0 Likes
4
1081
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:25 PM . Last Modified: ‎2024-04-05 12:14 AM

We have a ACRP in row cooling unit with acrp Version: v3.7.5 Date: 01/07/2015 SNMP and SMTP are not working at the same time?

The software/firmware is as below:

Application Module
   
Name: acrp
Version: v3.7.5
Date: 01/07/2015
Time: 11:17:51
 
     
 
APC OS (AOS)
   
Name: aos
Version: v3.7.5
Date: 11/28/2012
Time: 11:12:41

Is there a fix for this issue?

(CID:130093736)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:25 PM . Last Modified: ‎2024-04-05 12:14 AM

0 Likes
2
1081
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:25 PM . Last Modified: ‎2024-04-05 12:14 AM

Hi Murat,

 

Can you please be more specific about your issue. I can say that there is no known issue with SNMP and SMTP (E-Mail) working at the same time but to help troubleshoot your issue, we'd need to know exactly what is failing. Is it unable to both send an e-mail and a trap at the same time? If you have e-mail configured, are you then unable to use SNMP to access the card? What exactly is happening?

What troubleshooting have you done? If you're not receiving e-mails or traps, have you tried a packet capture to verify the data is not being sent? Did you look at the logs at the time of the issue?

 

Steve

(CID:130093799)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:25 PM . Last Modified: ‎2024-04-05 12:14 AM

In response to DCIM_Support
0 Likes
0
1081
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:25 PM . Last Modified: ‎2024-04-05 12:14 AM

Hi Steve,

 

Below is what we are facing:

I was in the datacenter yesterday, when I noticed one of the AC units had flashing amber lights. I checked out the display, and it had some errors from last week. (Those errors have cleared themselves up, by the way). I thought it was odd because I didn’t see any email alerts. So I went into Struxureware to investigate this unit, and noticed there was no email settings configured. So I configured SMTP settings and ran a test email, all was good.

 

About an hour later, I started receiving  alerts like the one I’ve attached. I went back into the configuration for this unit, and looked at the SNMPv1 settings, comparing them to other units. I used the password for “snmpv1 read” . Still those errors persisted for the rest of the afternoon, 8 at a time, at least on the hour.

 

I deleted the A/C unit from Struxureware, and put it back, using SNMP as the discovery method, and still the errors persist. The only way I could get the alerts to stop was to remove the SMTP settings from the unit.

 

While I was looking at the other AC units, I noticed a lot of them don’t have SMTP settings configured. So I think that means they aren’t going to send out any email alerts. My concern is that if I configure all of them for email alerts, they’ll all start spitting out the SNMP errors.

(CID:130093821)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:25 PM . Last Modified: ‎2024-04-05 12:14 AM

In response to DCIM_Support
0 Likes
0
1081
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:25 PM . Last Modified: ‎2024-04-05 12:14 AM

Murat,

 

Sorry, I see no attachments.

Where did you set up the e-mail alerts, on the device or in DCE? 

What exactly are the alarms you are receiving?

Is StruxureWare actually reading information from the device?

Did you set up both read and write community names in DCE/on the device?

Is priority scanning enabled?

Do the community names have specific IPs associated to them on the network card or is the NMS IP set to all 0s?

 

Perhaps you could tell me what events you're seeing in the network card's event log.


Steve

(CID:130093823)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
DCIM_Support Mentor
Mentor

Posted: ‎2020-07-04 04:25 PM . Last Modified: ‎2023-10-22 04:16 AM

0 Likes
0
1081
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:25 PM . Last Modified: ‎2023-10-22 04:16 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore