Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84600members
353869posts

Redundant GeoSCADA 1 MAIN server, 1 Permanent Standby Server

EcoStruxure Geo SCADA Expert Forum

Find out how SCADA systems and networks, like EcoStruxure Geo SCADA Expert, help industrial organizations maintaining efficiency, processing data for smarter decision making with IoT, RTU and PLC devices.

Solved
Oncom
Commander
Commander
0 Likes
9
4322

Redundant GeoSCADA 1 MAIN server, 1 Permanent Standby Server

 

ArchitectureArchitecture

Hi All,

 

I have architecture above. 

- 2 Server, 1 server in control network, and 1 server in office network. and both are connected directly peer to peer. 

- 2 separate network.

 

is it architecture is possible?
I was trying to configure as redundant, but it become a problem when Server B as MAIN

what I want is Server A always as MAIN / Primary. and Server B can synchronize data from Server A and Server B can accessed by Client B.

 

thanks
 😀


Accepted Solutions
JChamberlain
Schneider Alumni (Retired)
Schneider Alumni (Retired)

Re: Reundant GeoSCADA without changing MAIN server

You might want to raise this with support, we can help you more effectively in through the correct channels.

 

If you right click the server icon and select Invalid Configuration it will tell you why your configuration is invalid.

 

Use a name or address that doesn't exist at all, rather than one that just doesn't have CS installed. We use ICMP as one component for detecting isolation, it doesn't rely on CS replying. I recommend using 'Dummy' or similar, so someone else who looks at the config in future doesn't think it is a mistake.

 

See below what I think will work for you. I'm not 100% sure what each machine's IP address is, I've assumed:

 

Main (A) is 129.76.3.1

Standby (B) is 129.76.3.3

 

Dummy should be configured for the Main's Standby A and the Dummy's Standby B.MainPartner.JPGStandby.JPGMainPSs.JPG

 

 

 

See Answer In Context

9 Replies 9
sbeadle
Janeway Janeway
Janeway
8
4320

Re: Reundant GeoSCADA without changing MAIN server

Yes, configure server B as a Permanent-Standby. It will serve data and sync from A, but never go Main.

See this new video for architecture guidance:

https://www.youtube.com/watch?v=lmbMy4jJGX0&list=PLa7UGrWOTyjnPpCJxnTZkdBM_6D70qoKl

Search for Permanent Standby in the F1 help.

 

JChamberlain
Schneider Alumni (Retired)
Schneider Alumni (Retired)
7
4302

Re: Reundant GeoSCADA without changing MAIN server

To have B as a permanent standby you'll have to either install an additional hot standby on the control network side (recommended) or configure the permanent standby so it thinks there are is an additional hot standby - the permanent standby needs to have two hot standby partners configured.


NoName.JPGDummyName.JPG

Oncom
Commander
Commander
0 Likes
6
4295

Re: Reundant GeoSCADA without changing MAIN server

@sbeadle Hi Steve, thanks for your respond.

in your video, and also mentioned by @JChamberlain the MAIN server should have standby pair. so is it still possible?

image.png

 

 


I was try to configure it but fail. my Permanent standby Server doesn't start: always in state: Starting.. 

I configure Permanent Standby Server as on Manual Help 

SC_OPCSERVER(STANDBY).PNG

 

and here is my configuration on MAIN server:

SC_SCADASERVER(MAIN)_PERMANENT.PNGSC_SCADASERVER(MAIN)_STANDBYTAB.PNG

 

what I was trying in MAIN Server:
-put IP adress of StandbyPC(permanent standby) on Standby A : Permanent standby PC can start but show up Error Invalid configuration, Main Server also show invalid configuration

 

-put IP address of Main PC (this computer IP it self) : Main Server can start as Main, Standby Server always in Starting state

 

-put IP address of other PC (no clearscada) : Main Server can start as Main, Standby Server always in Starting state

JChamberlain
Schneider Alumni (Retired)
Schneider Alumni (Retired)

Re: Reundant GeoSCADA without changing MAIN server

You might want to raise this with support, we can help you more effectively in through the correct channels.

 

If you right click the server icon and select Invalid Configuration it will tell you why your configuration is invalid.

 

Use a name or address that doesn't exist at all, rather than one that just doesn't have CS installed. We use ICMP as one component for detecting isolation, it doesn't rely on CS replying. I recommend using 'Dummy' or similar, so someone else who looks at the config in future doesn't think it is a mistake.

 

See below what I think will work for you. I'm not 100% sure what each machine's IP address is, I've assumed:

 

Main (A) is 129.76.3.1

Standby (B) is 129.76.3.3

 

Dummy should be configured for the Main's Standby A and the Dummy's Standby B.MainPartner.JPGStandby.JPGMainPSs.JPG

 

 

 

Oncom
Commander
Commander
0 Likes
3
4233

Re: Reundant GeoSCADA without changing MAIN server

@JChamberlain Hi,

 

I was try again using that configuration from you. but still the Standby doesn't want to Start, the state always: Starting..

already change the port too in permanent standby tab to 5482, and still didn't work

 

BTW, to raise this with support, do we need to have support/CF? or just simply email to Trss-support@se.com or your email 😉?

 

 

Thanks

BevanWeiss
Spock
Spock
0 Likes
2
4230

Re: Reundant GeoSCADA without changing MAIN server

When you ping the Primary Server IP address from the Permanent Standby server what result do you get?

If that doesn't work, then you need to fix that issue.

 

If that does work, then you should try TCPing (or telnet) to the default port 5481 to ensure that this works.  If it doesn't, then you likely have a firewall problem.

 

The IP addresses that you have listed seem a little unusual based upon the first image that you have suggested.

I would have expected that you would be using link local addresses for the direct link between the two servers (Primary and Permanent Standby), and hence would have 169.254.x.y format IP addresses.  You could allocate a Class A, B or C private IP address (or even technically a public IP address) to these interfaces, but it seems wasteful if they will only be used to link these two computers together for the ClearSCADA data replication.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Oncom
Commander
Commander
0 Likes
1
4227

Re: Reundant GeoSCADA without changing MAIN server

hi @BevanWeiss ,

 

I can ping from each others, and firewall has been disabled on both side. I already successful configure it as Redundant pairs. that 5481 port should be OK then.

 

Yes this is unusual Class B IP address using public IP, I already mentioned it to them (my customer) to use private IP as a standard.

and the link between computers is only connected each others for data replication.

BevanWeiss
Spock
Spock
0 Likes
0
4224

Re: Reundant GeoSCADA without changing MAIN server

I would recommend leaving all ports as default 5481.

 

If you have already successfully configured the servers as redundant pairing, then you should just need to go to the Permanent Standby, and change the mode on this server (the Permanent Standby) from Hot-Standby Pair, to Permanent Standby, and things should work.  If it complains about wanting a Standby B address just enter 0.0.0.0 for this.

 

You will absolutely need to have the Primary Server running first, for the Permanent Standby to transition from Starting to Synchronising. And then once Synchronised it should just run as Permanent Standby from that point until the Primary Server is lost, in which case it will revert to Starting (until Re-synchronisation can occur again).

 

To get official tech support, you would need to have a Site ID that is in support (technically all sites that you are involved with should be within support).


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Oncom
Commander
Commander
0 Likes
0
4201

Re: Reundant GeoSCADA without changing MAIN server

now it works after I restart all PC and still using this configuration from @JChamberlain .

 

Thanks All, @JChamberlain @BevanWeiss @sbeadle