Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Importing History Using LoadDataValue and LoadDataFile

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • Importing History Using LoadDataValue and LoadDataFile
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • WebX 19
  • Request Form 18
  • Lists, Events & Alarms 16
  • ViewX 15
  • Setup 12
  • Application Programming 12
  • Telemetry 8
  • Events & Alarms 7
  • Lists 7
  • Mimic Graphics 7
  • Downloads 6
  • Geo SCADA Expert 5
  • SCADA 5
  • IoT 5
  • Support 5
  • Drivers and Communications 4
  • Security 4
  • 2025 3
  • IEC 61131-3 Logic 3
  • DNP 3 3
  • Virtual ViewX 2
  • Trends and Historian 2
  • Architectures 1
  • Templates and Instances 1
  • Releases 1
  • Maps and GIS 1
  • Mobile 1
  • Geo Scada 1
  • Tools & Resources 1
  • Privacy Policy 1
  • OPC-UA 1
  • ClearSCADA 1
  • Python 1
  • Previous
  • 1 of 4
  • Next
Latest Blog Posts
  • Python API - Reading the Instance and Template Structure
  • Python API - How to get Earthquake data into a Geo SCADA Map
  • Python API - Creating and Configuring Data Tables
  • Python API - Setting aggregates
  • Python API - Clearing an aggregate link
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Anonymous user
Not applicable
‎2021-06-09 04:00 PM
1 Like
0
1742
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-09 04:00 PM

Importing History Using LoadDataValue and LoadDataFile

Originally published on Geo SCADA Knowledge Base by Anonymous user | June 10, 2021 01:00 AM

📖 Home  Back  
Several methods exist in the Historic aggregate class for importing data into point and accumulator histories.

LoadDataValue

 LoadDataValue( Value{Variant},
Timestamp{Time},
Quality{Long},
Reason{Byte} )

Values for Quality parameter (ClearSCADA uses standard OPC HDA quality definitions), e.g.:

  • 0 = Bad
  • 64 = Uncertain
  • 192 = Good

Values for Reason parameter (Reason For Logging field available in the historic database):

  • 0 = Current Data
  • 1 = Value Change
  • 2 = State Change
  • 3 = Timed Report
  • 4 = End of Period
  • 5 = End of Period Reset
  • 6 = Override
  • 7 = Release Override
  • 8 = Modified/Inserted

LoadDataValues

 LoadDataValues( Value{Array of Variant},
Timestamp{Array of Time},
Quality{Array of Long},
Reason{Array of Byte} )


Same as LoadDataValue except the parameters passed in are arrays instead of single values. A maximum of 5,165 elements are allowed in the arrays otherwise an error will be raised.
The Reason argument is optional - when omitted defaults to 0 (Current Data).

LoadDataValuesEx

 LoadDataValuesEx( Value{Array of Variant},
Timestamp{Array of Time},
Quality{Array of Long},
Status{Array of Long},
State{Array of Byte},
Reason{Array of Byte},
MSState{Array of Byte} )

Extended version of LoadDataValues that allows all of the properties of the historic data record to be specified.
The Status, State, Reason and MSState paramaters are all optional.
The Status parameter is a bit mask of flags that varies between drivers.
To calculate the State from the Value specify the state as 255 (or omit the parameter).
If there is no master-station state (or feature is disabled) then specifiy the MSState as 255 (or omit the parameter).

LoadSuppressionValues

 LoadSuppressionValues( Type{Array of Short},
Timestamp{Array of Time} )

Values for Type parameter (consequential alarm type):

  • 0 = None
  • 1 = Consequential
  • 2 = Maintenance

LoadDataFile

 LoadDataFile( FileName{String} )

The LoadDataFile method takes a filename as its single parameter. This is the name of a local CSV on the main server. Some points to note about the files to be imported:

  • Each line of the CSV file specifies a single record and has the format: YYYY,MM,DD,HH,MM,SS,Value
  • The file must be in ANSI format.
  • To insert comments into the file start the line with a semi-colon.
  • Reason is set to 0 (Current Data) on import.

Performance

LoadDataFile is much faster at importing records than LoadDataValues.

Go: Home Back

Author

Biography

Anonymous user

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Newer Article
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore