Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

[Imported] Deleting Template- Two step verification

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • Re: [Imported] Deleting Template- Two step verification
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
309
AndrewScott
Admiral AndrewScott
99
BevanWeiss
Spock BevanWeiss
91
AdamWoodlandToo
Lt. Commander AdamWoodlandToo
38
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Solved
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: β€Ž2019-11-26 01:48 PM . Last Modified: β€Ž2023-05-03 12:22 AM

0 Likes
3
1694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2019-11-26 01:48 PM . Last Modified: β€Ž2023-05-03 12:22 AM

[Imported] Deleting Template- Two step verification

>>Message imported from previous forum - Category:General Items<<
User: scottdavis11, originally posted: 2019-09-11 10:43:26 Id:507
I had a problem in my Clear SCADA system when I deleted my Template by mistake.
Is there anyway that a Two Step verification can be added in case of special action like deletion or any other way to avoid apart from Changing permission of the user?

Labels
  • Labels:
  • SCADA
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: β€Ž2019-11-26 01:48 PM

0 Likes
2
1693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2019-11-26 01:48 PM

>>Responses imported from previous forum


Reply From User: BevanWeiss, posted: 2019-09-12 06:30:44
What problem did you have?
If you were deleting a template that has a number of instances then I suspect that you did indeed get a prompt to confirm that you were deleting things... if there are items with history then a prompt appears advising which points and how much history will be deleted.

A deletion isn't really such a special action, it's just a configuration change like all the other configuration changes possible. I'm not sure that ClearSCADA is to blame here πŸ˜‰
With great power comes great responsibility.


Reply From User: scottdavis11, posted: 2019-09-13 08:16:15
Yes thats true 😞 . But is there any way to have two step authentication or to have a confirmation action with password to overcome these issues


Reply From User: BevanWeiss, posted: 2019-09-18 21:36:37
[at]scottdavis11 said:
Yes thats true 😞 . But is there any way to have two step authentication or to have a confirmation action with password to overcome these issues

I'm confused... now you want two step authentication?

For Control actions there is indeed the ability to configure a number of additional verification options per object. For Configuration actions there is nothing similar. If you look into how the Control verification operation is configured, then perhaps you could contact your local Schneider Tech Support and do a feature request for something similar for Configuration changes. If you let me know the SUP reference number for it after then I'd likely +1 it πŸ™‚

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 3
sbeadle
Kirk sbeadle Kirk
Kirk

Posted: β€Ž2019-11-26 01:48 PM

0 Likes
2
1694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2019-11-26 01:48 PM

>>Responses imported from previous forum


Reply From User: BevanWeiss, posted: 2019-09-12 06:30:44
What problem did you have?
If you were deleting a template that has a number of instances then I suspect that you did indeed get a prompt to confirm that you were deleting things... if there are items with history then a prompt appears advising which points and how much history will be deleted.

A deletion isn't really such a special action, it's just a configuration change like all the other configuration changes possible. I'm not sure that ClearSCADA is to blame here πŸ˜‰
With great power comes great responsibility.


Reply From User: scottdavis11, posted: 2019-09-13 08:16:15
Yes thats true 😞 . But is there any way to have two step authentication or to have a confirmation action with password to overcome these issues


Reply From User: BevanWeiss, posted: 2019-09-18 21:36:37
[at]scottdavis11 said:
Yes thats true 😞 . But is there any way to have two step authentication or to have a confirmation action with password to overcome these issues

I'm confused... now you want two step authentication?

For Control actions there is indeed the ability to configure a number of additional verification options per object. For Configuration actions there is nothing similar. If you look into how the Control verification operation is configured, then perhaps you could contact your local Schneider Tech Support and do a feature request for something similar for Configuration changes. If you let me know the SUP reference number for it after then I'd likely +1 it πŸ™‚

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Tanquen
Lt. Commander Tanquen
Lt. Commander

Posted: β€Ž2020-08-24 08:09 PM

In response to sbeadle
0 Likes
1
1483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-08-24 08:09 PM

I just did something similar. At some point there was a paste in the wrong group so I had to open many groups and delete each one. After a few I bumped a key and it went up to the root group and I did not notice until it started to delete everything. 😞

 

I ran a full back up Saturday but I just lost all my work from Sunday and today. 😞 I do not like all the groups and dragging and copying and pasting. It’s too easy to let go in the wrong spot or grab the wrong object.

 

Is there an auto backup to back everything up once an hour or something?

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: β€Ž2020-09-09 06:11 AM

In response to Tanquen
0 Likes
0
1416
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-09-09 06:11 AM

Yes, create a new Backup object, set a folder target and filename format so you get a new backup file each time. Set the backup to save Config, Data and Datafiles only.

Then create a new schedule and edit properties and schedule to set your interval to 1 hour. Then drag the backup onto your schedule in order to trigger it. Voila, an hourly database backup.

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of