How to call the ClearSCADA built in Time Average function?

EcoStruxure Geo SCADA Expert Forum

Schneider Electric support forum about installation, configuration, integration and troubleshooting of EcoStruxure Geo SCADA Expert (ClearSCADA, ViewX, WebX).

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • EcoStruxure Geo SCADA Expert Forum
  • How to call the ClearSCADA built in Time Average function?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
sbeadle
Kirk sbeadle Kirk
321
AndrewScott
Admiral AndrewScott
116
BevanWeiss
Spock BevanWeiss
99
View All

Recommended Forums

  • Remote Operations Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure Geo SCADA Expert Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2020-07-05 09:17 PM . Last Modified: ‎2023-05-03 12:13 AM

0 Likes
3
2300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 09:17 PM . Last Modified: ‎2023-05-03 12:13 AM

How to call the ClearSCADA built in Time Average function?

Is it possible to call the ClearSCADA Time Average function from a .NET application using the client library? Any example code will be much appreciated.

 

Thanks a lot.

Labels
  • Labels:
  • SCADA
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-07-06 10:55 PM

0 Likes
2
2283
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 10:55 PM

Yes, it's possible.

 

From the .NET API you can InvokeMethods, you just need to know the name of the Method that you want to call, and what aggregate it is on, and what arguments to provide to it.

Pretty much all of these can be found in the DB Schema.

So I would start there.

 

If you're on your local GeoSCADA Expert server you can probably just go here:

https://localhost/schema/CHistoryBase

 

And that should show you the methods available.  You can see 'ProcessedValue' which will return 'a single processed historic value', which sounds like what a Time Average would be.

Then if you look at the argument for it, it wants:

  • StartTime (Time)... should be easy
  • EndTime (Time)... should be easy
  • Aggregate (Long)... you probably need to find out what number is associated with the aggregate you want.. I forget where this was found, I think it's in the help somewhere, or tprojects
  • Reason (String).. to filter the values if needed

It will return a variant representing the processed value.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2020-07-07 02:19 AM

In response to BevanWeiss
0 Likes
1
2276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-07 02:19 AM

Here's some sample code to do that - comments do some of the explaining:

                // Retrieve the last day's data 
                DateTime startTime = DateTime.UtcNow.Subtract(TimeSpan.FromDays(1));
                DateTime endTime = DateTime.UtcNow;

                // Retrieve an average of the last day's values - Processed Data
                // Historic Aggregate code 3 = average of values. Search help for "Animations for Historic Data" for codes.
                object[] pParams = new object[4] { startTime, endTime, 3, "" };
                object value = (object)myPoint.InvokeMethod("Historic.ProcessedValue", pParams);
                Console.WriteLine("Processed Average Value: " + value.ToString());

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BevanWeiss
Spock BevanWeiss
Spock

Posted: ‎2020-07-06 10:55 PM

0 Likes
2
2284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-06 10:55 PM

Yes, it's possible.

 

From the .NET API you can InvokeMethods, you just need to know the name of the Method that you want to call, and what aggregate it is on, and what arguments to provide to it.

Pretty much all of these can be found in the DB Schema.

So I would start there.

 

If you're on your local GeoSCADA Expert server you can probably just go here:

https://localhost/schema/CHistoryBase

 

And that should show you the methods available.  You can see 'ProcessedValue' which will return 'a single processed historic value', which sounds like what a Time Average would be.

Then if you look at the argument for it, it wants:

  • StartTime (Time)... should be easy
  • EndTime (Time)... should be easy
  • Aggregate (Long)... you probably need to find out what number is associated with the aggregate you want.. I forget where this was found, I think it's in the help somewhere, or tprojects
  • Reason (String).. to filter the values if needed

It will return a variant representing the processed value.


Lead Control Systems Engineer for Alliance Automation (VIC).
All opinions are my own and do not represent the opinions or policies of my employer, or of my cat..
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

sbeadle
Kirk sbeadle Kirk
Kirk

Posted: ‎2020-07-07 02:19 AM

In response to BevanWeiss
0 Likes
1
2277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-07 02:19 AM

Here's some sample code to do that - comments do some of the explaining:

                // Retrieve the last day's data 
                DateTime startTime = DateTime.UtcNow.Subtract(TimeSpan.FromDays(1));
                DateTime endTime = DateTime.UtcNow;

                // Retrieve an average of the last day's values - Processed Data
                // Historic Aggregate code 3 = average of values. Search help for "Animations for Historic Data" for codes.
                object[] pParams = new object[4] { startTime, endTime, 3, "" };
                object value = (object)myPoint.InvokeMethod("Historic.ProcessedValue", pParams);
                Console.WriteLine("Processed Average Value: " + value.ToString());
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-07-07 10:00 PM

In response to sbeadle
0 Likes
0
2258
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-07 10:00 PM

Time Average = 30

StdDev = 5

 

Thanks a lot for your help!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore