[Imported] Voice alarm annunciation and voice telephony support

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • [Imported] Voice alarm annunciation and voice telephony support
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
319
AndrewScott
Admiral AndrewScott
114
BevanWeiss
Spock BevanWeiss
97
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
39
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 09:37 AM . Last Modified: ‎2023-05-03 12:28 AM

0 Likes
3
3807
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 09:37 AM . Last Modified: ‎2023-05-03 12:28 AM

[Imported] Voice alarm annunciation and voice telephony support

>>Message imported from previous forum - Category:ClearSCADA Software<<
User: Roughneck42, originally posted: 2019-01-23 19:50:24 Id:353
A client put the following in a spec. for a new SCADA system..
"The HMI shall be capable of generating all specified alarms and notify operators via voice, SMS or email. All alarms shall be logged for viewing and reporting purposes. All alarms shall be locally enunciated via HMI software and speakers."

Wondering how best to handle the voice notification and local enunciation requirements...

Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-11-06 09:37 AM

0 Likes
2
3805
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 09:37 AM

>>Responses imported from previous forum


Reply From User: adamwoodland, posted: 2019-01-23 22:01:03
I know some customers have used SCADAPhone to read out alarms to uses via the phone, that might have something for doing the same via speakers but I don't know.


Reply From User: JesseChamberlain, posted: 2019-01-24 01:00:00
I would be asking for clarification on whether they actually want the whole alarm read out or the bell is enough locally....

Otherwise a system call to some command line text to speech program?


Reply From User: sbeadle, posted: 2019-01-24 08:20:22
It would be an easy setup to link the ClearSCADA alarm redirection to twilio.com for SMS and Voice alarms. The simplest way is to send emails from ClearSCADA. The next step would be to use a system command alarm redirection which starts up a program to send the message through twilio's web service - and maybe write the results back to ClearSCADA's database.


Reply From User: BevanWeiss, posted: 2019-01-24 11:46:17
As the others have noted, ClearSCADA doesn't support Voice based alarm redirections internally, although it does have good enough support for SMS and Email based.
We've used twilio before along with a very basic command line executable to perform Twilio interaction which allows for text-to-speech to be used in calling a phone number.
More complex interactions, such as IVR (Interaction Voice Response) can be built up using Twilio, but the complexity increases quite dramatically beyond the simple make a phone call and speak some words (which is absolutely trivial).

My concern with Twilio has always been the reliability of it.
a) it requires that you have a working internet connection from the ClearSCADA server to the Twilio server
b) it requires that the Twilio service is available to serve your request
c) it requires that your administration hasn't failed to pay the Twilio fees
d) it requires all of the Telecom provider services to allow the phone call to be contacted to the operator phone number.

This has always seemed a bit 'unreliable' to me, especially given that so much of this isn't under direct OT control. But trying to find voice capable modems to do most of it inhouse is almost impossible these days, and packages like SCADA Phone have their own issues


Reply From User: sbeadle, posted: 2019-01-24 12:06:51
All good points. The weakest point is the data uplink, which these days is comparable to relying on phone calls, 3G or SMS to send alarms, so in my view it's a reasonable solution rather than adding on external software.


Reply From User: geoffpatton, posted: 2019-01-24 18:38:02
Win 911 does voice calling.
I don't really like it though.
It requires a specific type of Modem.
I had to jump through hoops to get it working with redundant pair of servers because only one server is main. Then you have to setup all the alarms in it.
If it is restarted it will call out all the active alarms again.
I had one customer using this and I only came in after their original integrator disappeared and then I just had to make sure things worked as they upgrade versions and computers.


Reply From User: BevanWeiss, posted: 2019-01-24 19:45:09
I would preference SCADA Phone over Win911... but I would preference almost anything else above SCADA Phone.

It would be nice if there was a way for people to write proper Alarm Redirection drivers (which the Simple DDK doesn't really provide for), as then things like SIP / Skype / WhatsApp / Viber / Smoke signal integration could be added...
Cludging around it with method call redirections which trigger System commands which execute custom executables or batch files really isn't a great way, and tends to be a one way street, or requires magic trust in configurations for two way.


Reply From User: adamwoodland, posted: 2019-01-24 22:28:16
I've been contemplating writing an interface from ClearSCADA to Microsoft Flow, which would be pretty cool. But that is as far as it has got so far 🙂


Reply From User: Roughneck42, posted: 2019-01-24 22:52:04
thanks for the pointers, but there needs to be a native solution, the water companies seem to demand voice support. other scada systems provide this and support hardware like the Multitech MT9234MU-CDC-XR


Reply From User: BevanWeiss, posted: 2019-01-27 00:48:12
[at]Roughneck42 when you say 'other scada systems provide this', which SCADA systems are you referring to exactly?
FactoryTalk ViewSE, CitectSCADA, WinCC SCADA, iFix SCADA, InTouch etc etc etc do not support voice call alarm escalation natively. The majority of them don't even support proper alarm escalation.


Reply From User: BevanWeiss, posted: 2019-01-27 01:04:25
[at]adamwoodland I was all excited by your mention of Microsoft Flow, but looking more into it, it's got some pretty harsh limitations. The On-premises Data Gateway doesn't support custom data sources (only SQL Server, SharePoint, Oracle, Informix, Filesystem, DB2). Which limits what would be able to be done with a ClearSCADA connector.

That would mean that it would be possible to query the alarms (via SQL server linked ClearSCADA) however acknowledging the alarms based upon a flow action wouldn't be possible (without horrible hacks, like putting a file into a directory which means acknowledge).

Certainly willing to help out where practicable if I'm wrong on this however..


Reply From User: Roughneck42, posted: 2019-01-28 23:24:39
VTSCADA (https://www.trihedral.com/scada-alarm-notification) and Ignition (https://docs.inductiveautomation.com/display/DOC/Voice+Notification+Module) come to mind as supporting this functionality. win911 is not an option as the need to support two databases is a no go.


Reply From User: Roughneck42, posted: 2019-01-30 16:13:16
[at]sbeadle said:
It would be an easy setup to link the ClearSCADA alarm redirection to twilio.com for SMS and Voice alarms. The simplest way is to send emails from ClearSCADA. The next step would be to use a system command alarm redirection which starts up a program to send the message through twilio's web service - and maybe write the results back to ClearSCADA's database.

so I would be grateful of any technical documents detailing how this can be achieved....


Reply From User: sbeadle, posted: 2019-02-01 17:19:30
Using a system command to redirect alarms to a .exe with parameters requires you to create an alarm redirection 'System Command Action'. This has a 'Command' field, which needs to be something like:
c:\\myfolder\\mycommand.exe "%OAlarmDesc%" "%ACondName%" "%ASeverity%" "%ACondActiveDateTime%" "%ASubCondActiveDateTime%" "%ASubCondName%" "%OFullName%"

To send all alarm state changes, edit the root group properties on your system and add a single redirection on the 'Redirection' tab: fields on the line are:
Auto, Always, your-action, Low, Critical, Region=empty, Delay=0, Never, 0

You can alter what fields are sent to the system - the above list may also need "%OStateAreaOfInterest%" if you are using AoI and want the user to know it.
Then use the twilio API to write a program which connects to twilio and sends the data to whoever needs to know (which can be decided by your program - perhaps by querying the ClearSCADA database too).

Use the twilio messaging API (https://www.twilio.com/docs/sms) or similar.

A down-side to this design is that the command execution starts and ends each time an alarm update is done. A more efficient way would be to put this code in a DDK driver as a Method on a single 'channel' object. Then use a Method redirection instead of a System Command redirection, with the same parameters. The Method is passed to the driver process which handles the notification asynchronously. The driver process can also use the Twilio API to read incoming messages such as for alarm ack or delivery notifications.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-01-30 11:26 AM . Last Modified: ‎2020-02-03 08:05 AM

In response to sbeadle
0 Likes
1
3734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-30 11:26 AM . Last Modified: ‎2020-02-03 08:05 AM

Good afternoon, 

 

You can find on internet all the content about Voice for WIN-911. 

The answer is yes! 

 

Also earlier this month we came up with a new Notifier function "Announcer".

 

Last, this is not a voice notifier but what a lot of our customers moving to WIN-911 Mobile App.

 

Please don't hesitate to contact me by direct message with any other questions. 

 

You can purchase WIN-911 via shop.Exchange.se.com.

 

Regards, 

 

Arish Rojas 

WIN-911 Software

North America Channel Manager 

 

  • Tags:
  • alarms
  • telephony support
  • voice
  • WIN-911
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2020-01-31 01:17 PM . Last Modified: ‎2024-01-29 08:13 AM

In response to Anonymous user
1 Like
0
3714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-31 01:17 PM . Last Modified: ‎2024-01-29 08:13 AM

Thanks.

LINKS EDITED 29 JAN 2024.

Note that Geo SCADA 2019 now has enhanced Alarm Redirection features, and can now pass contact information to alarm redirection methods, leading to easy integration with modern cloud-based voice notification systems such as Twilio.

 

There's an example in the 2019 release notes (Link: https://download.schneider-electric.com/files?p_Doc_Ref=Geo_SCADA_2019_RelNotes_202212&p_enDocType=O...  ) showing what to do, and full implementation details on GitHub at https://github.com/GeoSCADA/Driver-Notify/blob/master/NotifyDemo%20Description.pdf 

 

Geo SCADA allows configuration of alarm notification via its redirection features, allowing the choice of notification types such as email, SMS and now voice. User accounts can be configured with multiple contact details. The rules-based configuration includes features for redirection based on time of day, alarm severity, place in hierarchy and Area of Interest, multiple sends with rosters, calendars and schedules and geographical co-ordinates of the alarm and users.

 

SMS, email and voice notification all include capabilities for alarm acknowledgement, with built-in security features, and redirection can also include escalation and the filtering of actions if users are already logged in.

 

Steve Beadle - Geo SCADA Expert Programme Manager.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore