GeoSCADA connection to a Powerflex drive using Ethernet/IP

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • GeoSCADA connection to a Powerflex drive using Ethernet/IP
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-08-08 07:36 PM . Last Modified: ‎2023-05-03 12:02 AM

0 Likes
5
2582
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-08 07:36 PM . Last Modified: ‎2023-05-03 12:02 AM

GeoSCADA connection to a Powerflex drive using Ethernet/IP

Hi group, 

 

Has anybody tried connecting to a Powerflex VSD from GeoSCADA?  I am able to connect to a Micro800 PLC but when I try to connect the drive, I get an error: INVALID ORIGINATOR TO TARGET NETWORK CONNECTION
REDUNDANT_OWNER.

 

Any help on this would be appreciated. 

Labels
  • Labels:
  • SCADA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-08-08 10:00 PM

0 Likes
0
2572
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-08 10:00 PM

The driver only claims to support the core AB PLC ranges (ref). If you raise a case with support with the driver and comms log we can pass them to development to see if it can be made compatible, but no promises.

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-08-15 05:56 PM

In response to Anonymous user
0 Likes
1
2524
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-15 05:56 PM

Do you have any wireshark captures for this?

 

My suspicion is that Geo SCADA Expert Ethernet/IP driver will indeed be performing 'Unconnected Message' requests.

I have been wrong before however... but it's generally easier to do unconnected messaging.. since it doesn't require keeping a bunch of state around the place.. and handling callbacks etc.

 

PS: You can get a ModbusTCP comms module for the PowerFlex drives.. which would have allowed the SCADAPack RTU to talk directly to the drive.

There is some discussion of an Ethernet/IP 'driver' for the SCADAPack RTU... but I'm not sure what timeline that has.

It should be able to leverage the CIP subsystem for the M580 PLCs, that wouldn't allow for the 'tag-based' stuff that people will want, but would be exactly what you'd like to do here.

It might be worth you finding that 'Idea' and giving it an upvote if you haven't already.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-08-08 10:00 PM

0 Likes
0
2573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-08 10:00 PM

The driver only claims to support the core AB PLC ranges (ref). If you raise a case with support with the driver and comms log we can pass them to development to see if it can be made compatible, but no promises.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-08-08 10:13 PM

0 Likes
3
2570
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-08 10:13 PM

Are you able to provide a screen shot of the error message as shown? (or as formatted within the logs)

 

It looks like the VSD is potentially expecting (demanding) and your connection type be a specific 'redundant_owner' connection.

So.. there's a few questions

 

  1. Are you trying to write things to the VSD, or only read?
  2. Is there already another PLC that 'owns' this device (i.e. that has a connection to it)?

 

I very much suspect that there would be some additional challenges with writing to Ethernet/IP CIP devices, since there will be some control hoops needed for most things (like VSDs that will only respond to the device owner, and will require a constant stream of updates otherwise they will trip out with a comms timeout).

 

And trying to connect to a device if something else is already connected likewise is probably an issue, since the devices often treat the first connection as special, and may require second (and subsequent) connections to go through an alternative connection method (which might be where this invalid network connection 'redundant_owner' is involved... redundant_owner would definitely be a somewhat special connection type that the VSD probably wants if you're the second connection trying to write to it.. and there is likely some weird stuff around device ownership redundancy that would be needed.. and which I don't think is reasonable to expect GeoSCADA to do)


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-08-09 05:36 PM

In response to BevanWeiss
0 Likes
2
2559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-09 05:36 PM

Hi Bevan,

 

1. I am only trying to read. I dare not to write to VSDs when trying out new features :).

2. Yes there is a Micro800 PLC as a bridge between VSDs and the Scadapack RTU to read VSD parameters. Suspecting it being the issue, I halted the running program but that didn't help either.

 

There is a feature in Ethernet/IP which uses unconnected message query. I think Geo SCADA needs to support such reads.Capture.PNG

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2021-08-15 05:56 PM

In response to Anonymous user
0 Likes
1
2525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-15 05:56 PM

Do you have any wireshark captures for this?

 

My suspicion is that Geo SCADA Expert Ethernet/IP driver will indeed be performing 'Unconnected Message' requests.

I have been wrong before however... but it's generally easier to do unconnected messaging.. since it doesn't require keeping a bunch of state around the place.. and handling callbacks etc.

 

PS: You can get a ModbusTCP comms module for the PowerFlex drives.. which would have allowed the SCADAPack RTU to talk directly to the drive.

There is some discussion of an Ethernet/IP 'driver' for the SCADAPack RTU... but I'm not sure what timeline that has.

It should be able to leverage the CIP subsystem for the M580 PLCs, that wouldn't allow for the 'tag-based' stuff that people will want, but would be exactly what you'd like to do here.

It might be worth you finding that 'Idea' and giving it an upvote if you haven't already.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-08-15 07:00 PM

In response to BevanWeiss
0 Likes
0
2519
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-15 07:00 PM

Hi Bevan,

 

I dont have wireshark captures for that. 

 

I will look into the option of using Modbus TCP adapter. Thanks for that suggestion. 

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore