Plant SCADA OPC Connectivity to GeoSCADA Historian
EcoStruxure Geo SCADA Expert Forum
Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Next option is to ask through your official Support channel.
I have not setup a remote OPC client to access to Plant SCADA since Citect 5.42, which was a pain and I think it is still basically the same. Registering some Citect files on the Client system and then configuring DCOM settings on both systems.
That being said you might want to consider OPC UA. Plant SCADA supports being a OPC UA server (not sure if that is a licensed option or which version OPC UA server was first available on) and Geo SCADA's Client has supported UA for awhile. That would probably be the easier route since there is no DCOM to have to mess with.