Virtual ViewX always shows the database tree when a user logs on

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Virtual ViewX always shows the database tree when a user logs on
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
319
AndrewScott
Admiral AndrewScott
114
BevanWeiss
Spock BevanWeiss
97
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
39
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
geoffpatton
Captain geoffpatton
Captain

Posted: ‎2023-07-13 08:37 AM

1 Like
5
2090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-07-13 08:37 AM

Virtual ViewX always shows the database tree when a user logs on

Is there a way to make Virtual ViewX not show the database tree every time a user logs on?

For most users it would be better that it always not be opened when they logon.

Of course it would be nice if it remembered if the user had it open or not last time they logged on like ViewX does.

 

Labels
  • Labels:
  • Virtual ViewX
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2023-08-11 04:13 AM . Last Modified: ‎2025-03-13 08:24 AM

0 Likes
1
1962
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-08-11 04:13 AM . Last Modified: ‎2025-03-13 08:24 AM

Yes, you can hide the database tree on start of a VVX session.

To do this you need to customise and save the Main DAT file which ViewX uses to set screen appearance, then copy the files from your own user folder to the VVX user folders.

The procedure is:

a) Run ViewX with a normal Windows user, log in and close the database tree

b) Do not log out, just Exit ViewX

c) Find the folder c:\Users\<your Windows user>\AppData\Roaming\Schneider Electric\ClearSCADA (Use Local if earlier than 2023)

d) Copy the ViewX Global Settings.dat file from this folder. (It may be easier to copy the \Schneider Electric\ClearSCADA folder and its files)

e) Paste these files into the equivalent folders for just the active VVXLocalUser Windows accounts. 

(Might be named VVXLocalUser or VVXLocalUser.<hostname> or what you set up manually in the VVX Applications tab.

 

Note that some settings which are saved between ViewX runs are modified on VVX start, such as hiding the alarm banner and ribbon - these cannot be altered.

 

Note also that in Geo SCADA 2023 the folder for these files is moving to  c:\Users\<your Windows user>\AppData\Roaming\Schneider Electric\ClearSCADA.

 

Edited: the destination user account was incorrect, should have been VVXLocalUser etc.

 

sbeadle_0-1741879476147.png

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2023-08-11 04:13 AM . Last Modified: ‎2025-03-13 08:24 AM

0 Likes
1
1963
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-08-11 04:13 AM . Last Modified: ‎2025-03-13 08:24 AM

Yes, you can hide the database tree on start of a VVX session.

To do this you need to customise and save the Main DAT file which ViewX uses to set screen appearance, then copy the files from your own user folder to the VVX user folders.

The procedure is:

a) Run ViewX with a normal Windows user, log in and close the database tree

b) Do not log out, just Exit ViewX

c) Find the folder c:\Users\<your Windows user>\AppData\Roaming\Schneider Electric\ClearSCADA (Use Local if earlier than 2023)

d) Copy the ViewX Global Settings.dat file from this folder. (It may be easier to copy the \Schneider Electric\ClearSCADA folder and its files)

e) Paste these files into the equivalent folders for just the active VVXLocalUser Windows accounts. 

(Might be named VVXLocalUser or VVXLocalUser.<hostname> or what you set up manually in the VVX Applications tab.

 

Note that some settings which are saved between ViewX runs are modified on VVX start, such as hiding the alarm banner and ribbon - these cannot be altered.

 

Note also that in Geo SCADA 2023 the folder for these files is moving to  c:\Users\<your Windows user>\AppData\Roaming\Schneider Electric\ClearSCADA.

 

Edited: the destination user account was incorrect, should have been VVXLocalUser etc.

 

sbeadle_0-1741879476147.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

geoffpatton
Captain geoffpatton
Captain

Posted: ‎2023-08-11 07:27 AM

In response to sbeadle
0 Likes
0
1958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-08-11 07:27 AM

Thanks Steve.

I thought it would be copying those files but the location I tried putting them was wrong.

Reply

Link copied. Please paste this link to share this article on your social media post.

joshribbons
Ensign joshribbons
Ensign

Posted: ‎2025-03-12 04:35 PM

0 Likes
0
903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-12 04:35 PM

I have been trying to get this working on a server running 2023 Nov 2024 Update. I have confirmed the settings using ViewX are being saved into the roaming folder as I can see the dates change every time I close ViewX.

I have copied the dat files into every conceivable location for any associated user including Default and still it will not show the alarm banner on login or close the database tree!

@sbeadle you mentioned VVX will modify some settings such as alarm banner - how

Reply

Link copied. Please paste this link to share this article on your social media post.

geoffpatton
Captain geoffpatton
Captain

Posted: ‎2025-03-13 05:31 AM

0 Likes
0
880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-13 05:31 AM

I actually never applied this. The customer decided they didn't mind the database tree. I just assumed it would work if I had modified the files in the correct location.

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2025-03-13 08:25 AM

1 Like
0
872
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-13 08:25 AM

Solution modified to specify the correct user/folder location.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore