Using automation interface with C# to load history

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Using automation interface with C# to load history
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
DavidSkilbeck
Lt. Commander DavidSkilbeck
Lt. Commander

Posted: ‎2021-02-23 04:16 PM . Last Modified: ‎2023-05-03 12:05 AM

0 Likes
15
6802
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-23 04:16 PM . Last Modified: ‎2023-05-03 12:05 AM

Using automation interface with C# to load history

Hi, I am trying to load history values to a tag. I refer to the last section of the below

 

https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Using-SOAP-interface-to-connect-to-Geo-SCADA/ba...

 

 

 

 

// Get object
ScxV6DbClient.ScxV6Object O = S.FindObject( "New Analogue Point" );

// The line below doesn't work because Interface is declared in the IDL as a vanilla IDispatch, instead we need to use late-binding via Reflection
// O.Interface.LoadDataValues( Values, Times, Qualities );

// Instead, use reflection:
// Get the Historic aggregate
object Historic = O.Interface.GetType().InvokeMember( "Historic", System.Reflection.BindingFlags.GetProperty, null,O.Interface,null );

// Invoke the LoadDataValues method
if ( Historic != null )
  Historic.GetType().InvokeMember( "LoadDataValues", System.Reflection.BindingFlags.InvokeMethod, null, Historic, new object[] { Values, Times, Qualities } );

 

 

 

 

I have changed the code to below

 

 

 

ScxV6Server S = new ScxV6Server();
S.Connect("Local", "admin", "admin");
// Get object
ScxV6DbClient.ScxV6Object O = S.FindObject("System.Xxxxx.HistoryAnalogPoint");
// Get the Historic aggregate
object Historic = O.Interface.GetType().InvokeMember("Historic", System.Reflection.BindingFlags.GetProperty, null, O.Interface, null);
//// Invoke the LoadDataValues method
if (Historic != null)
    Historic.GetType().InvokeMember("LoadDataValues", System.Reflection.BindingFlags.InvokeMethod, null, Historic, new object[] { sampleGS[i], sampleStartDateTime[i], 192 });

 

 

 

When the code gets to the line - ScxV6Server S = new ScxV6Server();

the following error occurs (Class not registered).

 

System.Runtime.InteropServices.COMException
HResult=0x80040154
Message=Retrieving the COM class factory for component with CLSID {EEAD2002-0777-11D2-AF05-0000E82E7A14} failed due to the following error: 80040154 Class not registered (0x80040154 (REGDB_E_CLASSNOTREG)).
Source=DNP3FT
StackTrace:
at InsertHistoryCOMAPI.Program.Main(String[] args) in C:\Users\Administrator\source\repos\\Program.cs:line 186

 

Thanks,

Labels
  • Labels:
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-02-24 06:13 PM

In response to DavidSkilbeck
0 Likes
7
6698
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-24 06:13 PM

It's CHistoryBase which has the aggregate.

 

Why are you doing the GetType()?

 

Why not just obtain the Historic aggregate on the object that you want to load the historic data for, and then call InvokeMethod on that aggregate, and pass in the required items...

 

i.e.

aggr.InvokeMethod("LoadDataValue", new object[] {reason, quality, timestamp, value});

or

aggr.InvokeMethod("LoadDataValues", new object[] {valueArray, timestampArray, qualityArray, reasonArray});

or

aggr.InvokeMethod("LoadDataValuesEx", new object[] {valueArray, timestampArray, qualityArray, statusArray, stateArray, reasonArray, msStateArray, putAsideArray} );

 

My offline code example actually shows a version without the new object[] {...}..., and instead just directly passing the arguments after the methodName.  It doesn't match the .NET API help method definition... but it's obviously worked for me at some time.  I haven't fired up Visual Studio to check out the InvokeMethod signature.. maybe it does accept a variable number of arguments.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 15
AdamWoodland
AdamWoodland Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-02-23 05:42 PM

0 Likes
14
6797
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-23 05:42 PM

Try

 

new Serck.ScxV6Server()

 

If that doesn't work you may need to regsvr32 DBClient.dll (in the x86 ClearSCADA installation folder), the installer should do that but maybe something went wonky somewhere.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

DavidSkilbeck
Lt. Commander DavidSkilbeck
Lt. Commander

Posted: ‎2021-02-23 06:50 PM . Last Modified: ‎2021-02-24 01:10 AM

In response to AdamWoodland
0 Likes
13
6794
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-23 06:50 PM . Last Modified: ‎2021-02-24 01:10 AM

Hi, I added the Serk, it still had an  error.

