Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Does Geo scada work as an OPC DA Server?

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Does Geo scada work as an OPC DA Server?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
sbeadle Champion
335
AndrewScott
AndrewScott
125
BevanWeiss
BevanWeiss
104
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
Valentino
Valentino Leader
Leader

Posted: ‎2021-08-20 04:44 AM . Last Modified: ‎2023-05-03 12:01 AM

0 Likes
8
6044
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-20 04:44 AM . Last Modified: ‎2023-05-03 12:01 AM

Does Geo scada work as an OPC DA Server?

Goodmorning everyone,

 

I have Geoscada server which also works as an OPC DA server.

If I use Matrikon software on the same server to access Geoscada via OPC. I read all the data correctly.

But if I use another PC on the same network, I cannot access the Geoscada data.

 

I thinks that is a ports problem.

 

So I'm here to ask.
What TCP ports should I reserve for correct operation?
I opened ports 5481 and 135 but it doesn't work.
Do I have to open doors 5500 to 5509 as well?
Where do I find this information on the manule?

 

Can I have this configuration?
can i tunnelig for the OPC DA?
Can I read that data from other PCs on the network?
Does the OPC DA work locally, but does it also work remotely?

 

 

Thanks for the help!!

Labels
  • Labels:
  • SCADA
  • Telemetry
  • ViewX
  • Tags:
  • english
  • geoscada
  • opc
  • opc da
  • scada
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa500295_brid
sesa500295_brid Troubleshooter
Troubleshooter

Posted: ‎2021-08-20 04:52 AM

1 Like
7
6042
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-20 04:52 AM

Hi,

You need to configure DCOM settings for Server Machine and Client Machine. Please see below matrikon documents for DCOM settings.

https://www.matrikonopc.com/dcom-configuration-opc.aspx

Without DCOM settings you can't use OPC-DA in network.

Matrikon, Cogent and OPC expert has some solutions on Tunneling if you don't want to deal with DCOM settings.

Hope it will solve your issue,

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

tfranklin
tfranklin
Leader

Posted: ‎2021-08-20 05:57 AM

In response to Valentino
1 Like
1
6031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-20 05:57 AM

No need for OFS here.  Just install the data access components for Geo SCADA on the remote box.  Basically, run the installer on the remote box and set it to custom.  Uncheck everything except for data access.  This'll install the ODBC driver and Configure Connections application.  Go to the configure connections application and create a connection to your primary server. 

 

Your OPC client should then see a connection locally for something like Serck.ScxV6OPCDA.MAIN.10.0.0.3 where MAIN is what I called the connection and 10.0.0.3 is the IP of the server. 

 

Note, your server may need appropriate licensing for this.

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
sesa500295_brid
sesa500295_brid Troubleshooter
Troubleshooter

Posted: ‎2021-08-20 04:52 AM

1 Like
7
6043
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-20 04:52 AM

Hi,

You need to configure DCOM settings for Server Machine and Client Machine. Please see below matrikon documents for DCOM settings.

https://www.matrikonopc.com/dcom-configuration-opc.aspx

Without DCOM settings you can't use OPC-DA in network.

Matrikon, Cogent and OPC expert has some solutions on Tunneling if you don't want to deal with DCOM settings.

Hope it will solve your issue,

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

tfranklin
tfranklin
Leader

Posted: ‎2021-08-20 05:34 AM

In response to sesa500295_brid
1 Like
3
6035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-20 05:34 AM

As mentioned above, when you go across network you'll be running into Windows DCOM issues.  Fortunately, Geo SCADA has a native "tunnel" type feature where you can install the data access components on a remote machine (local to your client) and point the Client Config app to the main server.  The OPC client can then point to the new CS configuration and Geo SCADA will effectively tunnel the data, bypassing COM. 

 

Other options are just as the previous person mentioned.  Configure DCOM properly or invest in a different tunneling software.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

Valentino
Valentino Leader
Leader

Posted: ‎2021-08-20 05:49 AM

In response to tfranklin
0 Likes
2
6033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-20 05:49 AM

Thanks for reply.

Is this native functionality the "OPC Factory Server"?

Do I have to install this software on the remote machine and configure it to point to the Geoscada server? does it work like the DCOM?

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

tfranklin
tfranklin
Leader

Posted: ‎2021-08-20 05:57 AM

In response to Valentino
1 Like
1
6032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-20 05:57 AM

No need for OFS here.  Just install the data access components for Geo SCADA on the remote box.  Basically, run the installer on the remote box and set it to custom.  Uncheck everything except for data access.  This'll install the ODBC driver and Configure Connections application.  Go to the configure connections application and create a connection to your primary server. 

 

Your OPC client should then see a connection locally for something like Serck.ScxV6OPCDA.MAIN.10.0.0.3 where MAIN is what I called the connection and 10.0.0.3 is the IP of the server. 

 

Note, your server may need appropriate licensing for this.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

Valentino
Valentino Leader
Leader

Posted: ‎2021-08-20 06:08 AM

In response to tfranklin
0 Likes
0
6029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-20 06:08 AM

Ah great!
in this way it is as if I have a tunneling software but in reality I am using the "configure connection" of GeoScada!

 

Thanks!

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

Valentino
Valentino Leader
Leader

Posted: ‎2021-08-20 07:35 AM

In response to sesa500295_brid
0 Likes
2
6023
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-20 07:35 AM

Thanks for reply!

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

tkswathik
tkswathik
Contributor

Posted: ‎2021-08-20 08:00 AM

In response to Valentino
0 Likes
1
6014
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-20 08:00 AM

Hi,

 

In your original question you had asked:

 

Do I have to open doors 5500 to 5509 as well?

 

Answer is "Yes" you have to, if there is a firewall in between the computer where the "GeoSCADA components" installed and the GeoSCADA server, along with port 5481. 

 

Another thing I noticed is this would need the Guest account to be enabled and have access to the folders you plan to access through OPC Client. In our system we had the Guest disabled, but we had to add this to a folder's security and provided "read" access.

 

 

 

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
BevanWeiss
Champion

Posted: ‎2021-08-20 08:36 PM

In response to tkswathik
0 Likes
0
5992
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-20 08:36 PM

One important thing to note here is that this is a licenced feature.

There is a licence restriction on the number of 'OPC Clients' that can connect to a Geo SCADA Expert server.

 

Any OPC Client can connect, and you don't need to install other software.

You can either use the raw OPC-DA connection, in which case DCOM etc are a problem.  Or you can use the Data Access Component method (as mentioned by another) in which case you install these components on the client machine, and then you can access an OPC-DA 'service' locally to the client, which then tunnels it through the normal 5481/5500-55xx ClearSCADA / GeoSCADA Expert ports.

 

I'd recommend the second OPC tunnelling through Data Access Components if you can.  If you can't, then you'll just have to deal with the DCOM stuff... which is never fun.

 

For either case, OPC client licence (on server) is required.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore