Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

[Imported] DNP3 Backfilling

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • [Imported] DNP3 Backfilling
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
sbeadle Champion
335
AndrewScott
AndrewScott
125
BevanWeiss
BevanWeiss
103
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
sbeadle
sbeadle Champion
Champion

Posted: ‎2019-11-06 02:52 PM . Last Modified: ‎2023-05-03 12:25 AM

0 Likes
1
2151
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 02:52 PM . Last Modified: ‎2023-05-03 12:25 AM

[Imported] DNP3 Backfilling

>>Message imported from previous forum - Category:ClearSCADA Software<<
User: amanshow, originally posted: 2019-04-15 08:08:39 Id:406
Good day. It's me again.

I would like to know how to configure DNP3 clearscada backfilling. My employer told me it had something to do with checking unsolicited messages but I've already had it ticked off but the backfilling still hasn't occurred. I would appreciate any help.

Thank you very much.

Labels
  • Labels:
  • SCADA
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sbeadle
sbeadle Champion
Champion

Posted: ‎2019-11-06 02:53 PM

0 Likes
0
2145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 02:53 PM

>>Responses imported from previous forum


Reply From User: amanshow, posted: 2019-04-15 13:03:43
Hello, my partner and I found an error in SCADAPack E Config that says:
System Error Code: 1031
System Error Description: Event Data Lost. An RTU event buffer has overflowed resulting in loss of data.

What do you think we should do? Any help would be very much appreciated.


Reply From User: dmercer, posted: 2019-04-15 22:34:24
Events aren't necessarily sent back to SCADA straight away, they will be stored and will attempt to send them when the limits set on the DNP3 Events property page are reached or when it receives a poll for that class. If comms to SCADA is not healthy then it will continue to store them until the event buffer gets full, at which point the buffer overflow and some data is lost.

I'm guessing that you have Default Enabled Event Classes set to No Classes, the outstation in ClearSCADA is not set to enable unsolicited, and you're not polling all classes often enough.


Reply From User: amanshow, posted: 2019-04-16 08:39:00
I actually have Default Enabled Event Classes set to Class 1, 2, 3 and the outstation is set to enable unsolicited, and my classes have scheduling polled enabled, but all have the same interval of 5S.


Reply From User: geoffpatton, posted: 2019-04-16 14:56:34
Is you SCADA Master address set the same on both ClearSCADA and the SCADAPack?


Reply From User: amanshow, posted: 2019-04-17 03:11:55
Yes, it is.

There's been a progress. The backfill actually worked when I set the timezone to local time (just as my partner set his scadapack rtu to local time)and it backfilled! However, there's something wrong with it because while rtu feeds clearscada values, my historic trend creates' current data for future', as far as I can remember that's how it said but you get the gist of it. Basically, my trend for a certain parameter already has a data on the trend that's currently four hours in advanced (e.g. it's currently 11AM but my trend shows it has data lined up until 3PM) but my current data 'corrects' it on the way.

However, when we enabled our feature of Target Scheduling, the local time blocks the feature from working, and we are forced to turn back to UTC for timezone. That's when the backfill doesn't work anymore. So, basically, we're at loss on what to do. I would appreciate any help.

Thank you all.


Reply From User: geoffpatton, posted: 2019-04-17 14:30:32
Wish I knew the solution for you. We use UTC and it works fine for us. Now DST is a problem. you have to leave that turned off on the computer or everything is off by an hour. We however do not use Targeted Scheduling. Ours are on 4G cellular or fiber and we just periodically poll the Classes and the SCADAPack sends data when its buffers fill.
If we lose connection it back fills when we reconnect.
Years ago there was a firmware issue when a SCADAPack would quit sending data, only thing it sent was it was online. A reboot would fix it for a while. Of course they fixed it in a new firmware. So maybe try a newer or slightly older firmware to see if the firmware is the problem.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
sbeadle
sbeadle Champion
Champion

Posted: ‎2019-11-06 02:53 PM

0 Likes
0
2146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2019-11-06 02:53 PM

>>Responses imported from previous forum


Reply From User: amanshow, posted: 2019-04-15 13:03:43
Hello, my partner and I found an error in SCADAPack E Config that says:
System Error Code: 1031
System Error Description: Event Data Lost. An RTU event buffer has overflowed resulting in loss of data.

What do you think we should do? Any help would be very much appreciated.


Reply From User: dmercer, posted: 2019-04-15 22:34:24
Events aren't necessarily sent back to SCADA straight away, they will be stored and will attempt to send them when the limits set on the DNP3 Events property page are reached or when it receives a poll for that class. If comms to SCADA is not healthy then it will continue to store them until the event buffer gets full, at which point the buffer overflow and some data is lost.

I'm guessing that you have Default Enabled Event Classes set to No Classes, the outstation in ClearSCADA is not set to enable unsolicited, and you're not polling all classes often enough.


Reply From User: amanshow, posted: 2019-04-16 08:39:00
I actually have Default Enabled Event Classes set to Class 1, 2, 3 and the outstation is set to enable unsolicited, and my classes have scheduling polled enabled, but all have the same interval of 5S.


Reply From User: geoffpatton, posted: 2019-04-16 14:56:34
Is you SCADA Master address set the same on both ClearSCADA and the SCADAPack?


Reply From User: amanshow, posted: 2019-04-17 03:11:55
Yes, it is.

There's been a progress. The backfill actually worked when I set the timezone to local time (just as my partner set his scadapack rtu to local time)and it backfilled! However, there's something wrong with it because while rtu feeds clearscada values, my historic trend creates' current data for future', as far as I can remember that's how it said but you get the gist of it. Basically, my trend for a certain parameter already has a data on the trend that's currently four hours in advanced (e.g. it's currently 11AM but my trend shows it has data lined up until 3PM) but my current data 'corrects' it on the way.

However, when we enabled our feature of Target Scheduling, the local time blocks the feature from working, and we are forced to turn back to UTC for timezone. That's when the backfill doesn't work anymore. So, basically, we're at loss on what to do. I would appreciate any help.

Thank you all.


Reply From User: geoffpatton, posted: 2019-04-17 14:30:32
Wish I knew the solution for you. We use UTC and it works fine for us. Now DST is a problem. you have to leave that turned off on the computer or everything is off by an hour. We however do not use Targeted Scheduling. Ours are on 4G cellular or fiber and we just periodically poll the Classes and the SCADAPack sends data when its buffers fill.
If we lose connection it back fills when we reconnect.
Years ago there was a firmware issue when a SCADAPack would quit sending data, only thing it sent was it was online. A reboot would fix it for a while. Of course they fixed it in a new firmware. So maybe try a newer or slightly older firmware to see if the firmware is the problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore