MQTT Driver in Geo SCADA Expert 2019

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • MQTT Driver in Geo SCADA Expert 2019
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
323
AndrewScott
Admiral AndrewScott
118
BevanWeiss
Spock BevanWeiss
100
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
vpartinov
Crewman vpartinov
Crewman

Posted: ‎2020-06-18 01:28 AM . Last Modified: ‎2023-05-03 12:13 AM

0 Likes
11
5011
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-18 01:28 AM . Last Modified: ‎2023-05-03 12:13 AM

MQTT Driver in Geo SCADA Expert 2019

Someone having problems with the new MQTT JSON Schema A driver? 

 

I decided to test it, so everything works fine until I found out the data is not stored into historian. The configuration, the broker, the json format, everything is fine, even in the log files it recognizes the values and timestamps, it associated the topics, items and points. No error in the log files but there are nothing in the historian of the points. Also in ViewX the connection with broker is good, but for the current values of the points there are nothing (Waiting for initial data) even though in the log file says that there are data for these points. 

 

Labels
  • Labels:
  • Drivers
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2020-06-18 08:38 AM

0 Likes
10
4982
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-18 08:38 AM

Hi,

 

It could be that the data format is incorrect? The format requires a timestamp value and point names/values. If there is no timestamp then data will not be processed.

 

An example is:

{
    "time": 1592493746,
    "Analog1": 51
}

The time is a 'unix epoch' number of seconds since 1 Jan 1970, and the point 'Tag' field should be "Analog1" in this case.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2020-06-18 08:38 AM

0 Likes
10
4983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-06-18 08:38 AM

Hi,

 

It could be that the data format is incorrect? The format requires a timestamp value and point names/values. If there is no timestamp then data will not be processed.

 

An example is:

{
    "time": 1592493746,
    "Analog1": 51
}

The time is a 'unix epoch' number of seconds since 1 Jan 1970, and the point 'Tag' field should be "Analog1" in this case.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Rich-C
Lieutenant JG Rich-C
Lieutenant JG

Posted: ‎2022-08-25 12:36 PM

In response to sbeadle
0 Likes
9
4017
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-25 12:36 PM

Hello,

 

So I am having the same issues I cant get values to show even though my broker and device are showing healthy communication. 

 

I have 3 sensors Temperature & Humidity , Moisture and C02 values I am trying to show. 

 

How can I check to see if Geo SCADA is pulling the data? 

 

 

 

Thanks, 

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2022-08-26 02:34 AM

In response to Rich-C
0 Likes
8
4001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-26 02:34 AM

Please check the driver log file, usually at:

C:\ProgramData\Schneider Electric\ClearSCADA\Logs\Drivers\DriverMQTT_001.log (and 002, ...)

The JSON needs to be formatted correctly, and the point configuration needs to match the point names in the JSON string.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Rich-C
Lieutenant JG Rich-C
Lieutenant JG

Posted: ‎2022-08-29 11:27 AM

In response to sbeadle
0 Likes
7
3968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-29 11:27 AM

Hello, Sbeadle

 

 

Thanks for the response. 

 

might need a little more assistance with matching the JSON string with Tag in GeoSCADA.

 

 

So, after reviewing the logs I can see the ID, class, state and name of the points. what do I have to match in geoscada?  below is the log maybe you can advise me which one?

 

Thanks again..

 

Logging started at 25-AUG-2022 20:27:44.958 (UTC)
File : C:\ProgramData\Schneider Electric\ClearSCADA\Logs\Drivers\DriverMQTT_001.log
System : Microsoft Windows 10 Professional Edition, 64-bit (10.0.19044)
CPU : 1 x Intel Unknown Family 6, Model 165, Stepping 2
Intel(R) Core(TM) i7-10750H CPU @ 2.60GHz
ClearSCADA Core : Build 6.83.8017.1 (Release)
Local time zone : UTC-04:00 (Daylight)
Process ID : 16388
Computer : RICH-LAPTOP
Driver : MQTT
Started : 25-AUG-2022 20:27:44.668
Uptime : 0 00:00:00.291

Logging options:
APP : Application
ERR : Errors
OBJ : Database Objects
PNT : Points
REQ : Requests (Actions)
DAT : Point Updates (Data)
PER : Paho Errors
Threads:
16392 : Main
-------------------------------------------------------------------------------
Registry settings:
HKEY_LOCAL_MACHINE\Drivers\ErrorMsgBox = False
HKEY_LOCAL_MACHINE\Drivers\HeartbeatEavesdrop = False
HKEY_LOCAL_MACHINE\Drivers\ServerPollInterval = 5000
HKEY_LOCAL_MACHINE\Drivers\AsyncPointRequests = True
HKEY_LOCAL_MACHINE\Drivers\SecondaryDataMaxPointUpdates = 250
HKEY_LOCAL_MACHINE\Drivers\MaxPendingAsyncPointRequests = 300
HKEY_LOCAL_MACHINE\Drivers\ValueMapScanningInterval = 1000
HKEY_LOCAL_MACHINE\Drivers\SelectBestChannel = False
HKEY_LOCAL_MACHINE\Drivers\BreakDuration = 100
HKEY_LOCAL_MACHINE\Drivers\PostHangupDelay = 0
HKEY_LOCAL_MACHINE\Drivers\TimeJumpLimit = 50
HKEY_LOCAL_MACHINE\Drivers\RequestTimeout = 600
HKEY_LOCAL_MACHINE\Drivers\RequestTimeoutExtn = 300
HKEY_LOCAL_MACHINE\Drivers\ScannerCommandTimeout = 30
HKEY_LOCAL_MACHINE\Drivers\ScannerRequestTimeout = 180
HKEY_LOCAL_MACHINE\Drivers\EavesdropPSTNTimeout = 30
HKEY_LOCAL_MACHINE\Drivers\RxFailureLimit = 10
HKEY_LOCAL_MACHINE\Drivers\TxFailureLimit = 10
HKEY_LOCAL_MACHINE\Drivers\RetryAssignInterval = 30
HKEY_LOCAL_MACHINE\Drivers\RxTimeoutLimit = 20
HKEY_LOCAL_MACHINE\Drivers\TxTimeoutLimit = 20
HKEY_LOCAL_MACHINE\Drivers\GracefulSocketCloseTimeout = 1000
HKEY_LOCAL_MACHINE\Drivers\AllowInboundConFromAllOS = False
HKEY_LOCAL_MACHINE\Drivers\DirectOnDemandRetryPeriod = 120
HKEY_LOCAL_MACHINE\Drivers\PortServerSettingsTimeout = 10
HKEY_LOCAL_MACHINE\Drivers\ComtrolFreeportDelay = 250
HKEY_LOCAL_MACHINE\Drivers\MaxBatchWriteSize = 1000
HKEY_LOCAL_MACHINE\Drivers\ListenPortRangeStart = 0
HKEY_LOCAL_MACHINE\Drivers\ListenPortRangeEnd = 0
HKEY_LOCAL_MACHINE\Drivers\ResolveNameRetryInterval = 300
HKEY_LOCAL_MACHINE\Drivers\ResolveNameRetryTimeLimit = 10
HKEY_LOCAL_MACHINE\Drivers\PointStatInterval = 4
HKEY_LOCAL_MACHINE\Drivers\PointStatTopX = 25
HKEY_LOCAL_MACHINE\DriverMQTT\LogEnableTelnet = False
25-AUG-2022 20:27:46.280 [Main] Database classes (21)...
Name |Type
------------------------+----------------
CProfile |Resource
CProfileFloat |Resource
CProfileULong |Resource
CProfileLong |Resource
CAdvBITValueMap |Resource
CAdvBYTEValueMap |Resource
CAdvWORDValueMap |Resource
CAdvDINTValueMap |Resource
CAdvUDINTValueMap |Resource
CAdvREALValueMap |Resource
CAdvDOUBLEValueMap |Resource
CAdvStringValueMap |Resource
CDynacardStore |Resource
CAdvOutstation |Modem
CSSLCertificate |Resource
CSSLCertificateAndKey |Resource
CMQTTBroker |Channel
CJSONSchemaAPntDigital |Point
CJSONSchemaAPointAnalog |Point
CJSONSchemaAPntCounter |Point
CJSONSchemaADevice |Outstation
------------------------+----------------
25-AUG-2022 20:27:46.287 [Main] Creating all objects
25-AUG-2022 20:27:46.287 [Data Cache] Started new thread (ID=18116)
25-AUG-2022 20:27:46.288 [Main] Creating objects for class "CMQTTBroker"
25-AUG-2022 20:27:46.288 [Main] Creating "Demo.Aranet.MQTT.New Broker" [CMQTTBroker,7524]
25-AUG-2022 20:27:46.289 [Main] Finished creating objects for class "CMQTTBroker", 1 Objects
25-AUG-2022 20:27:46.289 [Main] Creating objects for class "CJSONSchemaAPntDigital"
25-AUG-2022 20:27:46.290 [Main] Finished creating objects for class "CJSONSchemaAPntDigital" 0 Objects
25-AUG-2022 20:27:46.290 [Main] Creating objects for class "CJSONSchemaAPointAnalog"
25-AUG-2022 20:27:46.290 [Main] Creating "Demo.Aranet.MQTT.Co2" [CJSONSchemaAPointAnalog,7529]
25-AUG-2022 20:27:46.291 [Main] Creating "Demo.Aranet.MQTT.Temperature and Humidity" [CJSONSchemaAPointAnalog,7526]
25-AUG-2022 20:27:46.291 [Main] Finished creating objects for class "CJSONSchemaAPointAnalog", 2 Objects
25-AUG-2022 20:27:46.292 [Main] Creating objects for class "CJSONSchemaAPntCounter"
25-AUG-2022 20:27:46.292 [Main] Creating "Demo.Aranet.MQTT.Moisture" [CJSONSchemaAPntCounter,7527]
25-AUG-2022 20:27:46.293 [Main] Finished creating objects for class "CJSONSchemaAPntCounter", 1 Objects
25-AUG-2022 20:27:46.293 [Main] Creating objects for class "CJSONSchemaADevice"
25-AUG-2022 20:27:46.294 [Main] Creating "Demo.Aranet.MQTT.Aranet" [CJSONSchemaADevice,7525]
25-AUG-2022 20:27:46.305 [Main] Finished creating objects for class "CJSONSchemaADevice", 1 Objects
25-AUG-2022 20:27:46.305 [Main] Finished creating all objects
25-AUG-2022 20:27:46.305 [Main] Initialising all objects
25-AUG-2022 20:27:46.309 [Main] (id=7524) SubObj:Demo.Aranet.MQTT.Aranet(id=7525) CDrvMQTTSubscriptionObject::SetSubscriptionState() Disconnected to SUBSCRIBE Pending Healthy Connection
25-AUG-2022 20:27:46.311 [Main] Paho {3} =========================================================
25-AUG-2022 20:27:46.311 [Main] Paho {3} Trace Output
25-AUG-2022 20:27:46.311 [Main] Paho {3} Product name: Eclipse Paho Asynchronous MQTT C Client Library
25-AUG-2022 20:27:46.311 [Main] Paho {3} Version: 1.3.0
25-AUG-2022 20:27:46.311 [Main] Paho {3} Build level: 2019-04-10T12:19:29Z
25-AUG-2022 20:27:46.311 [Main] Paho {3} OpenSSL version: OpenSSL 1.1.0j 20 Nov 2018
25-AUG-2022 20:27:46.311 [Main] Paho {3} OpenSSL flags: compiler: cl
25-AUG-2022 20:27:46.311 [Main] Paho {3} OpenSSL build timestamp: built on: reproducible build, date unspecified
25-AUG-2022 20:27:46.311 [Main] Paho {3} OpenSSL platform: platform: VC-WIN64A
25-AUG-2022 20:27:46.311 [Main] Paho {3} OpenSSL directory: OPENSSLDIR: "D:\dev\SDKs\OpenSSL\misc\64DR"
25-AUG-2022 20:27:46.311 [Main] Paho {3} =========================================================
25-AUG-2022 20:27:46.338 [Main] a18ca05564134879ab3e29cd0971334f.s2.eu.hivemq.cloud:8883,clientId-x73hOp0W7i CDrvMQTTBroker::SetConnectionState() Disconnected to Starting
25-AUG-2022 20:27:46.338 [Main] a18ca05564134879ab3e29cd0971334f.s2.eu.hivemq.cloud:8883,clientId-x73hOp0W7i CDrvMQTTConnection::Connect()
25-AUG-2022 20:27:46.339 [Main] Finished initialising all objects
25-AUG-2022 20:27:46.339 [Main] Database objects (5)...
Id|Class |State |Reqs|Rply|Name
--------+------------------------+--------+----+----+--------------------------
7524|CMQTTBroker |Synced | 0| 0|Demo.Aranet.MQTT.New Broker
7525|CJSONSchemaADevice |Synced | 0| 0|Demo.Aranet.MQTT.Aranet
7526|CJSONSchemaAPointAnalog |Synced | 0| 0|Demo.Aranet.MQTT.Temperature and Humidity
7527|CJSONSchemaAPntCounter |Synced | 0| 0|Demo.Aranet.MQTT.Moisture
7529|CJSONSchemaAPointAnalog |Synced | 0| 0|Demo.Aranet.MQTT.Co2
--------+------------------------+--------+----+----+--------------------------
25-AUG-2022 20:27:47.924 [18152] a18ca05564134879ab3e29cd0971334f.s2.eu.hivemq.cloud:8883,clientId-x73hOp0W7i CDrvMQTTConnectListener::on_success()
25-AUG-2022 20:27:47.924 [18152] Sending event MQTT connect request succeeded to "Demo.Aranet.MQTT.New Broker" from scanner
25-AUG-2022 20:27:47.924 [18152] a18ca05564134879ab3e29cd0971334f.s2.eu.hivemq.cloud:8883,clientId-x73hOp0W7i CDrvMQTTConnectListener::on_success()
25-AUG-2022 20:27:47.924 [Main] a18ca05564134879ab3e29cd0971334f.s2.eu.hivemq.cloud:8883,clientId-x73hOp0W7i CDrvMQTTBroker::SetConnectionState() Starting to Healthy
25-AUG-2022 20:27:47.925 [Main] a18ca05564134879ab3e29cd0971334f.s2.eu.hivemq.cloud:8883,clientId-x73hOp0W7i Subscribing to topic "Aranet"(Id=7525) using QoS 1
25-AUG-2022 20:27:47.925 [Main] a18ca05564134879ab3e29cd0971334f.s2.eu.hivemq.cloud:8883,clientId-x73hOp0W7i(id=7524) SubObj:Demo.Aranet.MQTT.Aranet(id=7525) CDrvMQTTSubscriptionObject::SetSubscriptionState() SUBSCRIBE Pending Healthy Connection to Waiting For SUBACK
25-AUG-2022 20:27:48.048 [18152] a18ca05564134879ab3e29cd0971334f.s2.eu.hivemq.cloud:8883,clientId-x73hOp0W7i CDrvMQTTSubscribeListener::on_success()
25-AUG-2022 20:27:48.048 [18152] Sending event MQTT subscribe ack to "Demo.Aranet.MQTT.New Broker" from scanner
25-AUG-2022 20:27:48.048 [Main] a18ca05564134879ab3e29cd0971334f.s2.eu.hivemq.cloud:8883,clientId-x73hOp0W7i(id=7524) SubObj:Demo.Aranet.MQTT.Aranet(id=7525) CDrvMQTTSubscriptionObject::SetSubscriptionState() Waiting For SUBACK to SUBSCRIBE Succeeded
25-AUG-2022 20:27:48.048 [Main] a18ca05564134879ab3e29cd0971334f.s2.eu.hivemq.cloud:8883,clientId-x73hOp0W7i CDrvMQTTSubscriptionObject::HandleSubscriptionAck() succeeded
26-AUG-2022 08:27:44.229 [Main] a18ca05564134879ab3e29cd0971334f.s2.eu.hivemq.cloud:8883,clientId-x73hOp0W7i CDrvMQTTConnection::Disconnect()
26-AUG-2022 08:27:44.229 [Main] a18ca05564134879ab3e29cd0971334f.s2.eu.hivemq.cloud:8883,clientId-x73hOp0W7i CDrvMQTTBroker::SetConnectionState() Healthy to Stopping
26-AUG-2022 08:27:44.230 [18148] a18ca05564134879ab3e29cd0971334f.s2.eu.hivemq.cloud:8883,clientId-x73hOp0W7i CDrvMQTTDisconnectListener::on_success()
26-AUG-2022 08:27:44.230 [18148] Sending event MQTT disconnect request succeeded to "Demo.Aranet.MQTT.New Broker" from scanner
26-AUG-2022 08:27:44.435 [Data Cache] Thread terminated (ID=18116)
26-AUG-2022 08:27:44.438 [Main] Driver stopped after 0 11:59:59.770
-------------------------------------------------------------------------------
Logging stopped at 26-AUG-2022 08:27:44.438 (UTC)

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2022-08-30 02:38 AM

In response to Rich-C
0 Likes
6
3959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-08-30 02:38 AM

Screenshot 2022-08-30 103653.jpg

 

Check both your topic name and the tag name. The Tag name in the JSON must match the point configuration.

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Rich-C
Lieutenant JG Rich-C
Lieutenant JG

Posted: ‎2022-09-02 09:03 AM

In response to sbeadle
0 Likes
5
3916
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-02 09:03 AM

Hello,

 

I need some assistance with adding the geoscada node..I am stuck from moving the box files from github to my pc local folder step.

 

Place the files from the Box folder here into a working folder. I used:??????????????????????????????????

Install Node-Red

This guide is for Windows, on other platforms, please find instructions on the Node and Node-Red web sites.

Install Node

  1. Go to https://nodejs.org/en/#home-downloadhead and select the LTS version (currently 12.18.4 LTS) to download.
  2. Install this – you will then be directed to install the Additional Tools – this may work, but if not and you see "The request was aborted: Could not create SSL/TLS secure channel", then you need to follow these steps for the additional tools:
    1. Download and install the latest Powershell from: https://github.com/PowerShell/PowerShell
    2. Edit the file: "C:\Program Files\nodejs\install_tools.bat" and replace "%SystemRoot%\System32\WindowsPowerShell\v1.0\powershell.exe" with "C:\Program Files\PowerShell\7\pwsh.exe" in two places on the last line.
    3. Run this batch file and check for success.
    4. (Link to this additional fix: https://github.com/nodejs/node/issues/33140 )

(These commands may not work through a web proxy or PAC file such as in a company network.)

Install Node-Red

Start "Node.js command prompt" from the Start menu (as Admin). Then enter:

npm install -g --unsafe-perm node-red

This will install node-red, taking a few minutes.

Our node needs a package called xml2js, so also run:

npm install -g --unsafe-perm xml2js

(These commands may not work through a web proxy or PAC file such as in a company network.)

Add the Geo SCADA node

Spoiler
Place the files from the Box folder here into a working folder. I used:??????????????????????????????????

C:\Users\<your user id>\AppData\Roaming\npm\node_modules\node-red

The files are in a subfolder named "node-dev-geoscada":

Then from the Node.js command prompt execute:

npm install C:\Users\Administrator\AppData\Roaming\npm\node_modules\node-red\node-dev-geoscada

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2022-09-05 02:48 AM

In response to Rich-C
0 Likes
4
3857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-05 02:48 AM

Your title implies you want to use MQTT, but the content is from a document describing how to use the Geo SCADA web services with Node-Red. So what do you want to do - MQTT or web services?

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Rich-C
Lieutenant JG Rich-C
Lieutenant JG

Posted: ‎2022-09-06 07:03 AM

In response to sbeadle
0 Likes
3
3809
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-06 07:03 AM

Hello, Mr. sbeadle

 

I want to configure MQTT in GeoScada but your instructions are not clear to  me I am not a programmer or developer so I was trying to mimic the screenshot you posted and I saw you were using NODE-Red to show the data tag "Analog1" which I don't see in my logs.

 

I posted my logs of the MQTT driver and you mentioned to match it with the tag in GEOSCADA but the logs do not show the same tag name as the one you have " Analog1". 

 

 

I have tried to match all 3 tag names from my logs to GEOSCADA and I still don't get DATA. 

 

 

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2022-09-09 06:27 AM

In response to Rich-C
0 Likes
2
3766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-09 06:27 AM

Please see these release notes: https://schneider-electric.box.com/shared/static/2790008bt5j5j5victze9r5cln6bea36.pdf

Find the MQTT section on page 26, and follow the instructions there.

BUT note the command line for mosquitto_pub is incorrect, it should be:

mosquitto_pub -h 127.0.0.1 -p 1883 -t /East\MyDevice1 -m "{\"time\":1559225529, \"Analog1\":12.3}"

 

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Rich-C
Lieutenant JG Rich-C
Lieutenant JG

Posted: ‎2022-09-20 01:34 PM

In response to sbeadle
0 Likes
1
3616
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-20 01:34 PM

Hello Support,

 

I have tested moquitto broker and the test was successful with publishing and subscribing the the test data. 

 

I'm still not sure why Geoscada is not getting the data.

 

Is there a support phone number I can call? or a remote support I can schedule?

  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

AndrewScott
Admiral AndrewScott
Admiral

Posted: ‎2022-09-21 01:18 AM

In response to Rich-C
0 Likes
0
3600
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-21 01:18 AM

@Rich-C The contact details for customer support are here:

https://community.se.com/t5/Geo-SCADA-Knowledge-Base/Geo-SCADA-Expert-Support/ba-p/279117 


Andrew Scott, R&D Principal Technologist, AVEVA
  • Tags:
  • english
  • scada
  • SCADA app
  • SCADA software
  • SCADA tutorial
  • Telemetry and SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore