Hi,
can someone help me with this recurring error (not all the time) :
11/10/2024 08:34:36|Information|10/11/2024 08:34:36.006 TCPSERVERCHANNEL ForceChannelFault Socket=000011B4, ChannelId=66, TokenId=31, Reason=Id: BadTcpInternalError
11/10/2024 08:34:37|Information|10/11/2024 08:34:36.006 Connection cleanup initiated for client [10.3.104.15]:61804, ChannelId=66
11/10/2024 08:34:37|Error|10/11/2024 08:34:36.105 Unexpected error during OnReadComplete, SocketException 'Une connexion existante a dû être fermée par l’hôte distant'
11/10/2024 08:34:37|Information|10/11/2024 08:34:36.106 TCPSERVERCHANNEL ForceChannelFault Socket=00001204, ChannelId=79, TokenId=1, Reason=Id: BadTcpInternalError
11/10/2024 08:34:37|Information|10/11/2024 08:34:36.106 Connection cleanup initiated for client [10.3.104.15]:58048, ChannelId=79
thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-13 06:35 PM . Last Modified: 2024-10-13 07:39 PM
With OPC UA, as with many client-server setups, there could be many reasons, but some questions:
The "An existing connection was forcibly closed by the remote host" (if Google Translate is correct) error suggests that you're connecting to the OPC UA server port successfully but the application, Windows, or something in between like an NIPS, is actively disconnecting you. Often seen by a TCP reset flag being received at the client (should be able to see this in Wireshark or any packet capture setup you might have) but can be something else.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-13 06:35 PM . Last Modified: 2024-10-13 07:39 PM
With OPC UA, as with many client-server setups, there could be many reasons, but some questions:
The "An existing connection was forcibly closed by the remote host" (if Google Translate is correct) error suggests that you're connecting to the OPC UA server port successfully but the application, Windows, or something in between like an NIPS, is actively disconnecting you. Often seen by a TCP reset flag being received at the client (should be able to see this in Wireshark or any packet capture setup you might have) but can be something else.