However, I removed the Serk and after that all errors cleared.

I am now able to run the code further.

 

@AdamWoodland 

I find it unclear at the moment, what is the format it is looking for as regards to Values, Times, Qualities.

Historic.GetType().InvokeMember( "LoadDataValues", System.Reflection.BindingFlags.InvokeMethod, null, Historic, new object[] { Values, Times, Qualities } );

Should it be more { Value, Time, Quality }? Value = 4.45, Time = 2021/02/24 12:30:22:55, Quality = 192?
If I can get it to write one value to the history of a point it would be a start.

Thanks,

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-02-24 03:00 AM

In response to DavidSkilbeck
0 Likes
12
6747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-24 03:00 AM

What does the schema say the arguments to LoadDataValues should be?


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

AdamWoodland
AdamWoodland Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-02-24 12:41 PM . Last Modified: ‎2023-04-25 04:09 AM

In response to BevanWeiss
0 Likes
11
6730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-24 12:41 PM . Last Modified: ‎2023-04-25 04:09 AM

Also see https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Importing-History-Using-LoadDataValue-and-LoadD...

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

DavidSkilbeck
Lt. Commander DavidSkilbeck
Lt. Commander

Posted: ‎2021-02-24 12:44 PM . Last Modified: ‎2021-02-24 02:10 PM

In response to AdamWoodland
0 Likes
10
6728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-24 12:44 PM . Last Modified: ‎2021-02-24 02:10 PM

Thanks Adam, I hadn't found that.

Thanks,

 

Hi, I notice the later article indicates four parameters

 LoadDataValue( Value{Variant},
                Timestamp{Time},
                Quality{Long},
                Reason{Byte} )

where the first indicates three

{ Values, Times, Qualities }

which should it be?

 

So I have tried

 

{ sampleGS[i], sampleStartDateTime[i], sampleQuality[i], sampleReason[i] }

 


which when written to the console looks like
4.0218887,2020,07,22,16,11,38,010,192,8 this may not be correct format?


This throws an error

 

 

System.Reflection.TargetInvocationException
HResult=0x80131604
Message=Exception has been thrown by the target of an invocation.
Source=System.Private.CoreLib
StackTrace:
at System.RuntimeType.InvokeDispMethod(String name, BindingFlags invokeAttr, Object target, Object[] args, Boolean[] byrefModifiers, Int32 culture, String[] namedParameters)
at System.RuntimeType.InvokeMember(String name, BindingFlags bindingFlags, Binder binder, Object target, Object[] providedArgs, ParameterModifier[] modifiers, CultureInfo culture, String[] namedParams)
at System.Type.InvokeMember(String name, BindingFlags invokeAttr, Binder binder, Object target, Object[] args)
at InsertHistoryCOMAPI.Program.Main(String[] args) in C:\Users\Administrator\source\repos\Xxxxx\Program.cs:line 200

Inner Exception 1:
ArgumentException: Value does not fall within the expected range.

 

 

Thanks,

  • Tags:
  • scada
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-02-24 03:02 PM

In response to DavidSkilbeck
0 Likes
9
6710
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-24 03:02 PM

If using C# recommendations are:

 

LoadDataValues requires ARRAYS, not single values

LoadDataValue requires single values, not arrays

 

You should use DateTimeOffset as DateTime inputs to functions, and expect DateTimeOffset as return values.

You shouldn't explicitly "box" 'Value' (variant) datatypes, you can use the native intrinsic type just fine.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

DavidSkilbeck
Lt. Commander DavidSkilbeck
Lt. Commander

Posted: ‎2021-02-24 04:16 PM

In response to BevanWeiss
0 Likes
8
6704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-24 04:16 PM

Hi Bevan,

where in the schema were you referring to above please.

