[Imported] Alarm lists and alarm bell

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • [Imported] Alarm lists and alarm bell
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
319
AndrewScott
Admiral AndrewScott
114
BevanWeiss
Spock BevanWeiss
97
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
39
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-10-25 03:38 PM . Last Modified: ‎2023-05-03 12:39 AM

0 Likes
3
2852
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-10-25 03:38 PM . Last Modified: ‎2023-05-03 12:39 AM

[Imported] Alarm lists and alarm bell

>>Message imported from previous forum - Category:ClearSCADA Software<<
User: florian, originally posted: 2018-10-24 19:29:14 Id:192
This is a re-posting from the obsoleted (October 2018) "Schneider Electric Telemetry & SCADA" forum.

-----------------

**_hardin4019:_**
**_Is it possible to get the alarm bell with the count of unacknowledged, acknowledged alarms, and silence bell to show up on an alarm list that is imbedded in a mimic and prefiltered?_**

---------------------------

bevanweiss:
Not that I'm aware of. Apart from the actual bell sound, the rest could all be emulated with mimic graphics and animations. But I'm not sure it would have much benefit.

Are you wanting a completely separate Alarm Banner pre-filtered at the bottom of every site / area?

That does conflict with the original intended purpose of the Alarm Banner, which was specifically to show you alarms which you may not be directly looking at on your current mimic view / alarm panel. A filtered Alarm List isn't sufficient?

----------------------

**_hardin4019:_**
**_What was requested was a single mimic with 3 diferent alarm lists. Each list is filtered to include only certain severities. One list for Critical, One List for High and Medium, One list for Low and Alert. The idea being that in the near future, the work stations the controllers sit at will have more monitors, and can have an entire Monitor dedicated to this alarms list screen._**

------------------------------

AWoodland:
Whilst not quite what is asked, have you looked into the fullscreen alarm banner feature? Basically you set a head to be an alarm banner only, no mimics/etc (they all get opened on another head)

The bell is attached to the banner, not alarm lists, so you can't make the beeps from lists.


----------------------------

**_hardin4019:_**
**_I had thought the same thing, but that wasn't what was requested. I did end up using the alarm lists and making my own Queries and points to count the number of alarms and make my own icons. Not as simple as the alarm banner, but it falls right in line with what was requested and it appears to work fine so far._**

 

 

Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-10-25 03:39 PM

0 Likes
2
2851
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-10-25 03:39 PM

>>Responses imported from previous forum


Reply From User: martin_froehner, posted: 2019-05-16 14:01:05
Hi,
is it possible to just get the bell from the alarm banner? Or even better the functionality to acknowledge the sound of an alarm. For better understanding: We build our own Alarmlist, cause the "built in Version" is not enough for our customer. Everything works with the list. But now we have a customer who wants an alarm sound to be played when an alarm occurs. Which is also working. Now we need a button or something else to acknowledge the sound, cause otherwise it won't stop. And our customer doesn't want the standard alarm banner at all. Can I somehow include the Alarmbanner in a mimic? So I could hide everything except the button? Or do you have any other idea on how to solve the problem?

Regards,
Martin


Reply From User: hardin4019, posted: 2019-05-20 20:33:47
Is the alarm sound assigned to the alarm "Severity" in the Server Configuration tool under Severities? If so, it should stop sounding once acknowledged or the alarm bell silenced by clicking on the red flashing box in the "built in alarm banner".

Being able to silence the alarm sound from a custom alarm Mimic or inset Alarm List is something I had never figured out and from the looks of things, wasn't available to be done outside of the built in alarm banner.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2019-10-25 03:39 PM

0 Likes
2
2852
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-10-25 03:39 PM

>>Responses imported from previous forum


Reply From User: martin_froehner, posted: 2019-05-16 14:01:05
Hi,
is it possible to just get the bell from the alarm banner? Or even better the functionality to acknowledge the sound of an alarm. For better understanding: We build our own Alarmlist, cause the "built in Version" is not enough for our customer. Everything works with the list. But now we have a customer who wants an alarm sound to be played when an alarm occurs. Which is also working. Now we need a button or something else to acknowledge the sound, cause otherwise it won't stop. And our customer doesn't want the standard alarm banner at all. Can I somehow include the Alarmbanner in a mimic? So I could hide everything except the button? Or do you have any other idea on how to solve the problem?

Regards,
Martin


Reply From User: hardin4019, posted: 2019-05-20 20:33:47
Is the alarm sound assigned to the alarm "Severity" in the Server Configuration tool under Severities? If so, it should stop sounding once acknowledged or the alarm bell silenced by clicking on the red flashing box in the "built in alarm banner".

Being able to silence the alarm sound from a custom alarm Mimic or inset Alarm List is something I had never figured out and from the looks of things, wasn't available to be done outside of the built in alarm banner.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-01-30 11:41 AM . Last Modified: ‎2020-02-03 08:02 AM

In response to sbeadle
0 Likes
1
2732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-30 11:41 AM . Last Modified: ‎2020-02-03 08:02 AM

Good afternoon, 

 

If you would like for the Alarm Tag to be read out loud to you.

WIN-911 came out with a new Notifier function "Announcer"  earlier this month.

 

Also, here is a link that will help you if you would like a Voice call for WIN-911. 

 

Last, this is not a voice notifier but what a lot of our customers moving to WIN-911 Mobile App

 

Please don't hesitate to contact me by direct message with any other questions. 

 

You can purchase WIN-911 via shop.Exchange.se.com. 

 

Regards, 

 

Arish Rojas 

WIN-911 Software

North America Channel Manager 

Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2020-01-31 01:16 PM

In response to Anonymous user
0 Likes
0
2712
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-01-31 01:16 PM

Thanks.

 

Note that Geo SCADA 2019 now has enhanced Alarm Redirection features, and can now pass contact information to alarm redirection methods, leading to easy integration with modern cloud-based voice notification systems such as Twilio.

 

There's an example in the 2019 release notes (Link: https://schneider-electric.box.com/shared/static/zbqrws07ln0mt3wbf0j5e0mxbv1vnvls.pdf ) showing what to do, and full implementation details on github.

 

Geo SCADA allows configuration of alarm notification via its redirection features, allowing the choice of notification types such as email, SMS and now voice. User accounts can be configured with multiple contact details. The rules-based configuration includes features for redirection based on time of day, alarm severity, place in hierarchy and Area of Interest, multiple sends with rosters, calendars and schedules and geographical co-ordinates of the alarm and users.

 

SMS, email and voice notification all include capabilities for alarm acknowledgement, with built-in security features, and redirection can also include escalation and the filtering of actions if users are already logged in.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore