Point configuration - Scada message "duplicate alarm source"
EcoStruxure Geo SCADA Expert Forum
Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-2008:32 PM
Yes... you have a Duplicate Alarm Source.
On more than one of your objects, on the Alarm tab of the configuration, you have the same value for the 'Alarm Source' field.
This is not allowed.
Alarm Source MUST be unique across a ClearSCADA / Geo SCADA Expert database.
If you leave it blank, then it will be the FullName of the object (which is also unique).
I actually haven't tried to enter an Alarm Source for an object which is the FullName of another object... I wouldn't recommend doing this, I can imagine a potential bug here with the detection of it.. I might test just to confirm it's detected correctly.
Lead Control Systems Engineer for Alliance Automation (VIC). All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..