 

ok, I will try LoadDataValue.
Can any body give correct variable type and values that I can place into the line below, that they know works, so that I can at least see it work please.

Historic.GetType().InvokeMember("LoadDataValue", System.Reflection.BindingFlags.InvokeMethod, null, Historic, new object[] { sampleValueTest, sampleStartDateTimeTest, sampleQualityTest });

 

sampleValueTest

 

sampleStartDateTimeTest

sampleQualityTest

 

Thanks,

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-02-24 06:13 PM

In response to DavidSkilbeck
0 Likes
7
6699
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-24 06:13 PM

It's CHistoryBase which has the aggregate.

 

Why are you doing the GetType()?

 

Why not just obtain the Historic aggregate on the object that you want to load the historic data for, and then call InvokeMethod on that aggregate, and pass in the required items...

 

i.e.

aggr.InvokeMethod("LoadDataValue", new object[] {reason, quality, timestamp, value});

or

aggr.InvokeMethod("LoadDataValues", new object[] {valueArray, timestampArray, qualityArray, reasonArray});

or

aggr.InvokeMethod("LoadDataValuesEx", new object[] {valueArray, timestampArray, qualityArray, statusArray, stateArray, reasonArray, msStateArray, putAsideArray} );

 

My offline code example actually shows a version without the new object[] {...}..., and instead just directly passing the arguments after the methodName.  It doesn't match the .NET API help method definition... but it's obviously worked for me at some time.  I haven't fired up Visual Studio to check out the InvokeMethod signature.. maybe it does accept a variable number of arguments.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

DavidSkilbeck
Lt. Commander DavidSkilbeck
Lt. Commander

Posted: ‎2021-02-25 02:42 PM

In response to BevanWeiss
0 Likes
6
6652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-25 02:42 PM

Hi, I was attempting to follow the below,

 

 

// Get object
ScxV6DbClient.ScxV6Object O = S.FindObject( "New Analogue Point" );

// The line below doesn't work because Interface is declared in the IDL as a vanilla IDispatch, instead we need to use late-binding via Reflection
// O.Interface.LoadDataValues( Values, Times, Qualities );

// Instead, use reflection:
// Get the Historic aggregate
object Historic = O.Interface.GetType().InvokeMember( "Historic", System.Reflection.BindingFlags.GetProperty, null,O.Interface,null );

// Invoke the LoadDataValues method
if ( Historic != null )
  Historic.GetType().InvokeMember( "LoadDataValues", System.Reflection.BindingFlags.InvokeMethod, null, Historic, new object[] { Values, Times, Qualities } );

 

 

I thought this would allow for data to be loaded into the history of the point.

Thanks,

 

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-02-25 05:34 PM

In response to DavidSkilbeck
0 Likes
5
6645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-25 05:34 PM

Here's something from @sbeadle , it's where I'd start from... 

https://github.com/GeoSCADA/Utilities-and-Examples/blob/main/InsertHistoricData/Program.cs

 

His LoadDataValue example

// Add a value
Object[] p1 = new Object[4];
p1[0] = 1;
p1[1] = 192;
p1[2] = now;
p1[3] = 1;
PointObj.Aggregates["Historic"].InvokeMethod("LoadDataValue", p1);

 

Although I prefer the inline definition of the new object[] {} (as my previous example used)

 

He's got another example here:

https://github.com/GeoSCADA/Utilities-and-Examples/blob/main/SetInternalPoint/Program.cs

where he uses InvokeMethod on the base object (i.e. PointObj from the above example) but has a longer qualifier on the method name ("Historic.RawValues" in this version... but that would be "Historic.LoadDataValue" if you wanted to invoke the LoadDataValue method instead).

 

The tproject concept has quite a lot of jumping backwards through hoops, which seems unnecessary.

