Writing to M340 PLC over modbus tcp from Geo Scada?

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Writing to M340 PLC over modbus tcp from Geo Scada?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
315
AndrewScott
Admiral AndrewScott
105
BevanWeiss
Spock BevanWeiss
95
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
39
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Geo SCADA Expert Forum
Anonymous user
Not applicable

Posted: ‎2021-12-09 01:15 PM . Last Modified: ‎2023-05-02 11:59 PM

0 Likes
2
1023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-09 01:15 PM . Last Modified: ‎2023-05-02 11:59 PM

Writing to M340 PLC over modbus tcp from Geo Scada?

Hi, I am really new to Geo Scada.

I have managed to read an analogue and digital address from an M340 plc over modbus tcp using the Modbus-Simple and Modbus-Advanced selection in geo scada and have it displayed in the HMI.

I am now trying to crate a basic push button that writes a bit back to the PLC over modbus tcp.

Can someone provide some guidance as to how to perform a modbus tcp write with Geo scada.

I would really appreciate any guidance.

 

Update: Got the analogue and digital write working. Still trying to get my head around stuff.

Thanks
Joshua

Labels
  • Labels:
  • SCADA
  • Tags:
  • english
  • modbus tcp write
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-12-14 01:26 AM

0 Likes
1
995
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-14 01:26 AM

You could tell us how you got it working Josh 🙂

That way when someone else comes along looking for the same answer, they will see your question and the associated answer.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-12-14 09:33 PM

In response to BevanWeiss
0 Likes
0
988
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-12-14 09:33 PM

Hi BevanWeiss,
Yes I did get it working and im planning to put some instructions together after I finish my current project.
I will make sure to add them to this post.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of