[Imported] DNP3 historic not showing any trending
  • Remote Operations
  • [Imported] DNP3 historic not showing any trending
sbeadle
Kirk sbeadle Kirk
319
AndrewScott
Admiral AndrewScott
114
BevanWeiss
Spock BevanWeiss
97
  • Remote Operations Forum
EcoStruxure™ Geo SCADA Expert
sbeadle
Kirk sbeadle Kirk
Kirk
Posted: ‎2019-11-06 02:50 PM . Last Modified: ‎2023-05-03 12:26 AM
864
User: amanshow, originally posted: 2019-04-13 16:51:30 Id:405
Hello, is there any other reasons than not having the same dnp class for the dnp3 tags to now show on trends? Maybe I missed something in the configuration?
I've enabled Historic Logging and even ticked Use Raw Data but it's not showing on the trend.
I would appreciate your help asap. Thanks.
  • SCADA
sbeadle
Kirk sbeadle Kirk
Kirk
Posted: ‎2019-11-06 02:51 PM
Reply From User: dmercer, posted: 2019-04-14 21:48:19
If the data is definitely coming into the server, then I would check the significant change and the historic data filter settings on the Analog Point/Binary Point tab. I normally give dnp3 analog points a significant change with a very small but non-zero number, and the histoirc data filter I set to Static and Event Data.
Reply From User: amanshow, posted: 2019-04-15 07:44:32
Thank you! I realized I haven't set it to Static and Event Data but now it worked.
sbeadle
Kirk sbeadle Kirk
Kirk