Perhaps back when it was created the Aggregates collection didn't exist.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

DavidSkilbeck
Lt. Commander DavidSkilbeck
Lt. Commander

Posted: ‎2021-02-25 05:52 PM . Last Modified: ‎2021-02-25 07:47 PM

In response to BevanWeiss
0 Likes
4
6643
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-25 05:52 PM . Last Modified: ‎2021-02-25 07:47 PM

Hi, I went back through some older code I had and came across this.

I just changed the date and this worked.
Apart from having to change the date to a more recent one of course.

 

 

 

 

DBObject TestPoint;
                Aggregate HistAgg;

                //Object[] argsTo;
                DateTime dt;
                Object[] argsTo = new Object[4];

                using (Connection conn = new Connection("ClearSCADA"))
                {

                    // Connect to local server
                    SecureString passwd = new SecureString();
                    string strPassword = "admin";
                    foreach (char c in strPassword)
                        passwd.AppendChar(c);
                    passwd.MakeReadOnly();
                    conn.Connect("localhost");
                    conn.LogOn("admin", passwd);
                    



                    //string pointValue = dict["Test2"];
                    // Get the point
                    TestPoint = conn.GetObject("System.Dashboard.Engineering Dashboard.Work Orders.Points.HistoryAnalogPoint");
                    // If Historic is enabled for the point, insert historic data
                    if (TestPoint.Aggregates.TryGetValue("Historic", out HistAgg) == true)
                    {

                        argsTo[0] = "4"; // Reason
                                         //argsTo[0] = column1[0]; 
                                         //argsTo[1] = "1"; // Quality
                        argsTo[1] = "192"; // Quality
                                           //argsTo[1] = column3[0]; // Quality
                        dt = new DateTime(2020, 3, 02, 11, 55, 52);
                        argsTo[2] = new System.DateTimeOffset(dt);
                        //argsTo[2] = column2[0]; //DateTime
                        //argsTo[3] = "88";
                        ////argsTo[3] = column4[0]; //Value
                        argsTo[3] = 4.45; //Value

                        HistAgg.InvokeMethod("LoadDataValue", argsTo);
                        
                    }
                    conn.LogOff();
                    conn.Disconnect();

 

 

Thanks, 

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

DavidSkilbeck
Lt. Commander DavidSkilbeck
Lt. Commander

Posted: ‎2021-02-25 10:28 PM

In response to DavidSkilbeck
0 Likes
3
6630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-25 10:28 PM

Hi, these are the settings for my Geo SCADA.

ErrorMessageCSV4Import.png

 

This a sample of the data I want to import
4.0218887,2020,07,22,16,11,38,010,192,8
3.1718216,2020,07,22,16,11,53,010,192,8

This is what I am getting in Geo SCADA

 

 

If I use the below it wont import historic values

dt = new DateTime(2020, 2, 26, 11, 55, 52);

If I change the 2020 to 2021 it imports.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-02-26 12:47 AM

In response to DavidSkilbeck
0 Likes
2
6619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-26 12:47 AM

Assuming that you were running your code at close to 5pm on the 26th February 2021... and you have a historic configuration set to keep data for 52 weeks... then 52*7 = 364 days... so the 26th February 2020 is NOT within your configured historic retention window.

In fact you're two days out, since last year was a leap year..

 

You should go back through the help files for the settings in the Server Configuration pane, really see what it says for each of the fields, and think about how that will relate to what you are trying to do.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

DavidSkilbeck
Lt. Commander DavidSkilbeck
Lt. Commander

Posted: ‎2021-07-11 08:21 PM

In response to BevanWeiss
0 Likes
1
5653
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-11 08:21 PM

Hi, is it possible to change the code above to do a LoadDataFile.

Thanks,

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-07-16 08:21 PM

In response to DavidSkilbeck
0 Likes
0
5588
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-16 08:21 PM

Yes, you'll just want to look at the schema to see what arguments you need to supply to that method, and note that the path must be:

  1. On the running MAIN server
  2. Accessible under the permissions that the Geo SCADA Expert server instance is running under (inclusive of both username and escalation settings)
  3. Using the correct path information to reach the file (given the server is not running in the same context as you may be running your script in)

Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore