Display X-Y plot without time line.

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Display X-Y plot without time line.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
hemanthv
Ensign hemanthv
Ensign

Posted: ‎2020-02-04 08:44 PM . Last Modified: ‎2023-05-03 12:18 AM

0 Likes
5
5695
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-04 08:44 PM . Last Modified: ‎2023-05-03 12:18 AM

Display X-Y plot without time line.

Hi, i am looking for how to display X-Y plot on ClearSCADA Trends not over a time line. 

Some thing similar to one as attached.

 

 

 

Attachments
Labels
  • Labels:
  • SCADA
  • ViewX
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
hemanthv
Ensign hemanthv
Ensign

Posted: ‎2020-02-04 11:19 PM

In response to hemanthv
0 Likes
0
5674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-04 11:19 PM

Crystal reports

See Answer In Context

Attachments
  • Tags:
  • ViewX
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-02-04 09:42 PM

0 Likes
0
5690
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-04 09:42 PM

Remember ClearSCADA / GeoSCADA Expert is NOT Excel.

 

ClearSCADA along with most other SCADA systems has Real-Time Visualisation Elements, and ClearSCADA also provides a Time-Series Historian.  It is not a general database system, and it is not a general chart display engine.

 

In saying that however, there are some possible pathways that you could look into.  And it will be slightly more complicated that you will likely want.

 

DynaCards and DynaGraphs.

DynaCards are a special kind of driver object which Schneider use for their Rod Pump controllers.

These essentially allow for storing a collection of timestamped Position vs Load tuples.  They get labelled against certain 'types' also, i.e. Stored, Shutdown, Malfunction, Reference, Start, Pump Up, Last Stroke...

 

Using a DynaGraph you're able to display a series of DynaCards for a particular 'type'.  i.e. you might have a DynaGraph which has just Stored cards (from a DynaCard Store) on it, or you might have both the Start and the Shutdown cards (to see a charge/discharge hysteresis cycle).

All sounds very magical right.... and here-in lies the problem for you.  It is magical, it's largely tied into Schneider proprietary device systems.  Which you most likely aren't using.  That means that you'll need to push the data into these DynaCard Stores yourself.

 

From your ClearSCADA server you can access the schema for the items here:

https://localhost/schema/CDynacardStore

 

You'll see there is a convenient Method called 'InsertRecords'.

 

I've just given it a try, and it kind of works.  I think I've run into a bug with it where it's not connecting lines.

But perhaps I'm just using it wrong.  There are a few other enhancement that I think it should have, as I mentioned, it's mainly used around Schneider Rod Pump controllers, so the typical audience is small for its functionality (and hence it may have bugs, and non-ideal behaviour).DynaCard.png


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-02-04 10:24 PM

0 Likes
3
5686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-04 10:24 PM

Duhh.... and actually I forgot about how the X-Y Plot even works also.

 

The timeline shown in the X-Y Plot is the window over which the data within the display is for.  The X-Y mapping of the X-Y plot is still based purely upon the sampled values of the X and Y points.

So the X-Y Plot is potentially what you will care about if you'll go through your unique X-Y values over some particular period of time (i.e. you care about the X-Y relationship only over the past hour/day/week/month/year etc...).

If you want unique stored X-Y samples, then the DynaCard/DynaGraph is still the way forward.

 

Here's an example of X-Y Plot... this should have been a pure bowl if it was only considering the X-Y mapping.... (i.e. the lines on the top should not exist.. they are artifacts from the time series impact I believe.. I wasn't able to find a historic algorithm that prevented these)

X-Y Plot.png


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
Reply

Link copied. Please paste this link to share this article on your social media post.

hemanthv
Ensign hemanthv
Ensign

Posted: ‎2020-02-04 11:11 PM

In response to BevanWeiss
0 Likes
2
5680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-04 11:11 PM

Yes, as per your last post.. Tried to use X-Y Trend.

X and Y values where in manually entered using ST with Time stamp. Once done same was mapped onto X-Y Trends. I was stuck with one problem. How to manually change the time to specific time using script on X-Y Trends.

 

Other option which also works is Storing information using ST in DataTable with X,Y columns and Displaying them on Crystal Reports directly. SQL Query Functions to insert values into DataTable.

 

I will try the Dynagraph but as of now we are going to settle with Option of crystal reports.

 

Thanks.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

hemanthv
Ensign hemanthv
Ensign

Posted: ‎2020-02-04 11:18 PM

In response to hemanthv
0 Likes
1
5677
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-04 11:18 PM

Crystal report displayed with graph..

 

 

 
  • Tags:
  • ViewX
Reply

Link copied. Please paste this link to share this article on your social media post.

hemanthv
Ensign hemanthv
Ensign

Posted: ‎2020-02-04 11:19 PM

In response to hemanthv
0 Likes
0
5675
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-02-04 11:19 PM

Crystal reports

Attachments
  • Tags:
  • ViewX
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore