hello everyone,
how can we clear GEO SCADA mimic caches
does it effects on mimics drawing in long term?
thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-05-30 06:15 AM
The embedded mimic cache is held in memory so restarting ViewX will clear this cache. You can also view the current content of the cache and change its size.
The ViewX cache (which isn't specific to mimics) is stored on disk so can be cleared by deleting the files in the cache folder (whilst ViewX is stopped):
The files will be downloaded from the server when the document is next displayed.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-05-30 06:15 AM
The embedded mimic cache is held in memory so restarting ViewX will clear this cache. You can also view the current content of the cache and change its size.
The ViewX cache (which isn't specific to mimics) is stored on disk so can be cleared by deleting the files in the cache folder (whilst ViewX is stopped):
The files will be downloaded from the server when the document is next displayed.